Topic: Clearance Issue

User: Wizard, Location: New Orleans

Asked on: Friday, August 30, 2024 at 9:53 pm EDT
Answered on: Thursday, March 6, 2025 at 1:54 am EST

Question: Trying to figure the clearance requirements for a chiller.We need to wire in a chiller but when we got to the site the chiller was already set. There is only 24 inches for the electrical panel door to the wall. Also, the door will not fully open, it only opens at about 69 degrees.I told the customer the chiller needs to be moved to get 36 inches of clearance.Does the section 110 code apply to panels mounted on equipment such as chillers?Was I correct in telling them that o cannot do the electrical work until the chiller is moved.

You are correct to be concerned about the clearance and access to the electrical panel on the chiller. Here's a breakdown of why, and the relevant code sections

Yes, NEC 110.26 (or your local equivalent) Applies
Scope of the NEC

The National Electrical Code (NEC) applies to electrical installations in buildings and
other structures. While a chiller itself is equipment, the electrical panel mounted on it and the wiring connecting to it is subject to the NEC. The chiller isn't exempt just because it's a piece of equipment.

Intent

The primary purpose of the NEC is to ensure electrical safety. Safe access to electrical equipment for maintenance, troubleshooting, and operation is a critical part of that.

NEC 110.26: Spaces About Electrical Equipment
This section outlines the requirements for working space around electrical equipment that is likely to require examination, adjustment, servicing, or maintenance while energized. This definitely includes the electrical panel on a chiller.

Key Requirements from NEC 110.26 (Consider these factors)



Depth of Working Space (110.26(A)(1))

The depth of the working space in front of the electrical panel depends on the voltage to ground and the conditions opposite the working space. Even for lower voltage systems (e.g., 480V or less), you likely need at least 3 feet (36 inches). Condition 1 (exposed live parts on one side and grounded parts on the other side) is common. Condition 2 (insulated surface on one side) may apply in some cases and allow less clearance.

Width of Working Space (110.26(A)(2))

The working space must be at least 30 inches wide. This doesn't mean the panel
is 30 inches wide, but rather that you have a clear 30-inch-wide space centered on the electrical equipment.

Height of Working Space (110.26(A)(3))

The working space must be clear and extend from the grade, floor, or platform to the height specified in 110.26(E). Usually, this requires at least 6.5 feet of headroom, or the height of the equipment, whichever is greater.

Access and Entrance to Working Space (110.26(C))

This is
critical. This section addresses the need for clear and unobstructed access to the working space.

Adequate Access

The working space must allow ready and safe access to all electrical equipment.

Entrance Requirements

Entrances to the working space must be of sufficient area to permit unimpeded movement of equipment and personnel.

Why You Are Right to Refuse Work
1. Safety

Your primary responsibility is to ensure the safety of yourself and anyone else who might work on the equipment in the future. Working in a cramped space with limited access to the panel significantly increases the risk of electrical shock, arc flash, and other injuries. The 69-degree door opening makes safe operation and maintenance very difficult.2.

Code Compliance

You are responsible for ensuring that your electrical work complies with the NEC (or local electrical code). Connecting the chiller to a panel with insufficient clearance would be a code violation.3.

Liability

If you proceed with the work despite the code violation and a safety hazard exists, you could be held liable if someone is injured as a result.

What To Do
1. Document Everything

Take pictures of the existing conditions, including the limited clearance, the restricted door opening, and any obstructions.2.

Communicate Clearly (In Writing)

Provide your customer with a written explanation of the code requirements (referencing NEC 110.26) and the safety concerns. Explain that you cannot perform the electrical work until the chiller is moved to provide the required clearance.
3.


Offer Solutions

Suggest options to the customer, such as:
Moving the chiller to a location that provides adequate clearance. Modifying the surrounding structure (if possible) to create more space. Using a different chiller model or configuration that allows for proper clearance. (Less likely after installation, but possible).4.

Consider Inspection

Inform the customer that the electrical inspector is likely to require the chiller to be moved to meet code requirements.

In summary, you are absolutely correct to refuse to perform the electrical work until the clearance issues are resolved. Your priority should be safety and code compliance.