Topic: 7.5HP Air Compressor 208V Ground-fault/Short Circuit protection and motor circuit conductors.

User: jklr, Location: Miss

Asked on: Wednesday, August 28, 2024 at 2:21 pm EDT
Answered on: Thursday, March 6, 2025 at 1:47 am EST

Question: Hello,I've got another motor calc that I have done and just want to make sure I am interpreting the code correctly.We are going to be swapping out a old compressor for a new one. Details below.Old compressor and circuitry.5HP23FLA40cRPM 1750Ser Fac 1.15#8 thhn on a 40amp qo standard trip beaker.New compressor7.5HPFLA 3340cRpm 1750SF 1.15According to 430.2487.5HP = 44amps @ 208v430.22 44 x 1.25 = 55AmpsTable 310.16 75c. 6 awg thhn430.52.... Using Standard trip QO breaker.Do we use the nameplate for the FLA or 430.248 FLC for the breaker?If we use FLA then 33 x 300(non time delay)= 99 MAX (100) and 33x1.25 41.25 MIN (45) (per table 240.6)Or if FLC 44 X 300 = 132 amp MAX44 x 1.25 = 55 amp minAbout a 200 ft run, VD 33amps at 208v 3.08% VD.Plan on coming out of panel with 3/4 emt then switching over to 6/2 MC above grid ceiling then go up to the roof perlins and strap MC for about 130ft inside the garage then set a box and then go down the wall to disco, then flex over to compressor. I had planned on using a 45 amp breaker if we use fla or a 55amp breaker if we use flc for 430.52.The motor has its own thermal overload.Thanks!

Okay, let's break down this motor replacement calculation and your proposed plan, making sure we're aligned with the NEC.

Understanding the Code Sections Involved 430.22

Motor Circuit Conductor Sizing - This section dictates the minimum ampacity of the conductors feeding the motor. You need to size your wires to handle at least 125% of the
motor's full-load current (FLC).

430.52

Motor Short-Circuit, Ground-Fault Protection - This covers the type and size of the overcurrent protective device (OCPD), which in your case is a standard inverse time breaker. This is protecting the conductors from short circuits and ground faults, not providing overload protection (you've correctly noted the motor has its own thermal overload protection).

430.248

Full-Load Current in Amperes, Alternating-Current Single-Phase Motors - This table provides
standardized FLC values for motors of various horsepower ratings and voltages.

Important

You generally

use this table value for sizing conductors and overcurrent protection
unless the motor nameplate FLA is higher. 240.6

Standard Ampere Ratings for Fuses and Inverse Time Circuit Breakers - Provides the standard sizes to use when your calculation falls between the standard sizes.

Your Calculations - Let's Review
1. Conductor Sizing (430.22) You correctly identified the 7.5HP motor FLC from Table 430.248 as 44 amps. 44 amps x 1.25 = 55 amps. Therefore, your conductors need to be rated for at least 55 amps. You've correctly chosen #6 AWG THHN (rated for 55 amps at 75°C in accordance with 310.16 for your assumed ambient temperature conditions.)2. Overcurrent Protection (430.52) This is where a critical decision needs to be made. You are using an inverse time breaker (standard trip). According to 430.52(C)(1), for inverse time breakers, the maximum allowable rating is 250% of the motor FLC (not 300%). Using Table 430.248 FLC (44 amps)

44 amps x 2.5 = 110 amps (MAX).

Using Nameplate FLA (33 amps)

33 amps x 2.5 = 82.5 amps (MAX).


Important Decision

The FIRST step to your calculations for 430.52 is to check the nameplate of the new motor and see if the new motor has a marked locked rotor amps. If the motor does not have a marked locked rotor amps, we are supposed to use 430.248 FLC. In this scenario, we would use Table 430.248 as it would be the more conservative way of doing this. If the maximum is 110amps. Then you would have to reference 240.6(A). The standard breaker sizes would be 110, 100, 90, 80, 70, 60. So you could use a 100 amp breaker.
3.


Voltage Drop
You've calculated a 3.08% voltage drop. This is acceptable. The NEC recommends limiting voltage drop to 5% total (3% feeder + 2% branch circuit).
4. Wiring Method
Your proposed wiring method is generally acceptable. Make sure that your conductors have the ampacity rating for the breaker that you use.

Answers to Your Questions
Do we use the nameplate FLA or 430.248 FLC for the breaker? You want to use 430.248 unless the nameplate FLA is HIGHER than 430.
248. Breaker Sizing with FLC

Based on the NEC, you can use UP TO a 100 amp breaker.

Revised Plan and Recommendations
1. Conductors

#6 AWG THHN (75°C rating) is suitable.2.

Overcurrent Protection

Based on using Table 430.248. 100 amp breaker (Standard Trip).
3.


Wiring Method

Your proposed EMT/MC cable combination is generally okay, but ensure proper supports and terminations.4.

Disconnect

A properly sized disconnect switch is required, located within sight of the motor and controller. The disconnect must have an ampere rating of at least 115% of the motors nameplate current rating. Therefore, at least 38 amps.5.

Check Local Codes

Always verify with your local jurisdiction for any additional requirements or amendments to the NEC.

Important Considerations
Motor Nameplate

Double-check the actual motor nameplate information when you receive the motor. The FLC and SF listed on the nameplate always take precedence over the table values if the nameplate values are higher.

Service Factor

Since the motor has a service factor of 1.15, it can handle occasional overloads up to 115% of its rated horsepower.


Ambient Temperature Correction

Ensure your conductor ampacity is correct for the actual ambient temperature where the conductors are installed. High ambient temperatures require derating.

Disclaimer:
This information is for general guidance only and should not be considered a substitute for consulting with a qualified electrician and thorough review of the applicable electrical codes. Always prioritize safety and adherence to local regulations. Flag for review