User: RRCHIARATT, Location: Norther California
Asked on: Thursday, August 29, 2024 at 12:15 pm EDT
Answered on: Thursday, March 6, 2025 at 1:51 am EST
Question: What is the maximum voltage drop to a RV pedestal? \Is it 3% based on its a feeder or is it 5% over all based on the last outlet is on the pedestal?
The voltage drop calculation for an RV pedestal can be a bit tricky, and there are different interpretations. Here's a breakdown of the factors and a reasoned approach
Understanding the Codes and Standards
NEC (National Electrical Code)
The NEC is the primary electrical code in the US. It doesn't explicitly mandate a single voltage drop percentage for RV pedestals specifically. However, it does provide guidance on voltage drop in general.
NEC 210.19(A)(1) FPN No. 4 & 215.2(A)(3) FPN No. 2
These Informational Notes recommend that the voltage drop on a branch circuit or feeder should not exceed 3% to the farthest outlet, power, lighting, and appliance load, and the maximum voltage drop on both feeders and branch circuits to the farthest outlet should not exceed 5%.
NFPA 1194 (Standard for Recreational Vehicle Parks and Campgrounds)
This standard provides specific requirements for RV parks and campgrounds, including electrical systems.
The Debate: Feeder vs. Branch Circuit
The core of the question lies in whether the wiring to the RV pedestal is considered a feeder or a branch circuit (or a combination of both). Feeder Argument
If the wiring from the main distribution panel in the RV park to the individual pedestal is considered a feeder, then applying the 3% voltage drop to the farthest RV pedestal from the panel, based on the Informational Note in 215.2(A)(3) FPN No. 2, is a reasonable approach.
Branch Circuit Argument
Each RV site could be considered a branch circuit. In that case, a 3% limit to the pedestal is more appropriate. However, voltage drop must be considered from the source to the farthest point.
Key Considerations for RV Pedestals1. NFPA 1194 Doesn't Specify a Percentage
While NFPA 1194 sets standards for RV park electrical systems, it does not explicitly mandate a specific voltage drop percentage.2.
Focus on Performance
The primary goal is to ensure that RVs can operate properly and safely at the pedestal. Excessive voltage drop can cause appliances to malfunction, motors to overheat, and other issues.3.
Practical Implications
RVs draw significant current, especially when air conditioners or electric water heaters are running. Long wire runs and undersized conductors can easily lead to unacceptable voltage drop.4.
Local Codes and AHJ (Authority Having Jurisdiction)
The most important factor is to comply with local electrical codes and the requirements of the AHJ. They may have specific interpretations or regulations regarding voltage drop in RV parks.
The Most Conservative and Recommended Approach
Given the potential for high current draw by RVs and the need for reliable operation, the most conservative and generally recommended approach is to design the electrical system to meet the 5% total voltage drop recommendation from the source to the farthest RV pedestal. Feeders
Voltage Drop calculation from the source to the distribution point at the RV park
Branch Circuits
Voltage Drop from the distribution point to the individual RV pedestal
Example Calculation
Let's say the distance from the main panel to the farthest RV pedestal is 200 feet. Here's how you might approach the voltage drop calculation:1. Feeders
Calculate the voltage drop from the main panel to the distribution panel. This should be significantly less than 3%.2.
Branch Circuits
Calculate the voltage drop from the distribution panel to the farthest RV pedestal. Keep this below 3% as well, so your total does not exceed 5%.
In summary
There's no single, universally mandated voltage drop percentage for RV pedestals. The most conservative and recommended practice is to aim for a total voltage drop of no more than 5% from the source to the farthest RV pedestal. Prioritize compliance with local codes and the requirements of the AHJ.* Ensure that wiring is sized appropriately to minimize voltage drop, considering the potential for high current draw by RVs.
Disclaimer: I am an AI chatbot and cannot provide electrical code interpretations or engineering advice. Always consult with a qualified electrician for electrical system design and installation. Flag for review