Topic: Series rating combination

User: Tainted, Location: New York

Asked on: Friday, August 30, 2024 at 8:39 pm EDT
Answered on: Thursday, March 6, 2025 at 1:54 am EST

Question: I know in some circumstances you cannot combine series ratings.But what about this scenario, is this an exception:Fuse A = 300kAICFuse B = 200kAICBreaker C = 65kAICBreaker D = 65kAICFuse A and B are in series and feed breakers C and D as shown below. Let's pretend breakers C and D are in a standalone panelboard labelled red.A is series rated with C at 100kAICB is series rated with D at 100kAICA does not series rate with DB does not series rate with CIs it correct to say that the red panelboard is series rated at 100kAIC?

Yes, in the scenario you've described, it is generally considered correct to say that the red panelboard is series rated at 100 kAIC, assuming the listed series rating of 100kAIC is a UL listed rating. Here's why: Series Ratings are Specific

Series ratings are only valid for the exact combinations of devices tested and listed by a nationally recognized testing laboratory (NRTL) like UL. You've stated that A series rates with C and B series rates with D.


Independent Series Combinations

The fact that A and C are series rated, and B and D are series rated, allows you to take advantage of both ratings separately. You're essentially applying two independent series rating combinations.

Lower Value Governs

The weakest link in the chain determines the overall withstand rating. Since both series combinations (A with C and B with D) are rated at 100 kAIC, that becomes the effective withstand rating for the downstream equipment.

Therefore, because A and C are listed for a 100kAIC series combination AND B and D are listed for a 100kAIC series combination, you can claim a 100kAIC SCCR for that red panelboard.
Important Considerations & Caveats



Manufacturer's Listings are Crucial

The key is that you must have documentation from the equipment manufacturer(s) that clearly states the specific series rating of 100kAIC for the A/C and B/D combinations. This information is typically found in UL listings, product data sheets, or engineering letters.

Without this documentation, you cannot claim a series rating.
Specific Device Types & Models

Series ratings are very specific to the exact type and model of each device (fuses and breakers). A series rating for one model of a breaker does not automatically apply to another model, even from the same manufacturer.


Upstream Device SCCR

The SCCR of the upstream devices (fuses A and B) must be equal to or greater than the available fault current at their line terminals. While you've specified their AIC ratings are high (300kAIC and 200kAIC respectively), ensure that the available fault current at that point in the system is less than or equal to those values.

No Field Modifications

The series-rated system must be installed exactly as tested and listed. Any field modifications (e.g., changing the enclosure, adding components that weren't part of the tested combination) will invalidate the series rating.

In summary, your reasoning is correct
if* the specific devices have been tested and listed as a series combination with a 100 kAIC rating. Always verify and document the manufacturer's listings to support your claim.