User: RicardoC77, Location: Cocoa, Fl
Asked on: Thursday, August 29, 2024 at 9:58 am EDT
Answered on: Thursday, March 6, 2025 at 1:50 am EST
Question: When sizing residential service “feeder” on a multi-family dwelling unit, from the meter center to each unit interior panel; NEC 310.12 ( B ) applies.“shall be permitted to have an ampacity not less than 83% of the feeder rating.”Question is:Does voltage drop is has to be considered and wire size adjusted per VD calculation?I have some feeders that range between 220-380’ long.
Yes, voltage drop must be considered, regardless of whether you're using the 83% rule in 310.12(B). The NEC recommends voltage drop limitations and you'll almost certainly exceed those limitations with feeders that long if you only size based on ampacity.Here's why: NEC Recommendations
While the NEC doesn't mandate a specific voltage drop percentage, it provides recommendations. 210.19(A)(1) FPN No.4 and 215.2(A)(3) FPN No.2 both suggest a maximum voltage drop of 3% for the feeder plus 5% for the feeder and branch circuit combined.
Performance Issues
Excessive voltage drop can cause appliances to malfunction, motors to overheat and fail prematurely, and lighting to dim. It's a performance and safety issue, even if it's not a strict NEC violation in many cases.
Long Feeders and the 83% Rule
The 83% rule in 310.12(B) is intended to allow for some reduction in conductor size after you've determined the load. It doesn't negate the need to consider voltage drop. In fact, using the 83% rule makes voltage drop more likely to be a problem because you're starting with a smaller conductor.
How to handle this
Calculate the Load
Accurately determine the calculated load for each dwelling unit. This is critical. Use Article 220 of the NEC. Consider the demand factors that apply to multi-family dwellings.2.
Calculate Initial Conductor Size based on 83% Rule (310.12(B))
Determine the minimum ampacity required using the 83% rule if you intend to apply it. For example, if your calculated load is 100A, the minimum allowed ampacity would be 83A.3.
Calculate Voltage Drop
Use a voltage drop calculator, or the formula in NEC Chapter 9, Informative Annex C, to calculate the voltage drop for the conductor size you determined in step 2. Make sure to use the actual length of the feeder (220-380 feet in your case) and the correct voltage (e.g., 120V or 240V). Also, use the correct wire type temperature rating.4.
Compare Voltage Drop to Recommendations
Is the voltage drop you calculated less than 3% for the feeder? If not, you need to increase the conductor size.5.
Iterate
If the voltage drop is too high, increase the conductor size and recalculate the voltage drop. Repeat until you achieve an acceptable voltage drop (ideally, less than 3%).6.
Verify Ampacity
After increasing the conductor size to meet voltage drop requirements, double-check that the conductor's ampacity is still sufficient to carry the calculated load.
Example (Simplified)
Let's say a unit's calculated load is 100A, and the feeder is 300 feet long, 240V, and using copper conductors.1.
Calculated Load
100A2.
Minimum Ampacity (83% Rule)
100A 0.83 = 83A. Based on Table 310.16, a #4 AWG copper conductor with a 75°C temperature rating would appear to be sufficient for 85A (assuming appropriate termination rating).
3.
Voltage Drop Calculation (using a simplified formula for illustration)
VD = (2 K I L) / CMIL K (copper constant) ≈ 12.9 I (current) = 100A L (length) = 300 feet CMIL (circular mils for #4 AWG) = 41,740 CMIL VD = (2 12.9 100 300) / 41,740 ≈ 18.5 Volts Percentage Voltage Drop = (18.5 / 240) 100 ≈ 7.7%4.
Comparison
7.7% voltage drop is far too high.5.
Iteration
Let's try a #1 AWG (CMIL = 83,690). VD = (2 12.9 100 300) / 83,690 ≈ 9.2 Volts Percentage Voltage Drop = (9.2 / 240) 100 ≈ 3.8%6.
Another Iteration Now let's try 1/0 (CMIL = 105,500) VD = (2 12.9 100 300) / 105,500 ≈ 7.3 Volts Percentage Voltage Drop = (7.3 / 240) 100 ≈ 3.0%7. Another Iteration Now let's try 2/0 (CMIL = 133,100) VD = (2 12.9 100 300) / 133,100 ≈ 5.8 Volts Percentage Voltage Drop = (5.8 / 240) 100 ≈ 2.4%In this simplified example, a 2/0 copper conductor would be needed to achieve acceptable voltage drop, even though #4 AWG would have appeared sufficient based on the 83% rule for ampacity.
Important Considerations
Aluminum vs. Copper
Aluminum conductors have a higher resistance than copper, so voltage drop will be more significant with aluminum.
Power Factor
The formulas and calculators assume a power factor close to 1.0. If the load has a low power factor, voltage drop will be higher.
Accurate Load Calculation
The most crucial step is accurately calculating the load. Underestimating the load will lead to underestimated voltage drop.
Local Requirements
Always check with the local electrical inspector for any specific voltage drop requirements or interpretations.
Software/Calculators
Utilize voltage drop calculators and software tools for accurate calculations. These tools often account for temperature, conduit type, and other factors.
Future Loads
Consider potential future load increases when sizing conductors.
In summary, always prioritize voltage drop calculations, especially for long feeders. The 83% rule in 310.12(B) should be used after* voltage drop has been addressed, not as a substitute for it. Flag for review