Topic: Ungrounded System Vs Corner Grounded System

User: wwhitney, Location: Berkeley, CA

Asked on: Saturday, August 31, 2024 at 12:16 pm EDT
Answered on: Thursday, March 6, 2025 at 1:55 am EST

Question: A 3P3W system can be either corner grounded or ungrounded. For the corner grounded configuration, we are allowed to use distribution equipment with 2 pole OCPD that only disconnects the ungrounded conductors.So suppose we have such a system, and change the supply from corner grounded to ungrounded, and add the necessary ground fault monitor. What new hazard exists with respect to the conductor without OCPD that didn't exist when that conductor was grounded?In other words, why aren't we allowed to designate one conductor of a ungrounded 3P3W system as "always wired straight through" and skip the OCPD on that one conductor? The same way we are allowed to treat the grounded conductor of any grounded system.[We could remove the 3 phase aspect of the question and just consider a 1P2W system with a voltage above 150V.]Cheers, Wayne

You've hit on a very subtle but crucial point in electrical safety and system design. Let's break down the hazard and why we can't simply designate a conductor as "always wired straight through" in an ungrounded system.

The Hazard Introduced by Ungrounded Operation

The key difference between a corner-grounded and an ungrounded system is the presence of a defined, predictable, and low-impedance path to ground in the corner-grounded system. When you remove the ground, you eliminate that immediate return path for a fault. This seemingly beneficial isolation introduces a dangerous scenario: Double Fault Hazard

In an ungrounded system, a
single ground fault will not trip a standard overcurrent protective device (OCPD). Instead, the first fault effectively raises the potential of the entire system relative to ground. The system voltage, which was balanced relative to ground in the grounded configuration, is now offset. The phase with the fault is near ground potential, but the other two phases are now at full line-to-line voltage relative to ground.

Here's the problem

A
second fault to ground on a different phase creates a line-to-line fault. This results in a very high fault current, limited only by the impedance of the conductors and the source. This second fault can now trip the OCPD... but only after a potentially dangerous interval. More concerning is the potential for both of these faults to be arcing faults, which may not trip an OCPD and can lead to fire.

Why We Can't Skip the OCPD


The reason we can't designate a conductor as "always wired straight through" in an ungrounded 3P3W system (or even a 1P2W above 150V) boils down to this "double fault" scenario:
No Protection Against Line-to-Line Faults

If you have no OCPD on one conductor, and a fault to ground occurs on one of the other conductors, then a second ground fault on the conductor with no OCPD will establish a line-to-line fault. Now, since that conductor has no protection, the fault is not limited by an OCPD. That is bad!

Potential for High Fault Current

Without an OCPD on
each phase, the maximum available fault current for a line-to-line fault is extremely high. This can cause:

Severe Equipment Damage

Wires can melt, insulation can fail, and equipment can explode.

Arc Flash Hazard

A high fault current creates a massive arc flash, which can cause severe burns or death.


Fire Hazard

Molten metal and burning insulation can easily ignite nearby materials.

Grounded Systems vs. Ungrounded Systems and OCPD Requirements


In a grounded system, the grounded conductor is normally allowed to be wired straight through (with specific exceptions, like switched neutrals). This is because the system is designed to ensure that a single fault from an ungrounded conductor to ground will immediately trip an OCPD. The grounded conductor provides a low-impedance path for the fault current. Even if we were to fault to ground on the grounded conductor, no current will flow (or very little, depending on the size of the grounding electrode conductor).

Ground Fault Monitoring

Adding a ground fault monitor to an ungrounded system alerts you to the first fault to ground. It does not eliminate the hazard of the second fault. The monitor ideally triggers an alarm, so you can find and fix the fault before a second one occurs. It can also be used to trip a main breaker (although this can cause unwanted downtime in some applications).

In Summary

The absence of an OCPD on any conductor in an ungrounded system removes a critical layer of protection against line-to-line faults that can occur after a ground fault develops on another conductor. The double-fault scenario creates a situation where the "unprotected" conductor can carry extremely high fault currents, leading to severe safety risks. That is why OCPDs are generally required on every phase in an ungrounded system. Flag for review