Topic: Pool lift disconnect

User: hhsting, Location: Glen bunie, md, us

Asked on: Tuesday, September 3, 2024 at 2:15 am EDT
Answered on: Thursday, March 6, 2025 at 1:57 am EST

Question: I have outdoor pool that has pool lift. Would NEC 2017 Article 680.13 maintenance disconnect apply to pool lift or not?

NEC 2017 Article 680.13, Maintenance Disconnecting Means, specifically applies to permanently installed swimming pool recirculating pump motors. A pool lift is not a recirculating pump motor.Therefore, NEC 2017 Article 680.13 does NOT apply to a pool lift.

However, you are not entirely out of the woods with electrical code requirements for the pool lift. You should consider the following: 680.26 (Equipotential Bonding)

This is crucial. You need to ensure the pool lift is properly bonded to the pool's equipotential bonding grid. This is vital for safety. The metal parts of the lift within reach of a person in the pool must be bonded.


680.22 (Lighting, Receptacles, and Equipment)

If the pool lift is cord-and-plug connected, any receptacles that supply it should be GFCI protected. Consider the placement of the pool lift in relation to the distances outlined in 680.22(A) for lighting and receptacles.

680.43 (Storable Swimming Pools)

While your pool isn't storable, the code addresses many aspects of these types of pools. Because your pool lift is providing assistance to people with disabilities, you need to make sure it meets all ADA standards for accessibility.


Manufacturers Instructions
: Always consult the pool lift manufacturer's instructions for specific electrical requirements. They may have specific recommendations that go beyond the NEC.* Local Codes: Your local jurisdiction may have amendments to the NEC or additional requirements. Always check with your local electrical inspector.In summary, focus on proper equipotential bonding of the pool lift and GFCI protection for any cord-and-plug connected power supply. Consult the manufacturer's instructions and local codes for complete compliance. You will want to engage a qualified electrician. Flag for review