Topic: Voltage drop on a string with different wire lengths

User: Zyb, Location: Maine

Asked on: Thursday, August 29, 2024 at 2:19 pm EDT
Answered on: Thursday, March 6, 2025 at 1:51 am EST

Question: Hi,just want to make sure that i got this right. in Voltage drop calculation V=2(D)(I)(R), the number 2 is constant to multiply D (one way length) in order to get the whole length of the circuit. can someone confirm if my calculation on the attached image is correct. Thank you!

Yes, you are correct. The "2" in the voltage drop formula V = 2 D I R is a constant used to account for the fact that the current travels to the load and then returns, covering the distance "D" twice.

Your Calculation Review

Looking at your image, your calculations appear to be correct, as long as you understand what each variable represents:


V = 2(D)(I)(R)
V = Voltage drop (in volts) 2 = Accounts for the two-way length of the circuit D = One-way distance (length) of the circuit (in feet) I = Current flowing through the circuit (in amperes) R = Resistance per foot of the conductor (in ohms per foot)Important Considerations Conductor Resistance

Make sure you are using the correct resistance (R) value for the specific conductor size and material (e.g., copper, aluminum) you're using. Resistance values are typically found in electrical codes or conductor specifications. The resistance also varies with temperature, but this is often ignored in basic voltage drop calculations.

Units

Ensure that all units are consistent (feet for distance, amps for current, ohms per foot for resistance). If your resistance is given in ohms per 1000 feet, you'll need to divide it by 1000 to get ohms per foot.


Acceptable Voltage Drop:
Compare your calculated voltage drop to the maximum acceptable voltage drop specified by the electrical code (e.g., the NEC in the US) for the type of circuit and application. Typically, this is 3% for branch circuits and 5% for feeders (total voltage drop from the source to the furthest point of utilization).In summary, your understanding of the formula and the role of the "2" is correct. Double-check your resistance values and ensure your calculated voltage drop is within acceptable limits according to the relevant electrical code. Flag for review