Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Power Distribution Block

User: JZE14, Location: Montana

Asked on: Monday, September 2, 2024 at 11:51 am EDT
Answered on: Thursday, March 6, 2025 at 1:56 am EST

Question: I am installing a 1000A 460V service, but I am having trouble finding a power distribution block that will work with the wires I need. The utility company is supplying this service with 3-350 MCM wires. I need to supply an existing 600A main and will be adding a 400A disconnect. I can't seem to find a power distribution block that is big enough for this. Any help would be appreciated.

Okay, this is a common challenge when dealing with large services and multiple disconnects. You're running into the issue of accommodating the required wire sizes for both the incoming utility feed and the multiple outgoing conductors within a relatively compact space. Here's a breakdown of the problem and some solutions

Understanding the Issue
Ampacity Requirements

You need a system that can handle 1000A total.


Incoming Conductors

3 x 350 MCM conductors per phase (or neutral).

Outgoing Conductors

Cables to a 600A disconnect and cables to a 400A disconnect. This typically means you need to land
multiple smaller conductors per phase on the load side to achieve the required ampacity for each disconnect.

Space Constraints

Panelboards and disconnects have limited space for large distribution blocks and multiple conductors.

Possible Solutions
1. Multiple Power Distribution Blocks in Combination

This is often the most practical and cost-effective approach. Instead of searching for one giant block, break the load distribution into smaller sections.

Layout



Input

A distribution block large enough to accept (3) 350 MCM conductors for each phase/neutral.


Outputs

Multiple smaller distribution blocks connected to the output of the main input block. These smaller blocks would have the correct number and size of connections to feed the 600A and 400A disconnects.

Example



Main Input Block

A block that can accept (3) 350 MCM conductors on the input. Search for distribution blocks rated for at least 1000A.

600A Disconnect Output

A block or blocks that can accept multiple conductors adding up to a 600A rating. You might use (3) 3/0 AWG conductors or similar.


400A Disconnect Output

A block or blocks that can accept multiple conductors adding up to a 400A rating. You might use (2) 3/0 AWG conductors or similar.2.

Using a Busbar System

A busbar system is more of a custom-engineered solution, but provides greater flexibility.

Layout

A main busbar is installed in the panel. The utility conductors connect to the busbar. Taps are made from the busbar using appropriately sized connectors to feed the 600A and 400A disconnects.

Pros

Very flexible, easily expandable, and handles very high currents.


Cons

More expensive, requires careful design and installation, takes up more space.3.

Parallel Conductors Directly to Disconnects (With Caution)

In some cases, you can use parallel conductors directly from the utility conductors to the disconnects.

Layout

The 350 MCM conductors are split to feed both the 600A and 400A disconnects without using distribution blocks.

Important Considerations

This MUST comply with NEC Article 310.10(H). Parallel conductors MUST be the same length, same conductor material, same size, same insulation type, and terminated in the same manner. This is critical for proper current sharing. This can become very messy with large conductors and difficult to install properly. It may not be practical in many situations due to space constraints and the difficulty of routing the conductors. Using correctly sized wire and lugs.4.

Consult with a Electrical Supply House / Distributor

A knowledgeable electrical supply house can be invaluable. They can help you select appropriate distribution blocks, busbar systems, connectors, and other hardware that meets your specific requirements and local codes. Provide them with the ampacity, conductor sizes, and the layout of your system.

Important Considerations and Best Practices



NEC Compliance

Ensure ALL wiring and connections comply with the National Electrical Code (NEC) and any local amendments. Pay close attention to conductor ampacity (NEC Table 310.16), termination requirements, and bonding/grounding.

Conductor Sizing

Double-check your conductor sizing calculations. 350 MCM is a common size for 1000A, but ensure it meets the specific conditions of your installation (temperature rating, ambient temperature, etc.). You might need larger conductors for certain applications.


Termination Torque

Properly torque ALL connections to the manufacturer's specifications. Loose connections are a major cause of electrical failures. Use a calibrated torque wrench.

Clearance and Working Space

Ensure adequate clearance and working space around the equipment, as required by the NEC.


Enclosure Size

Make sure the enclosure (panelboard or other enclosure) is large enough to accommodate the distribution blocks, conductors, and required bending radii.

Professional Installation

This type of installation is complex and potentially dangerous. It should be performed by a qualified and licensed electrician.

Example using Option 1 (Multiple Distribution Blocks)

Let's assume you choose the route of multiple distribution blocks:1.

Main Input Block

Search for a distribution block rated for 1000A (or slightly higher). It should have the capacity to accept (3) 350 MCM conductors for each phase and neutral. This block would also have multiple output terminals to feed the next set of distribution blocks.2.

600A Disconnect Distribution

You need to provide 600A. A common solution would be to run (3) 3/0 AWG conductors per phase/neutral. Select a distribution block (or blocks) that can accept the output of the main input block and provide (3) outputs for 3/0 AWG conductors.3.

400A Disconnect Distribution

You need to provide 400A. A common solution would be to run (2) 3/0 AWG conductors per phase/neutral. Select a distribution block (or blocks) that can accept the output of the main input block and provide (2) outputs for 3/0 AWG conductors.

Where to Find Distribution Blocks



Electrical Supply Houses

Your local electrical supply house is the best place to start. They can show you a variety of distribution blocks and help you select the correct ones.


Online Distributors

Companies like Grainger, Platt Electric, Graybar, and McMaster-Carr carry a wide selection of distribution blocks. Search using terms like "power distribution block," "terminal block," "multi-tap connector," and specify the amperage and conductor size requirements.*

Manufacturer Websites

Check the websites of manufacturers like Panduit, Ilsco, Marathon Special Products, and Eaton.

Recommendation:


I strongly recommend starting by contacting a reputable electrical supply house in your area. They can guide you through the options, provide accurate pricing, and ensure you're using components that are compatible and code-compliant. They can also help you with wire and lug selection.Good luck with your installation! Remember safety first. Flag for review

Previous Question Next Question