Topic: MCP selection along with NEC and UL508A

User: Mehdi, Location: United States

Asked on: Thursday, August 29, 2024 at 3:45 pm EDT
Answered on: Thursday, March 6, 2025 at 1:52 am EST

Question: 10HP Motor name plate shows volts 230/460 -Amps 21.6/10.8. We requested 208V motor and manufacturer said it is compactable but due to some reason they can provide 208V/Amps information on motor name plate. We ran the motor on 208 and it was drawing 19.8 Amps. In the beginning of the project, we looked into NEC table and found 10hp motor full load amps 30.8 at 208 volts. we selected the breaker 30-42 amps. I was wondering why motor is taking same amps on 208 what are on nameplate for 230 volts. I was not sure if we met the UL508a and NEC code in a right direction. Kindly help me to understand and learn. Thank you.

Okay, let's break down this situation and address your concerns about the motor's performance and code compliance.

Understanding the Basics Motor Nameplate

The nameplate is the definitive source of information for the motor's rated characteristics. It tells you the voltage(s) the motor is designed for and the corresponding full-load amps (FLA).


Voltage and Current Relationship

Ideally, for the same horsepower output, decreasing the voltage increases the current draw. This is because horsepower (HP) is related to voltage (V) and current (I) (and power factor and efficiency). Roughly, HP ~ V I. If HP stays constant and V decreases, I must increase.

NEC Tables

NEC tables (like Table 430.250 in the US) provide approximate full-load currents for standard motors. They are used for initial sizing of conductors and overcurrent protection. Always prioritize the motor nameplate data over the table data if it's available.

UL508A

This is a standard for Industrial Control Panels. It dictates how the control panel (including the motor starter, overloads, and other components) must be designed and built to be safe and compliant.

Analyzing Your Situation
1. Manufacturer Statement

The manufacturer states that the 230/460V motor is "compatible" with 208V. However, not providing a 208V nameplate rating is a red flag. It means the motor is likely
not optimized for 208V operation. It may be underperforming or operating outside its intended design parameters. While it might work, it doesn't mean it's the best or most efficient solution.2.

Observed Current Draw

You observed 19.8 amps at 208V. This is lower than the 21.6 amps listed on the nameplate for 230V. The important question is, is it doing 10HP as designed.
3.


Why the Lower Current Draw?
Several factors could contribute to the lower-than-expected current draw: Reduced Load

The motor might not be fully loaded. If the application requires less than 10 HP, the current will be lower. This is the most common reason.

Overvoltage and Lower Load

The manufacturer might be using the 230V winding, resulting in a lower operating temperature and longer life.4.

NEC and UL508A Considerations



Motor Branch Circuit Overcurrent Protection

NEC 430 requires you to size the overload protection based on the motor's nameplate FLA. Since you don't have a 208V FLA on the nameplate, this is problematic. You might be able to use the 230V FLA (21.6 amps) as a conservative estimate, but you should document this decision and consult with a qualified electrical engineer or inspector.

Feeder Overcurrent Protection

The feeder conductors feeding the motor branch circuit are sized based on the sum of the motor FLA and other loads.


UL508A

The UL508A standard requires proper component selection and application based on the motor's nameplate ratings. Not having a 208V nameplate complicates UL508A compliance. The inspector might question the application and design.

Addressing Your Concerns and Next Steps
1. Verify the Load

Confirm that the motor is operating at its intended load. If the motor is lightly loaded, the current draw will be lower. Try to measure the actual output power of the motor.2.

Contact the Motor Manufacturer

This is the most important step.

Demand Clarification

Push them for a written statement or documentation explaining why they consider the motor "compatible" with 208V and how it impacts performance. Ask for specific data on expected FLA, horsepower output, and temperature rise at 208V.


Warranty

Clarify whether operating the motor at 208V voids the warranty, especially since it's not explicitly rated for that voltage.

Documentation

Ask for any documentation or test reports supporting their claim of 208V compatibility.3.

Consult with a Qualified Electrical Engineer

An engineer can analyze the motor's performance, review the application, and determine if the existing breaker and wiring are adequately sized and compliant with the NEC and UL508A. They can also advise on alternative solutions.4.

Overload Protection

The overload relay (part of the motor starter) protects the motor from overcurrent due to mechanical overload. You must size it properly based on the motor's nameplate FLA (or the
expected FLA at 208V, if you can get that from the manufacturer). Set the overload protection to the lowest setting above the motor's full load amp rating.5.

Consider a 208V Motor

If possible, the
best solution is to replace the 230/460V motor with a motor specifically rated for 208V. This ensures optimal performance, efficiency, and compliance.6.

Voltage Drop

Even though your current draw is less than the FLA listed on the nameplate, voltage drop should still be considered.

In summary:
Operating a motor at a voltage different from its nameplate rating can lead to reduced performance, efficiency, and lifespan. You need to verify the load, get documentation from the manufacturer about the motor's expected performance at 208V, consult with a qualified electrical engineer, and carefully consider NEC and UL508A requirements. Consider a 208V-rated motor for best performance and compliance.The lack of a 208V FLA rating on the nameplate is a significant issue. Document everything, get written confirmation from the manufacturer, and involve a qualified electrical engineer to ensure safety and compliance. Don't simply rely on the motor "working" at 208V. Flag for review