Question: I took the nec special electrician exam and one of the questions on there was something along the lines of. How often should an underground conduit be grounded, every 50ft, 100ft, 500ft, 1000ft. Im struggling to find the answer in the code book. Can someone help me out, thanks!
You're right, that's a tricky question! The NEC doesn't specifically mandate grounding intervals for underground conduit in the same way it does for, say, grounding electrode conductors. Instead, the focus is on ensuring the equipment grounding conductor (EGC) within the conduit is properly installed and effective.Here's the breakdown of why the question is difficult and how to approach it: Conduit is considered grounded if in direct contact with earth
Metal conduit buried in direct contact with the earth is considered to be grounded through that direct contact with earth.
NEC focuses on EGC
The primary concern in the NEC is the effectiveness of the Equipment Grounding Conductor (EGC) that runs inside the conduit. The EGC's purpose is to provide a low-impedance path for fault current back to the source, tripping the overcurrent protective device.
NEC 250.4(A)(3) and (A)(5)
"Electrical continuity and the capacity to conduct safely any fault current likely to be imposed on it" are the key principles.
NEC 250.96(A) Bonding Other Enclosures
Metal enclosures, including metal conduits, are bonded to the EGC so that any potential on the metal will cause the OCPD to operate.
Conduit Body as a Grounding Jumper
Conduit bodies are allowed to be used as a grounding jumper as long as they meet the requirements of 250.92(B).
Why the Question is Misleading (Potentially)
Direct Burial Grounding
If the conduit is metallic and in direct contact with the earth, it is effectively grounded continuously. Additional grounding electrodes at regular intervals are generally NOT required solely for the conduit itself.
Plastic Conduit
If the conduit is non-metallic (PVC), there is no need to ground the conduit because it is non conductive.
How to Think About It (For Exam Purposes)
Consider the Context
The question probably isn't about grounding the conduit in the traditional sense (driving ground rods). It's more likely about ensuring the conduit is effectively part of the grounding path.*
Look for Related Articles
If I had to hazard a guess on a specific code section the exam writers may have had in mind, I would look into grounding and bonding requirements for other parts of the system that might influence the conduit's grounding (e.g., service entrance, separately derived systems).
In Summary
There is no article in the NEC that requires periodic grounding of underground metal conduit. Flag for review