Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 240V delta

User: jeff motta, Location: nj

Asked on: Thursday, August 29, 2024 at 1:44 pm EDT
Answered on: Thursday, March 6, 2025 at 1:51 am EST

Question: I am looking for some advice, I have a client who wants to add a power panel for 120v receptacles around the plant, I found a spare 200A 3phase breaker available, but the service is 240V delta. I plan to come off the spare 200a breaker from the 240v delta panel, install a 75KVA 240 delta to 208v/120v wye transformer to feed the new power panel, I wanted to know if there are any specifics as to breaker/fuse sizing.Thanks

You've got the right basic idea, but let's dial in the specifics for breaker and fuse sizing to ensure compliance and safety. Here's a breakdown of the calculation and important considerations, based on the National Electrical Code (NEC)

1. Transformer Sizing and Current Calculations
Transformer Capacity

75 kVA is a good starting point for a dedicated receptacle panel. However,

confirm this is adequate for the
actual load the receptacles will serve. Over sizing is safe, under sizing can cause problems. Primary (240V Delta) Full Load Amps (FLA)

FLA = kVA 1000 / (Voltage √3) FLA = 75 1000 / (240 1.732) FLA ≈ 180.4 Amps

Secondary (208Y/120V Wye) Full Load Amps (FLA)

FLA = kVA 1000 / (Voltage √3) FLA = 75 1000 / (208 1.732) FLA ≈ 208.1 Amps (This is a three-phase current, so each phase will carry approximately this amount)

2. Primary Overcurrent Protection (240V Delta Side)
NEC Article 450.3(B) Transformer Overcurrent Protection

This is critical. You are permitted to protect the primary side of the transformer at no more than 125% of the transformer's primary FLA rating.

Primary Breaker Sizing

125% of 180.4 Amps = 225.5 Amps You can use a 225A breaker to protect the primary side, you should not exceed this limit.

Important

The existing 200A breaker can be used on the primary. This will provide adequate overcurrent protection for the transformer and will allow the transformer to run to its maximum capacity. You are not required to use a 225A breaker.

Important Note on Feeder Size

The feeder conductors supplying the 200A breaker at your 240V panel must be sized to handle the load. At a minimum, the conductors must be rated for 125% of the transformer's primary current (180.4A
1.25 = 225.5 Amps). Ensure your existing feeder to the 200A breaker is adequately sized.

3. Secondary Overcurrent Protection (208Y/120V Wye Side)
NEC Article 450.3(B) Transformer Overcurrent Protection

Similar to the primary, the secondary can be protected at 125%.


Secondary Main Breaker in the New Panel

125% of 208.1 Amps = 260.1 Amps

This is a critical point

You cannot simply use a 250A breaker because you are limited to the next size standard breaker, you must use a 225A Breaker on the secondary side, this is critical!

Considerations



Main Breaker Rating of the Panel

Ensure the power panel itself is rated for at least 225A (or higher, if you anticipate future expansion).

4. Important Considerations and Best Practices
Coordination

Conduct a short-circuit study to ensure proper coordination between the primary and secondary breakers. You want the secondary breaker to trip before the primary, localizing the fault. An electrical engineer can perform this study.


Grounding

Absolutely critical. Properly ground the transformer per NEC Article 250. This includes:

Bonding the Transformer Enclosure

To the grounding electrode conductor (GEC) system.


Establishing a Grounding Electrode System at the Transformer Location

This might involve a grounding electrode conductor connected to a metal water pipe, a ground ring, or ground rods.

Bonding the Neutral Point of the Wye Secondary

This creates the solidly grounded neutral required for 208Y/120V systems. This is often done with a bonding jumper
inside the transformer.

Delta High Leg

If your existing 240V delta system has a "high leg" (typically 208V to ground), be absolutely sure it's properly identified and labeled in the existing panel and that you understand its impact on the new transformer. It shouldn't impact the transformer's performance, but it's a critical safety consideration.

Neutral Conductor

The neutral conductor from the transformer to the panel must be sized appropriately. Consider the potential for harmonic currents, which can overload the neutral. Upsizing the neutral to 200% of the phase conductors is not usually required, but analyze the potential for non-linear loads. If you have a high degree of non-linear loads, you may need to oversize it.


Voltage Drop

Calculate voltage drop from the transformer to the furthest receptacle. The NEC recommends limiting voltage drop to 3% for feeders and 5% overall.

Labeling

Clearly label
everything. Label the transformer, the panel it feeds, the source breaker in the 240V delta panel, and the function of the panel.

Local Codes



Verify all requirements with your local electrical inspector.
Local codes may have stricter requirements than the NEC.

In Summary (Key Breaker Sizes)



Primary Side (240V Delta)

Existing 200A breaker is fine, verify the existing feeder conductors supplying the 200A breaker is sufficient to handle 225A (125% of transformer primary current)


Secondary Side (208Y/120V Wye)

225A main breaker in the new power panel.

Important Considerations BEFORE you Begin



Load Calculation

Perform a detailed load calculation for the receptacles. What are they expected to power? This will ensure the 75kVA transformer is sufficient.


Available Fault Current

Calculate the available fault current at the secondary of the transformer. This will determine the required interrupting rating of the breakers in the new panel.

Qualified Electrician

This is
not a DIY project. Hire a qualified and licensed electrician with experience in transformer installations and three-phase power systems.

Permits:
Obtain all necessary electrical permits.This is a significant electrical project. Accuracy, safety, and compliance with all applicable codes are paramount. Engaging an experienced electrician and electrical engineer is highly recommended to ensure a safe and reliable installation. Good luck! Flag for review

Previous Question Next Question