Question: In 110.26(C) Entrance to and Egress from the Working Space for Large Equipment requiring an entrance/exit on each end of the working space if1) the equipment is over 6' wide and rated 1,200A or moreis this referring to a single piece of equipment or collectively? For instance, if a room has several equipment 10' wide but only rated 1,000A or if a room has several equipment 5' wide but each rated 2,000A, would either of these rooms need two entrance/exits?2) the equipment is the service equipment, is over 6' wide, and the sum of the service disconnects is 1,200A or more.is the width collectively or for a single service disconnect? For instance, if the sum of the service disconnects are 2,000A yet each service disconnect is less than 6' wide, would two entrance/exits be needed?
Let's break down 110.26(C) and address your questions
Key Points of 110.26(C) Regarding Entrance/Egress:
The rule is designed to ensure a safe and accessible escape route in case of an arc flash or other electrical incident, especially when working on or near energized equipment. It's about facilitating a quick and unobstructed exit.1. Equipment Over 6' Wide AND Rated 1,200A or More
This refers to a single piece of equipment. The language focuses on the equipment. If a single piece of equipment exceeds both the width and amperage thresholds, it triggers the dual entrance/egress requirement. Scenario 1 (Several pieces of equipment, 10' wide collectively, but each less than 1,200A)
No. If no single piece of equipment is both over 6' wide and rated 1,200A or more, then this particular part of the rule doesn't apply.
Scenario 2 (Several pieces of equipment, 5' wide each, but each rated 2,000A)
No. Again, no single piece of equipment exceeds the width requirement of 6', regardless of their amperage.
2. Service Equipment, Over 6' Wide, and Sum of Disconnects is 1,200A or More
Width refers to the single service equipment enclosure. The code states "Service equipment shall comply with this requirements" which indicates the width is to a single Service Equipment. Not the collective width of multiple pieces. The amperage rating refers to the sum of all service disconnects. Scenario (Sum of service disconnects is 2,000A, but each service disconnect is less than 6' wide)
In this case, a second means of egress is required. The code refers to "the sum of the disconnects" being 1200A or more. If the sum of disconnects is 2000A, that threshold has been met.
Summary of Scenarios1. Multiple Pieces of Equipment, Collectively >6' and Individually <1200A
No additional entrance/egress required, since no single piece of equipment is over 6 feet wide AND rated at least 1200A.2.
Multiple Pieces of Equipment, Collectively <6' and Individually >1200A
No additional entrance/egress required, since no single piece of equipment is over 6 feet wide AND rated at least 1200A.3.
Multiple Service Disconnects, <6' Wide each, but Sum of Amperage >1200A
Additional entrance/egress is required since the sum of the service disconnects are greater than 1200A.
Important Considerations
Clear Interpretation
When applying this rule, always prioritize safety and ensure clear, unobstructed egress paths.
AHJ Authority
The Authority Having Jurisdiction (AHJ) has the final say on code interpretation. Consult with your local inspector if you have any doubts or specific installation questions.
Disclaimer: I am an AI chatbot and cannot provide definitive legal or electrical code interpretations. This information is for general guidance only. Consult with a qualified electrical engineer or inspector for specific project requirements. Flag for review