Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Coiling Cable to Reduce Short Circuit

User: CaptainKu, Location: Kansas City

Asked on: Wednesday, August 28, 2024 at 3:50 pm EDT
Answered on: Thursday, March 6, 2025 at 1:48 am EST

Question: Hey all. I have a existing panel that arrived on site that is only rated 10KA SCCR. This is a 75HP air compressor. I was planning on running a 1/0 cable roughly 60feet to the panel but the short circuit at the end of the cable would still be 14KA. I have already trimmed down the calc as much as possible including using utility provided AFC instead of infinite bus. My thought was to extend the circuit to reduce the current but I would need to add about 100 feet. I am looking at the best way to install this cable and have a spare 24" tray I could install to loop the cable in ~4 times to get 100 feet added. I know looping in a circle could create additional inductance but would 4 loops of 1/0 cable in a 12' tray really cause a issue? Is there a better way to do this?

Okay, let's break down this scenario and evaluate the proposed solutions along with some alternatives. Dealing with SCCR issues can be tricky, but there are a few common approaches.

Understanding the Problem SCCR Mismatch

The panel's SCCR (Short Circuit Current Rating) is 10kA. Your calculated available fault current at the panel is 14kA. This means a fault within the panel could potentially cause damage beyond what the panel is designed to withstand.


Mitigation is Necessary

You MUST take steps to reduce the available fault current at the panel to be at or below the 10kA SCCR. Ignoring this is a significant safety hazard and code violation.

Analyzing Your Proposed Solution (Looping Cable)


While technically feasible, looping the cable in the tray is probably the LEAST desirable method for a few reasons: Practicality

Looping 1/0 cable, even four times, within a 24" tray to achieve 100 feet of extra length will be incredibly difficult to manage. The bending radius will be tough, and physically getting that much cable into the tray will be cumbersome.


Inductance Concerns (Minor but Present)

You are correct, coiling the cable can increase inductance, but in your case, it will likely be negligible for the power frequency (60Hz). The impact on fault current reduction through increased impedance will be minimal compared to simply adding the straight length of the cable.

Heat Dissipation

Concentrating that much conductor in a small space will hinder heat dissipation. While not a major concern given the limited fault duration, it's still a slight negative.


Code Issues (Possible)

While it likely won't explicitly violate the code, local inspectors may raise eyebrows.

Cost Effectiveness

Adding that much cable, the tray install, and the labor is likely less cost effective than other solutions listed below

Better Solutions


Here are the more common and preferable ways to address this SCCR issue:1. Current-Limiting Fuses

This is often the
best and most cost-effective solution.

How it works

Install a current-limiting fuse upstream of the panel. These fuses are specifically designed to rapidly interrupt fault currents and significantly reduce the let-through energy. This means the actual fault current seen downstream of the fuse is much lower than the calculated available fault current.

Selection

You need to select a fuse that has an interrupting rating high enough to interrupt the available fault current (14kA in your case) and also a
let-through current (I2t value) that is low enough to protect the panel (i.e., that allows no more than 10kA to pass through). Fuse manufacturers provide let-through charts.

Example

Look at fuses like Bussmann Low-Peak (LPJ series), Mersen Amp-Trap 2000 (ATDR series), or Littelfuse CCMR series.

Advantages

Relatively inexpensive, effective, compact, and easily installed.


Important

You must coordinate the fuse with the motor's inrush current requirements. The fuse must be able to withstand the motor's starting current without nuisance tripping. This will require using time delay fuses.2.

Current-Limiting Circuit Breaker

Similar to current-limiting fuses, but with the convenience of being resettable. These are typically more expensive than fuses, but they eliminate the need to replace the fuse after a fault.

Selection

As with fuses, select a breaker with an appropriate interrupting rating and a low enough let-through current.


Example

Square D offers current-limiting breakers.

Advantages

Resettable, provides overcurrent protection.


Disadvantages

Typically more expensive than fuses.3.

Replace the Panel

If feasible, consider replacing the 10kA panel with one that has a higher SCCR (e.g., 22kA or 65kA). This eliminates the need for additional components. However, this is often the most expensive option. This is unlikely to be a solution in your case since the panel is already on-site and presumably already wired.4.

Add a Reactor

These are inline inductors that increase impedance in the circuit.

Advantages

They are more cost effective than replacing the panel.


Disadvantages

They may require some calculation and engineering and are larger than fuses.

Recommendation


Start by investigating current-limiting fuses. It is almost always the most economical way to fix this issue. Work with an electrical supply house or fuse manufacturer's representative to select the correct fuse. Give them the following information: Available fault current at the panel (14kA). Required SCCR (10kA). Motor HP (75HP). Motor voltage. Motor Code letter. Existing cable size (1/0).They can help you choose a fuse that will meet all the requirements and provide adequate motor starting protection.

Important Considerations Documentation

Whatever solution you choose, carefully document the changes and update the panel schedule and any other relevant drawings.


Inspection:
Ensure your solution is compliant with all applicable codes and regulations, and get it inspected by the relevant authority.Let me know if you have any other questions. I can help with fuse selection if you can provide the motor's voltage and code letter. Flag for review

Previous Question Next Question