Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Transformer Fire Protection Barrier

User: ROHM, Location: USA

Asked on: Thursday, August 29, 2024 at 3:58 pm EDT
Answered on: Thursday, March 6, 2025 at 1:52 am EST

Question: We are looking to install a transformer fire barrier between two of our main incoming transformers (34.5 KV to 13.8V) at our substation that feed power to our facility. The fire barrier will be of a concrete masonry unit (CMU) type. There is a single containment for these two transformers and there is a cable tray that runs between the two transformers for protective relay controls. As a result of the tight distances between the transformers and the cable tray, the fire barrier (CMU) will be within 4 feet of the high voltage cables (34.5KV,13.8KV). The CMU will be grounded to the ground grid. The concern we have is that there is not enough distance between the barrier and the overhead transformer power lines and could cause an issue with there being a conductive path from the transformer lines through the fire barrier. Does anyone have any experience with this application and insight into if this setup is approved/allowed within NFPA70 and NFPA850 code?

You've raised a valid concern regarding clearances and potential hazards associated with placing a grounded CMU fire barrier in close proximity to high-voltage conductors. Let's break down the applicable codes and considerations.

NFPA 70 (National Electrical Code - NEC)



Clearances from Live Parts (Article 110)

This is the primary area of concern. The NEC mandates specific working clearances around energized equipment to ensure worker safety and prevent accidental contact.
Table 110.34(A) outlines nominal voltage to ground clearances to live parts. For 34.5kV, the minimum working clearance is dependent on the voltage range and whether it's a condition 1, 2 or 3. Condition 1 is exposed energized parts on one side and no grounded parts or grounded insulated parts on the other side. Condition 2 is exposed energized parts on one side and grounded parts on the other side. Condition 3 is exposed energized parts on both sides.

A 4-foot clearance may not be sufficient for 34.5kV, especially considering the CMU will be grounded. You MUST verify the required clearance using this table based on your specific voltage and conditions.
For 13.8 kV you would need to look at Table 110.31 for the clearances to live parts. The same principle apply to this table where you would need to verify the required clearance based on your voltage range and conditions. Grounding (Article 250)

The grounding of the CMU wall itself is good practice for safety and fault current paths. However, the grounding further emphasizes the importance of proper clearances. A grounded barrier significantly reduces the insulation provided by air.

Cable Trays (Article 392)

While less directly applicable to the barrier itself, ensure the cable tray's installation and grounding comply with NEC Article 392.

NFPA 850 (Recommended Practice for Fire Protection for Electric Generating Plants and High Voltage Direct Current Converter Stations)



Transformer Spacing and Fire Barriers (Chapter 12)

NFPA 850 provides guidelines for transformer spacing and the use of fire barriers. It often references the NEC for electrical clearances.

Containment

Since you have a containment area, NFPA 850's recommendations on drainage, oil spill control, and fire suppression systems become relevant.


Fire Resistance Ratings

NFPA 850 will specify the required fire resistance rating (in hours) for the CMU barrier based on the transformer size, oil volume, and separation distances to other assets.

Key Considerations and Recommendations


Clearance is Paramount

The most critical aspect is verifying that the 4-foot distance meets the minimum working clearances specified in NEC Article 110, specifically Table 110.34(A) (for 34.5kV) and Table 110.31 (for 13.8KV). These clearances are non-negotiable. Err on the side of caution and provide more distance if possible.
2.


Voltage Stress

While air can be an insulator, the high voltage stress near the conductors, combined with a grounded CMU wall, increases the risk of flashover or arcing.3.

Consult a Qualified Electrical Engineer



This is essential.
You need a licensed professional engineer experienced in high-voltage substation design to perform a thorough evaluation. This evaluation should include: Arc Flash Hazard Analysis

Determine if the presence of the grounded CMU wall alters the arc flash hazard.


Insulation Coordination Study

Assess the risk of overvoltage and insulation breakdown considering the close proximity of the grounded barrier.

Clearance Verification

Ensure
all clearances comply with the NEC and any applicable local codes.

Grounding System Review

Confirm the grounding system is adequate for fault current handling, given the additional grounded element.4.

Alternative Solutions (If Necessary)



Increase Distance

The simplest solution is to move the CMU wall further away from the conductors, if physically possible. This might require redesigning the containment area.


Partial Barrier with Increased Height

Instead of a full wall close to the conductors, consider a shorter wall positioned further back, but taller, to achieve the required fire resistance. This might require less footprint while providing adequate separation from the conductors.

Insulated Barrier

While expensive, consider using a barrier material that is fire-rated
and electrically insulated. This would mitigate the conductive path issue. You would still need to verify clearances but the risk would be significantly reduced.

Relocation of Cable Tray

Consider moving the cable tray to a different location.5.

Local AHJ (Authority Having Jurisdiction)

Discuss your plans with your local electrical inspector or building department before installation. They may have specific interpretations or requirements.

In summary, while a CMU fire barrier is a standard approach for transformer fire protection, its proximity to high-voltage conductors introduces significant safety concerns. Strict adherence to NEC clearance requirements, thorough engineering analysis, and consultation with the AHJ are crucial to ensure a safe and compliant installation.
Flag for review

Previous Question Next Question