Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Pool Water Bonding

User: Christoph, Location: Coopersburg, PA

Asked on: Wednesday, August 28, 2024 at 2:28 pm EDT
Answered on: Thursday, March 6, 2025 at 1:48 am EST

Question: I have a pool company that (after I pointed at the thing) claims that their sacrificial zinc anode provides the water bonding for their Pool in accordance with 680.26(C).Naturally after receiving the info on the anode from the contractor I got on the phone with the manufacturer and they say that this anode is indeed in contact with the water 18 square inches. However they understand that this product is made to corrode away and they of course do not advertise this as a pool water bond for that reason. A very interesting thing that this gentleman pointed out is that if there is a heater "that has an awful lot of metal in it". To sleep at night accepting that I would want to see some documentation on the pool heater that shows me that the heating coils are properly bonded and that the manufacturer is comfortable and in agreement with that circumstances.How do you inspectors or installers handle this? No ladder on this job and no wet-niche metallic luminaire.

This is a tricky situation and highlights the importance of proper bonding and the potential misinterpretations of 680.26(C). Here's how an inspector or installer should handle this, breaking it down step by step

1. Understanding the Code (NEC 680.26(C))
Purpose

The primary goal of 680.26(C) is to create an equipotential bonding grid in the pool water. This minimizes voltage gradients in the water to prevent shock hazards.


Requirement

The code requires a conductive surface area of at least 9 square inches to be submerged and in contact with the pool water. It specifically states that this surface area needs to be of brass, copper, or other approved corrosion-resistant metal.

Interpretation Challenge

The ambiguity arises in what constitutes a "permanent" and "reliable" connection, and whether a sacrificial anode designed to corrode meets that definition.

2. Evaluating the Contractor's Claim
Manufacturer Disagreement

The fact that the anode manufacturer explicitly states they do not recommend or advertise it as a water bonding solution is a HUGE red flag. Their acknowledgment of its intended corrosion is the nail in the coffin for this claim.

Corrosion is the Issue

Sacrificial anodes are designed to corrode preferentially. As they corrode, their surface area in contact with the water diminishes. Furthermore, the effectiveness of the electrical connection decreases as corrosion products build up. This directly violates the intent of a
permanent and reliable bond.

Surface Area Reduction

Even if the anode initially provides 18 square inches, that won't last. Its protective function inherently leads to its demise.

Material Compliance

Even though the anode is made of zinc, that is not brass or copper or other corrosion-resistant metal. Zinc is designed to corrode quickly when subjected to galvanic action in salt or chlorine pools.


Lack of Listing/Labeling

UL or other listing agencies aren't likely to list a sacrificial anode for this specific purpose. Proper electrical equipment is always labeled and identifiable.

3. The Heater as a Potential Bonding Point (Handle with extreme caution)
Verification is Key

If the contractor is relying on the heater,

you need independent verification, not just their word.
You should not accept this at all.
Documentation from the Heater Manufacturer

The contractor must provide documentation (installation instructions, engineering specifications) from the heater manufacturer that explicitly states the heater's internal components (specifically the heating elements) are: Designed to be water bonded. Meet the 9 square inch requirement (if relying on a specific internal component). Connected to a reliable, external bonding point. The manufacturer must be comfortable with the pool water chemistry of the pool for the life of the product.

Access for Inspection

You need to be able to inspect the connection point on the heater to ensure it's properly bonded to the pool's bonding grid.


Material Verification

The heater's documentation needs to specify the material of the heating elements in contact with the water. They MUST be corrosion-resistant (brass, copper, or other approved material).

4. How an Inspector/Installer Should Proceed
Reject the Sacrificial Anode Claim

Based on the manufacturer's statement and the inherent nature of a sacrificial anode, it is

not acceptable
as the sole means of meeting 680.26(C).
Demand Alternative Compliance

The contractor MUST provide an alternative method of complying with 680.26(C). This typically involves:

Bonding Grid

Installing a conductive grid (usually copper wire) extending around the perimeter of the pool, bonded to the pool reinforcing steel, all metal parts, and the pool equipment.


Dedicated Bonding Conductor

Running a solid copper bonding conductor (usually #8 AWG) to all metal parts within 5 feet of the pool's inside wall.

Water Bonding Fitting

Install a listed water bonding fitting, per the requirements of 680.26(C), if a suitable water bonding solution is required.


Inspect and Verify

Thoroughly inspect all bonding connections. Ensure they are mechanically sound, corrosion-resistant, and properly sized.*

Document Everything

Keep detailed records of the inspection, any deficiencies found, and the corrective actions taken. Include manufacturer documentation for any equipment used for bonding.

In Summary


The contractor's claim regarding the sacrificial anode is highly suspect. You need to reject this claim outright. The contractor needs to provide a code-compliant bonding system that meets the intent of 680.26(C) and is designed for long-term reliability. Don't accept their word for anything – demand documentation and perform thorough inspections. Protect yourself from potential liability by ensuring proper bonding.If there's any doubt, consult with a qualified electrical engineer familiar with pool bonding requirements or your local electrical authority (AHJ). They can provide definitive guidance based on local interpretations and regulations. Flag for review