Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: J Hooks

User: Sparky774, Location: Meriden, CT

Asked on: Monday, September 2, 2024 at 2:20 pm EDT
Answered on: Thursday, March 6, 2025 at 1:56 am EST

Question: I have a Generator installation that leaves no room to run Conduit or fasten to walls or Ceilings. I installed Caddy J Hooks hanging 6" below joists every 32". I installed my SER Cable (100 Amp) thru the hangers. I now need to run my control cable (1/2" Carflex) thru the caddy J Hooks. I used Cat 32, 2". I asked a friend who is also a Licensed Contractor and a B1 building official and he seems to think its fine considering the situation. The town I am doing this install is very technical and typically won't let anything slide. I just can't find where the J Hooks would be an approved NEC system for this install. There is plenty of head room and I am higher than the lowest duct............. Any advice would be appreciated....

Okay, let's break this down and look at the relevant NEC considerations, then offer some advice.

Understanding the Problem

You've used Caddy J-Hooks, which are commonly used for low-voltage cabling (data, telecom, etc.), to support both SER cable (Service Entrance cable, a higher voltage/amperage power cable) and flexible conduit containing control wires. The challenge is determining if this meets NEC requirements, especially in a jurisdiction known for strict enforcement.

Relevant NEC Sections and Considerations

Here's what the NEC likely covers for your specific situation: 300.11 Securing and Supporting

This is the
big one. It mandates how wiring methods must be supported.

(A) Secured to Structure

"Wiring methods shall be securely fastened in place." J-hooks can be a means of secure fastening, but often the listing of the J-hook itself and how it's used determine if it's appropriate for a particular wiring method.

(B) Raceways and Cables Supported from Suspended Ceiling Assemblies

This section applies to wiring above suspended ceilings, which is similar in concept to what you are doing beneath the joists, so we can look to it for guidance. It emphasizes the use of dedicated supports and independent support from the ceiling structure. You could potentially argue by analogy that your support system should provide a similar level of independence and reliability.


310.15 (formerly 310.16) Ampacities for Conductors

You need to ensure your SER cable is properly sized and installed.

338.10 Uses Permitted

This section addresses the use of SER cable itself. It outlines where SER cable can be used, and is generally permitted for branch circuits and feeders.


348.30 Securing and Supporting

This section specifically addresses Flexible Metal Conduit (FMC - Carflex). It will detail the requirements for supporting this type of conduit. Commonly, this is every 4.5 feet and within 12 inches of boxes, conduit bodies or other conduit terminations.

Article 725 Class 2 and Class 3 Remote-Control, Signaling, and Power-Limited Circuits

This applies to your control cable
if it's a Class 2 or Class 3 circuit, which it likely is. You still need to ensure proper installation and separation from power conductors as needed.

Key Issues & Concerns
1. Listing and Intended Use of J-Hooks

This is the MOST critical point. J-hooks are generally listed for low-voltage communication cables, not for power cables or conduit. Check the manufacturer's specifications and markings on the J-hooks themselves. They must be listed for the type of cable or conduit you're supporting, and for the weight it will bear. If the J-hooks are only listed for low-voltage cables, you are in violation. Using them for SER cable or even conduit containing power wires is likely a code violation. The Caddy CAT 32 is rated for low voltage cable and low voltage only.2.

Support Intervals

Even
if the J-hooks were appropriately listed, 32" intervals might be too wide for the Carflex, depending on the trade size. Check NEC 348.30.
3.


Securely Fastened

"Securely fastened" implies a robust, reliable connection that won't easily come loose or allow the cable/conduit to sag excessively. The inspector could argue that simply laying the cables in J-hooks doesn't meet this standard, particularly for heavier SER cable.4.

Separation of Power and Low-Voltage

While this may not be a strict
separation issue (putting them in separate raceways), the NEC generally favors physical separation of power and low-voltage wiring to minimize interference and potential hazards. Sharing the same J-hooks raises the question of whether this adequately addresses that concern.5.

AHJ (Authority Having Jurisdiction) Approval

Ultimately, the local inspector has the final say. Even if you can make a technical argument for your installation, if they're not convinced, you'll have to make changes.

Recommendations
1. Consult the Manufacturer's Specifications

Find the documentation for the Caddy J-Hooks you used.

Specifically look for

What types of cable/conduit are they listed for? What is the maximum weight they are rated to support? Are they listed for use with SER cable or conduit containing power conductors? Do they have specific installation instructions or limitations?2.

NEC Compliance Review

Double-check NEC 300.11, 338.10, 348.30, and Article 725 (if applicable) to ensure every aspect of your installation meets the requirements. Pay close attention to support intervals and secure fastening.
3.


Consider Alternative Support Methods

If the J-hooks are not approved for your application, you'll need to replace them with something that is. Some alternatives to consider (depending on space and accessibility) include:


Cable Tray

A small cable tray system specifically designed for power cables and conduit.

Conduit Clamps/Straps

Secure the SER cable and Carflex directly to the joists using appropriate conduit clamps or straps (if the joists are accessible and suitable for fastening).


Conduit Hangers

Use conduit hangers designed for suspending conduit from structural members.

Combination of Methods

Use a combination of methods for different cable/conduit types.4.

Talk to the Inspector
Before Inspection

The best approach is to proactively discuss your installation with the local electrical inspector
before they come out for the formal inspection. Explain your situation, show them the J-hook specifications, and be prepared to justify your approach. If they raise concerns, be willing to work with them to find a solution that meets code and their requirements. Providing documentation and a clear explanation of your reasoning can go a long way. This is especially important in a "technical" jurisdiction.5.

Document Everything

Keep copies of all product specifications, manufacturer's instructions, and your calculations. This will be valuable if you need to defend your installation to the inspector.

In Summary


While your friend might think the installation is "fine," NEC compliance is paramount. The key is the
listing and intended use* of the J-hooks. If they're not listed for the specific application, you'll need to find an alternative support method that is. Proactive communication with the electrical inspector is highly recommended. Good luck! Flag for review

Previous Question Next Question