Question: I'm an electrical contractor in Texas, I'm also the Master.I'm hoping this is the appropriate topic to post this here. If not, my apologies to the moderator, I looked over the other topics and this one seemed the most related.Without naming locations, my office is located 6 hours away from the location in question (Texas is big) and I don't service the area of the location. This job was a one-off because there were no able generator contractors in the area and I was an old friend of the head of maintenance (at the time) for this facility. He begged me to come help him.In 2022 I installed a stand by generator at a resort. The resort was soon to be completely remodeled and the new generator was the first thing they wanted to get done. I replaced an existing standby generator that was not functioning. All of the existing wiring from the generator to the ATS and from the ATS to the emergency systems power bank was all NEC compliant and didn't need to be replaced or modified. All we did was remove the old generator, set the new one and wire it up the way it was. We shut down the entire facility at 3 am to test the emergency systems. The ATS took over and provided power to the emergency power panels as expected, the elevators ran as normal. We exercised all of the emergency systems that we could except for actually running the fire pumps (but the fire pump system had power). I programmed the generator to exercise itself once a week and verified that it was doing so with the staff maintenance manager for four weeks after the project was complete.After the generator was set and tested, the facility had the fire alarm contractor onsite the next day to get his system current and compliant. He requested that I run a set of control wires from the ATS to the fire alarm control room. We did this. We installed two runs of CAT6 in EMT from the ATS and terminated them in a 1900 box located in the ceiling of the fire control room, we also left enough CAT6 to run anywhere in the fire control room. The other end is rolled up in the ATS enclosure. It was my understanding that the elevator company was supposed to terminate the signal wires in the ATS & the fire alarm panel to do whatever they are required to do with the elevator in case of a fire or power outage.Now, two years after and the facillity nearing the completion of the big remodel. Their local electrician is not wanting to connect the wires to the ATS because he really doesn't know where they go. That's understandable because I'm not really sure it is the electricians job to do this. The fire alarm company says it's the elevator company's responsibility and the elevator company says it's my responsibility because I installed the generator.I don't mind making the terminations nor do I mind traveling that far, if I'm suitably compensated for my time and travel.My question here is, what would other contractors do in this situation? If I did accept the job, where would I find out what the ATS is supposed to do for the fire control panel and the elevators? It it within the legal coverage of my electrical Masters license in Texas to do such work? Or should the elevator contractor be the one who is responsible?

Okay, this is a classic multi-trade finger-pointing situation. Here's a breakdown of how I'd approach it as a fellow contractor, along with some considerations specific to your situation in Texas

1. Understanding the Core Problem:
Lack of Clear Scope Definition

The original problem stems from a lack of clearly defined scopes of work and responsibility during the initial generator installation and subsequent fire alarm system upgrade. Who was ultimately responsible for integrating the generator, ATS, fire alarm system, and elevators?


"That's Not My Job" Mentality

Each trade is understandably focused on their specific area of expertise and potentially unwilling to venture into unknown territory.

2. What I Would Do (If I Were in Your Shoes)



Communication is Key

First, get on a call (or better yet, a video call) with the resort's management, their current electrician, the fire alarm contractor, and the elevator contractor. Clearly state your position.


Reiterate Your Original Scope

Remind them you installed the generator and connected it to the existing ATS based on the pre-existing infrastructure. The CAT6 runs were an accommodation to the fire alarm system upgrade, not part of the original generator installation.

Offer a Solution (for a Price)

"While this isn't strictly within my original scope, I understand the need to get this resolved. I am willing to come back and complete the connections, but it will be at my current hourly rate, plus travel expenses, materials, and a markup for project management. I'll need access to the wiring diagrams for the fire alarm system and elevator controls to ensure correct connections."


Clearly Define Deliverables

If you take on the work, clearly define what you will be doing. For example: "Connect CAT6 wires from ATS to fire alarm control panel and elevator control panel according to wiring diagrams provided by [Fire Alarm Company] and [Elevator Company]. Verify signal transfer and basic functionality with [Fire Alarm Company] and [Elevator Company]."

Get It in Writing

Don't start
anything without a signed change order or new contract outlining the scope, price, and responsibilities. This protects you later.

3. Determining Responsibility



In an Ideal World

The general contractor or the resort's project manager should have coordinated this integration from the start. They should have ensured all trades were on the same page and had the necessary documentation.

Realistically

Determining who
should be responsible at this point is less important than getting the work done correctly.

4. Finding the Information You Need



Wiring Diagrams (Critical)

The

absolutely essential
documents are the wiring diagrams for: The ATS (provided by the ATS manufacturer, or the generator manufacturer) The Fire Alarm Control Panel (provided by the fire alarm manufacturer or contractor) The Elevator Control System (provided by the elevator manufacturer or contractor) NFPA 72 (National Fire Alarm and Signaling Code)

This code will outline the requirements for generator/ATS interaction with the fire alarm system. Specifically, you'll want to understand any requirements for: Generator running indication to the fire alarm panel. Elevator recall functionality on generator start. Emergency Voice/Alarm Communication Systems (EVACS) power requirements.

NFPA 70 (NEC - National Electrical Code)

Article 700 (Emergency Systems), Article 701 (Legally Required Standby Systems), Article 702 (Optional Standby Systems) will be relevant. Also, verify the CAT6 is appropriate for this type of signaling, usually it has to have a higher fire rating.

Elevator Codes

You may need to consult the applicable elevator codes (likely based on ASME A17.1) to understand the required interaction between the fire alarm system and elevators. The elevator contractor should be providing this information.


ATS Manual

Consult the ATS manufacturer's manual for wiring diagrams, configuration settings, and any specific instructions for interfacing with fire alarm and elevator systems.

5. Texas Electrical Master License and Scope of Work



General Electrical Work

Yes, connecting low-voltage control wiring falls under the scope of your electrical master license in Texas,
as long as it's related to the electrical system (generator, ATS, etc.).

Fire Alarm Specific Work



Be cautious
. In Texas, fire alarm work requires a separate license. You can install the wiring, but the programming, testing, and commissioning of the fire alarm system must be done by a licensed fire alarm technician. You cannot troubleshoot the fire alarm panel itself. Elevator Control Work

You are unlikely to have the expertise to modify elevator controls.


Liability

This is a critical consideration. If you make an incorrect connection that damages equipment or causes a safety hazard, you could be held liable.

6. Why the Elevator Contractor May Be More Appropriate



Elevator Recall Functionality

The primary reason for the connection between the fire alarm system and the ATS is to trigger elevator recall in the event of a fire. This is typically an elevator control function. The elevator contractor is best positioned to understand the specific requirements of the elevator control system.


Proprietary Systems

Elevator control systems can be highly proprietary. The elevator contractor has the specialized knowledge and tools to interface with them safely and correctly.

7. Your Options and Recommendations



Option 1: Decline (Safest Option)

Politely decline the work, emphasizing that the integration is outside your original scope and that you're not a fire alarm or elevator specialist. Recommend they hire a qualified fire alarm/elevator integration contractor.


Option 2: Accept, But with Strict Conditions (Higher Risk, Higher Reward)



Clearly defined scope and price.
Require complete wiring diagrams and technical support from the fire alarm and elevator contractors. Limit your work to physical wiring only. Get written sign-off from the fire alarm and elevator contractors after they verify the connections are correct. Consult your insurance company

Discuss the potential liability implications with your insurance company before proceeding.


Option 3: Subcontract (Best Balance)

Consider subcontracting the actual termination and verification to a qualified low-voltage contractor who specializes in fire alarm/elevator integration. You would still manage the project and be responsible for the overall outcome, but you'd be leveraging the expertise of a specialist.

In Summary:


This is a complex situation with potential liability. Proceed with extreme caution. Focus on clear communication, well-defined scopes of work, and proper documentation. Don't be afraid to say "no" if you're not comfortable with the work. If you do take on the project, protect yourself with a detailed contract, require complete technical support, and consider subcontracting the integration work to a specialist.Good luck! Flag for review