Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Service disconnect

User: joec1824, Location: Ohio

Asked on: Wednesday, August 28, 2024 at 10:37 pm EDT
Answered on: Thursday, March 6, 2025 at 1:49 am EST

Question: Can an over size breaker be used if it is only being used as a disconnecting means? I want to use a tap box with an 800 amp breaker to feed 4 gang stacked meter socket. The 4 gang socket will have 4 150 amp breakers.

Okay, let's break down the NEC (National Electrical Code) implications of using an oversized breaker solely as a disconnecting means in your described scenario.

The Short Answer: Generally NO, with a critical exception for certain tap rules.The Long Answer & Explanation1. Overcurrent Protection vs. Disconnecting Means Overcurrent Protection

A breaker's primary function is to
protect conductors and equipment from overcurrents (overloads and short circuits). The breaker's ampacity rating must be appropriately sized to the conductors it protects, per NEC Article 240. Using an oversized breaker to protect a conductor rated for a lower ampacity is a direct violation of the NEC and creates a significant safety hazard (fire risk).

Disconnecting Means

A disconnecting means (typically a breaker or a switch) is used to isolate equipment or circuits for servicing, maintenance, or emergency shut-off. While a disconnect still can provide overcurrent protection, that's not its sole job. The NEC has requirements for the disconnect's suitability (voltage, interrupting rating), but specifically deals with overcurrent protection in a different section of the code.2.

The Problem with Your Proposed Setup
No General Exception

There is
no blanket exception in the NEC that allows you to disregard overcurrent protection requirements simply because a breaker is also being used as a disconnecting means. If the 800A breaker feeds the 4-gang meter socket, it must protect the conductors upstream of the 150A breakers.

Conductor Protection

The conductors feeding the 4-gang meter socket, as well as the meter socket itself, must be rated to handle the potential fault current that the 800A breaker could pass. This means extremely large (and likely very expensive) conductors.

Series Ratings

While not exactly what you are looking for, the 800A breaker needs to have a Series Rating equal to or greater than the Available Fault Current. This is often overlooked and needs to be verified.3.

The
Possible Exception: NEC Tap Rules (Article 240.21(C))
The Key Concept

The NEC does have provisions (tap rules) that can allow you to tap a smaller conductor from a larger feeder without requiring overcurrent protection at the tap point, provided very specific conditions are met.

NEC 240.21(C)(2)

This section, often called the "10-foot tap rule" or the "25-foot tap rule", might be applicable
if you can meet the following conditions:

Tap Conductor Ampacity

The tap conductors (those going from the tap box to the 4-gang meter socket) must have an ampacity that is: Not less than the calculated load. Not less than the rating of the device (in your case, the 150A breakers) or not less than the rating of the overcurrent protective device at the termination of the tap conductors. Not less than 1/3 of the rating of the overcurrent device protecting the feeder.

Tap Conductor Length

The tap conductors must not exceed 10 feet (or in some cases 25 feet - see NEC 240.21(C)(3)) in length.

Enclosure

The tap conductors must be enclosed in a raceway or otherwise protected from physical damage.


Tap Location

The tap cannot originate in a panelboard or other enclosure containing overcurrent protective devices (other than the tap box itself).

Field Installations

The tap conductors are permitted to be in the field (as opposed to a factory assembly).


NEC 240.21(C)(5)

This deals with 'Transformer Secondary Conductors' and won't likely apply to your case.4.

How the Tap Rule Might Work (with a HUGE IF)
Example

Let's say each meter socket is calculated at 100 amps. In this case you have to use 150 amps (breaker size) for the calculation because it's larger. The
minimum ampacity of the tap conductors going to the 4 gang meter socket would have to be at least 1/3 of 800 amps = 266.66 amps. If using the 10 foot tap rule you would have to use conductors rated for at least 266.66 amps.

Crucial Considerations for Tap Rules



Enforcement

Inspectors often scrutinize tap rules
very closely. Documentation and careful adherence to all the requirements are essential.

Available Fault Current

Be absolutely certain that the tap conductors, meter sockets, and downstream breakers have an adequate interrupting rating for the available fault current at that location. This needs to be calculated.

Engineering Review

For a setup like this, I
highly recommend having a qualified electrical engineer review your design to ensure compliance with the NEC and local codes.

In Summary and Recommendations
Direct Connection with an 800A Breaker: Not Recommended or Likely Code-Compliant. It's extremely unlikely you could directly feed a 4-gang meter socket with an 800A breaker without violating overcurrent protection requirements. Explore Tap Rules (Carefully!). The tap rules offer possible flexibility, but only if every condition is strictly met. Consider a Distribution Panel/Sub-Panel. A more common and often simpler solution would be to use a properly sized distribution panel downstream of your tap box, with appropriately sized breakers feeding each meter socket. This would provide better overcurrent protection and simplify the installation. The panel could also serve as your disconnecting means. Consult with a Qualified Electrician and/or Engineer. Given the size and complexity of your project, it's essential to consult with licensed professionals who can properly design, install, and inspect the system to ensure safety and code compliance. Do not attempt this on your own without professional guidance. Interrupting Rating (AIC)

Be certain the AIC rating of the 150A breakers are adequate for the available fault current.

Disclaimer:
This information is for general informational purposes only and should not be substituted for the advice of a qualified professional. Always consult with a licensed electrician or electrical engineer before making any decisions about electrical installations. Flag for review

Previous Question Next Question