Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 75 hP Motor Application with 150 hP motor installed

User: mayanees, Location: Westminster, MD

Asked on: Thursday, August 29, 2024 at 2:34 pm EDT
Answered on: Thursday, March 6, 2025 at 1:52 am EST

Question: We have a client that runs a cement operation where they have a 460V, 3-phase blower motor that pulls 97 amps. The motor is 150 hP with overloads at 180 amps and a motor nameplate fla of 169 amps.They recently had a fire at the motor and they'd like the starter to have dropped out.I've never heard of sizing the overloads under the motor rating, but would that have tripped for say 125 amps, and would that be a recommendation? The logical recommendation is to size the motor appropriately, and I know the motor will be in a low power factor situation, but would undersized overloads signal a load change?Thanks for any replies.

This is a complex situation with several factors to consider. Let's break it down

Understanding the Problem:
The Fire

The fact that a fire occurred and the overload protection
didn't trip is a major concern. That's what they are there to prevent.

High Current Draw (97A)

While less than the overload setting (180A) it is also below the FLA (169A). This indicates the motor may not be overloaded.

Overload Sizing (180A)

Exceeds 125% of the FLA.


Motor Nameplate FLA (169A)

This is the Full Load Amperage the motor should draw under normal operating conditions.

Motor HP (150 HP)

This is a fixed rating of the motor's output.


Low Power Factor

This could contribute to higher current draw but wouldn't directly cause a fire if the current remains within the FLA.

Why the Overloads Didn't Trip



Incorrect Overload Sizing

Overloads are primarily to protect the
motor windings from damage due to sustained overcurrent. Overloads are designed to trip at 125% of the FLA.

Other Faults

The fire could have been caused by something other than a simple overload:

Winding Insulation Failure

Deterioration of the insulation on the motor windings can lead to arcing and a fire, even without exceeding the overload setting. This could be due to age, heat, contaminants, or voltage surges.


Loose Connections

Loose connections at the motor terminals, starter, or wiring can cause resistance, heat buildup, and arcing.

Contamination

Dust, moisture, or chemicals inside the motor can reduce insulation resistance and lead to short circuits and fires.


Bearing Failure

A failing bearing can cause excessive friction, heat, and eventually motor failure and potentially fire.

Recommendations


Root Cause Analysis



Before doing anything else, determine the cause of the fire!
Was it winding insulation breakdown, loose connections, bearing failure, or something else? This is crucial to prevent recurrence. A qualified electrician or motor repair shop should perform a thorough inspection.2. Verify Motor Load

Confirm the 97 amp reading is accurate and representative of normal operation. Use a calibrated clamp meter. Take readings over a period of time to see if the current fluctuates. Verify voltage at the motor terminals under load. Low voltage can increase current draw.3.

Overload Sizing



NEC (National Electrical Code) Guidelines

NEC article 430 dictates overload protection for motors. Generally, overloads should be sized at 125% of the motor's nameplate FLA for motors with a service factor of 1.15 or higher, or a temperature rise of 40°C or less. For motors without these ratings, the overload should be sized at 115% of the FLA.

The Current Situation

180 Amps is far above 125% of 169 Amps. This is incorrect.


Recalculate

125% of 169A = 211A. 115% of 169A = 194A.

Recommendation

Sizing at 125A is too low. That might cause nuisance tripping.

Consult the motor manufacturer's recommendations
for the specific motor. Choose overload heaters or settings as close as possible to, but not exceeding, 125% (or 115% if applicable) of the motor FLA. For motors with a service factor greater than 1.0, sizing the overloads at 125% of the nameplate FLA should be sufficient, but you have to confirm the nameplate data for that motor.
4. Do NOT Undersize Intentionally

Purposefully undersizing the overloads significantly (like to 125A) is not a safe or code-compliant solution. It's a band-aid that may mask a more serious underlying problem and lead to frequent nuisance trips.5.

Address Low Power Factor (If Present)

While low power factor
alone shouldn't cause a fire if the current is still below the FLA, it can increase the overall current draw. Consider power factor correction capacitors at the motor or at the MCC to improve the power factor and reduce current. However, this is a separate issue from the overload protection.6.

Motor Condition



Insulation Test

Have the motor windings meggered (insulation resistance test) by a qualified electrician or motor shop. This will reveal any insulation degradation that could lead to future failures.

Bearing Inspection

Inspect the motor bearings for wear, noise, or excessive heat. Replace if necessary.


Cleaning

Clean the motor thoroughly to remove any accumulated dust, dirt, or debris that could contribute to overheating.7.

Wiring and Connections



Inspect All Connections

Carefully inspect all wiring connections at the motor, starter, disconnect switch, and MCC for tightness and signs of corrosion or overheating. Tighten or replace as needed.


Wire Size

Verify that the wiring is sized correctly for the motor's FLA, considering voltage drop.8.

Starter Inspection



Contact Condition

Inspect the starter contacts for pitting, burning, or wear. Replace the contacts or the entire starter if necessary.


Proper Operation

Verify that the starter is operating smoothly and reliably.9.

Grounding

Ensure that the motor and all electrical equipment are properly grounded according to code.10.

Consider a Motor Management Relay (MMR)

A modern motor management relay offers more advanced protection than basic overloads. These relays can monitor: Overcurrent/Undercurrent Overload Phase Loss/Imbalance Under Voltage/Over Voltage Ground Fault Temperature (with sensors in the motor windings) Stall Protection

Important Safety Considerations



Qualified Personnel

All electrical work must be performed by qualified and licensed electricians who are familiar with motor control systems and safety procedures.

Lockout/Tagout

Always use proper lockout/tagout procedures before working on any electrical equipment.


Personal Protective Equipment (PPE)

Wear appropriate PPE, including safety glasses, gloves, and arc-rated clothing, when working on electrical equipment.

In summary:
Do not undersize the overloads. Focus on identifying the root cause of the fire, properly sizing the overloads based on the motor FLA, ensuring the motor is in good condition, and verifying the wiring and connections are correct. A motor management relay can provide enhanced protection and valuable diagnostic information. Flag for review

Previous Question Next Question