Question: aluminum xhhw wire size for 200 amp service .referance 310.12 a,b, states the service feeder shall not be less than 83 percentof the service rating.therefore 200x.83=166 ampsso use 4/0 xhhw ?
You're on the right track! Let's break down the calculation and the code references to be absolutely sure.1. Your Calculation
200 amps (service rating) 0.83 = 166 amps. This is correct.
2. NEC 310.12(A) This section does allow for a reduction in size for service conductors supplying an entire dwelling unit. This reduction is based on the 83% factor you've calculated. Crucially, you can only use this section for single-family dwellings, not apartments, commercial buildings, or other types of occupancies.3. Aluminum XHHW Ampacity
According to NEC Table 310.16 (which is the standard table for ampacity of conductors rated 0-2000 volts, typically installed in raceway or cable), 4/0 Aluminum XHHW is typically rated for
180 amps at 75°C. Since that is greater than 166 amps that would be acceptable You must use the correct temperature rating column from Table 310.16 based on the terminations on your equipment (circuit breakers, service disconnect, etc.). Typically, terminations are rated for 75°C, so that's the column to use. If your terminations are only rated for 60°C, the ampacity of 4/0 aluminum will be significantly lower (only 150A), and it would be insufficient.4. Important Considerations and Where You Might Need to Increase Wire Size
Voltage Drop
Even if 4/0 aluminum meets the ampacity requirements, you must consider voltage drop. Longer runs of wire will have more voltage drop. Excessive voltage drop can damage equipment and cause lights to dim. Voltage drop calculations are essential, especially with aluminum conductors, which have higher resistance than copper.
Terminations
As mentioned above, make sure that the terminations for the wire (breaker, lugs, etc.) are rated for the same temperature as the wire.
Parallel Conductors
You cannot parallel conductors smaller than 1/0 AWG.
Oversizing for Future Load
It's often a good idea to slightly oversize service conductors to accommodate future load growth. It's much cheaper to do it now than to replace the service later.
Local Amendments
Your local electrical code might have amendments to the NEC that affect wire sizing. Always check with your local building department or inspector.
5. Summary and Recommendation Based on your calculation and the 83% rule in 310.12(A), 4/0 aluminum XHHW, rated for 180 amps, appears to be sufficient for a 200 amp service for a single-family dwelling assuming 75C terminals are used. However, you MUST still
Confirm the temperature rating of your terminations. Perform voltage drop calculations. Check for local amendments to the NEC.* Consider future load growth and whether oversizing is prudent.Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. This information is for educational purposes only and should not be used as a substitute for consulting with a qualified and licensed electrician. Electrical work can be dangerous, and it's essential to follow all applicable codes and safety regulations. Flag for review