Topic: Damaged conductors in cramped boxes

User: Hitchum, Location: New York

Asked on: Saturday, August 31, 2024 at 8:53 am EDT
Answered on: Thursday, March 6, 2025 at 1:55 am EST

Question: Hey folks,I was replacing a smoke alarm on a job and noticed charred insulation on some conductors in the (overfilled) ceiling box, and evidence of some arcing. I pulled a nearby luminaire and found the same thing - box was overfilled and two conductors were charred with compromised insulation. Neither circuits were protected by AFCI.Curious to get folks thoughts on potential causes here, especially since these circuits are not carrying high loads. The cables are 12 AWG BX, originally installed in the early 90s, and were properly terminated (i.e., anti-short bushings were used). My best guess is that 30+ year old insulation has become brittle, and is easily cracked when bent or moved, which is made worse by the box overfill.Some photos attached...Neil

Okay, Neil, those photos definitely tell a story, and your assessment is a good starting point. Let's break down the likely causes and then discuss potential solutions.

Likely Causes Based on Your Description and Photos



Age and Brittle Insulation

You're right, this is a HUGE factor. 30+ years is a long time for electrical insulation, especially in attics or ceilings that experience temperature extremes. The insulation becomes brittle, dries out, and cracks easily. Movement (even minor) can then expose the conductor, creating a short or arc. BX cable
can last a long time, but the insulation is often the weak point.

Box Overfill

Absolutely exacerbating the problem. Overfilling a box puts stress on the conductors and their insulation. It forces them to be bent at sharper angles than intended, further cracking aged insulation. The box itself then doesn't allow for proper heat dissipation.

Loose Connections

While you say the terminations are good, it's worth
re-emphasizing this. Over time, screw terminals can loosen due to vibration, thermal expansion/contraction, and the general settling of a building. Loose connections create resistance, resistance generates heat, and heat degrades insulation even faster. This can lead to arcing at the terminal itself, spreading outward. Even though the terminations appear ok, it is worthwhile to inspect the tightness of the terminations.

Minor Overloads (Cumulative Effect)

You mentioned the circuits aren't heavily loaded. However, even "minor" overloads, repeated over many years, can slowly heat the conductors and contribute to insulation breakdown. Think about using a hair dryer on the same circuit every morning. The sustained load, even if not tripping a breaker, stresses the wiring over time.

Dust/Debris

Dust and debris accumulating in the boxes can act as insulators, trapping heat and further contributing to insulation degradation. The dust can also be conductive under certain humidity conditions, increasing the risk of tracking.


"Tracking" Across Deteriorated Insulation

Once insulation starts to break down, it can become more conductive, particularly in humid conditions. This can create a very low-level "tracking" current between conductors or between a conductor and the box. Over time, this tracking current can char the insulation and eventually lead to a more significant fault.

Rodent/Insect Damage (Less Likely, But Check)

While not as common with BX, check for signs of rodent or insect damage. Rodents sometimes chew on wiring, and insects can nest in boxes, introducing moisture and debris.


Original Installation Issues (Less Likely, But Possible)

Could the BX connectors be overtightened, cutting into the insulation where the cable enters the box? Was the original installation rushed, with too much force used to cram wires into the box? These are less likely after 30 years, but worth considering.

Why No AFCI Trip?
Arc Type

Standard breakers are designed to protect against
overcurrent situations (like a short circuit that draws a lot of amps very quickly). Older AFCI breakers are designed to protect against series arcing. The arcing you're seeing may be a lower-level parallel arc, especially initially. It takes a certain amount of arc current to trip even a AFCI breaker, and a slow degradation may not produce that.

Old Breakers

Breakers do age. Their sensitivity can decrease over time. A 30-year-old breaker might not be as responsive to a fault as a new one.

Recommendations/Solutions



AFCI Protection is Now Essential

Given what you've found, adding AFCI protection to these circuits (and potentially others in the house) is absolutely crucial. This is a safety upgrade that will provide far better protection against arcing faults, even if they're low-level.

This is the most important thing you can do.
Identify Extent of Damage

You need to thoroughly inspect all accessible boxes on these circuits, especially those in ceilings and attics. Look for any signs of discoloration, cracking, or charring.

Correct Overfilled Boxes

This is non-negotiable. You
must correct the overfilled boxes. This means: Adding larger boxes or using box extenders (if permissible by code in your jurisdiction). Carefully re-routing wiring to minimize stress on the conductors. Consider the use of wire connectors that are designed to fit in tight spaces.

Carefully Re-Terminate

Even if the existing terminations
look good, carefully disconnect, clean, and re-terminate all connections in the affected boxes. Use new, high-quality wire connectors (e.g., Wago lever nuts are often preferred for their reliability and ease of use). Ensure connections are snug.

Consider Pigtailing

If the conductors are short and difficult to work with, consider pigtailing new lengths of wire onto the existing conductors. This gives you fresh, flexible wire to work with and eliminates the need to bend brittle conductors excessively. Use properly sized and rated wire connectors for the pigtails.

Insulate Damaged Areas (If Full Replacement Isn't Possible)

If the damage is limited and localized, and you cannot easily replace the entire run of cable, you
might be able to carefully wrap the damaged section of the conductor with electrical tape after correcting the cause of the damage. HOWEVER, this is a temporary fix and not a substitute for proper repair. The tape may not be rated for the temperature of the conductors, and the conductors may continue to degrade.

Monitor Circuits

After making the repairs, monitor the circuits for any unusual behavior (e.g., flickering lights, warm outlets, strange smells).

Consider a Full Wiring Inspection

Given the age of the wiring and the extent of the damage you've found, it's prudent to recommend a full wiring inspection to the homeowner. This would involve a qualified electrician thoroughly examining the entire electrical system for potential hazards.

Important Safety Precautions



Turn Off Power

Always de-energize the circuit at the breaker before working on any electrical wiring.

Test Before Touching

Use a non-contact voltage tester to verify that the circuit is indeed dead before touching any wires.


Work Methodically

Take your time and be careful. Electrical work is not something to rush.*

Know Your Limits

If you're not comfortable with any of these tasks, hire a qualified electrician.

In summary:
This is a situation that needs careful attention. You've identified a significant safety concern. Prioritize AFCI protection and fixing the overfilled boxes. A thorough inspection and potentially a full rewiring might be necessary to ensure long-term safety. Flag for review

Previous Question Next Question