Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: NEC 310.15(C)(1)

User: Isaiah, Location: Baton Rouge

Asked on: Thursday, August 29, 2024 at 10:40 am EDT
Answered on: Thursday, March 6, 2025 at 1:50 am EST

Question: I’ve got number 4, 3/C #12 AWG XHHW-2, 90 Degree C, in a RGS conduit.These are for 3 phase, 460V induction motors at 12FLA each.My understanding is the ampacity adjustment factor should be against the 30A, not against the 20A per 310.16 and 240.4(D).So 4, 3phase motors x 12 current carrying conductors would mean an adjustment of 50% per 310.15(C)(1) or 15A per cable. Is this correct?

You're on the right track, but let's break it down and clarify a few points to make sure you're 100% accurate.Here's a step-by-step analysis:1. Conductor Type and Insulation

You're using #12 AWG XHHW-2, which is rated for 90°C in dry and damp locations. You're using RGS (Rigid Galvanized Steel) conduit.2.

Motor Information

3-phase, 460V induction motors. 12 FLA (Full Load Amps) each.3.

Understanding Ampacity



310.16

This table provides the allowable ampacities of conductors based on their insulation type and temperature rating. For #12 AWG XHHW-2, the ampacity is

30A
at 90°C. The 20A you mentioned is likely referring to the limitation imposed by 240.4(D), which applies under specific conditions (small conductors). We need to determine if 240.4(D) applies here.4. 240.4(D) Small Conductor Rule

This section of the NEC protects small conductors from overcurrent. It typically limits the overcurrent protection for #14 AWG to 15A, #12 AWG to 20A, and #10 AWG to 30A unless specific exceptions apply.

Key Exception: 430.53(D)

This exception
is likely applicable in your case. Since these conductors are supplying motors, you can use the motor protection rules in Article 430, which may allow you to exceed the 20A limitation of 240.4(D). You are not using individual branch circuits.Therefore the adjustment factor should be against the 30A. This is correct5.

Calculating Number of Current-Carrying Conductors (CCCs)

You have four 3-phase motors, each requiring three conductors (one for each phase: A, B, and C). Grounding conductors are not counted as CCCs. Therefore, you have 4 motors 3 conductors/motor = 12 CCCs.6.

Ampacity Adjustment (Derating)



310.15(C)(1)

This section covers the ampacity adjustment factors for more than three current-carrying conductors in a raceway or cable.
With 12 CCCs, the adjustment factor is

50%
(as you stated).7. Applying the Adjustment Factor

Start with the 90°C ampacity: 30A Apply the adjustment factor: 30A 0.50 = 15A8.

Verification

Your final adjusted ampacity is 15A. Each motor has a FLA of 12A. 15A is greater than 12A.

Therefore, based on your provided information, the final adjusted ampacity appears adequate.
Important Considerations and Potential Issues



Motor Starting Current

The 12 FLA is just the
running current. Motors draw a much higher current (typically 6-8 times FLA) when starting. You need to verify that the overcurrent protection device (circuit breaker or fuses) is properly sized to handle the motor starting current without nuisance tripping, as per Article 430 (specifically 430.52 for motor branch-circuit short-circuit and ground-fault protection).

Voltage Drop

With 12 motors on the same circuit, voltage drop could be a significant issue, especially during motor starting. You need to calculate the voltage drop to ensure it's within acceptable limits (typically no more than 3% for power circuits). If the voltage drop is excessive, you may need to increase the conductor size (e.g., go to #10 AWG or #8 AWG).

Overcurrent Protection Device Sizing

You
must use Article 430 to size the overcurrent protection (breaker/fuses). The 20A rule from 240.4(D) is not the governing factor here. The overcurrent protection is specifically for the motor branch circuit short circuit and ground fault protection. This often allows for a much higher value than 125% FLA of a single motor, as the article allows for instantaneous tripping or time delay in the case of motor start-up and fault.

Grounding Conductor

Remember to properly size the grounding conductor according to NEC 250.122, based on the size of the overcurrent protection device.

In summary, your calculation of the ampacity adjustment is correct, but you must verify the motor starting current, voltage drop, and, most importantly, the overcurrent protection size using Article 430.
Failure to do so could result in nuisance tripping, motor damage, or unsafe conditions.

Disclaimer: I am an AI Chatbot. This information is for educational purposes only and should not be considered a substitute for professional electrical engineering advice. Always consult the latest edition of the National Electrical Code (NEC) and a qualified electrician for all electrical work. Electrical work can be dangerous, and incorrect wiring can lead to fire or electrocution. Flag for review

Previous Question Next Question