User: Greg1707, Location: Alexandria, VA

Asked on: Tuesday, September 3, 2024 at 11:25 am EDT
Answered on: Thursday, March 6, 2025 at 1:57 am EST

Question: A customer contacted me about their dryer vent. While cleaning the vent the technician was shocked. I checked with a non contact voltage tester and there was indeed current on the vent as well as the dryer frame. I found the cord had been installed incorrectly. The strap from the green screw to the neutral had been removed and the equipment ground on the cord had been connected to the neutral screw. I moved the equipment ground to the green screw and all is well.So, it appears as it was installed the appliance frame was not bonded. Would we expect the incorrect installtion would lead to current on the frame?

Yes, you would absolutely expect that incorrect installation to lead to current on the dryer frame and vent. Here's why: Normal Operation Leakage

Even in a perfectly functioning appliance, there's a small amount of leakage current from the ungrounded (hot) conductor to the chassis due to capacitive coupling. This is normal and is why grounding is so important.


Path of Least Resistance

With the ground wire connected to the neutral screw, the leakage current (and potentially fault current) would attempt to return to the service panel through the neutral. However, there are parallel paths! Some of that current would choose the dryer vent system (which is usually metal and in contact with the metal frame) to get back to ground, especially if there's any impedance in the neutral path.*

Why the Voltage Tester Alarms

A non-contact voltage tester detects the electric field created by voltage differences. When you have current flowing through the frame and vent, even a small amount, it creates a measurable voltage difference between the frame/vent and true ground, triggering the tester.

In Summary

By connecting the equipment grounding conductor to the neutral, you essentially floated the frame of the dryer at some voltage above ground potential. This is a dangerous situation, as it can lead to electric shock if someone touches the dryer frame while simultaneously touching a grounded object (like a water pipe or another appliance).

The correct installation:
Connecting the equipment grounding conductor (the green wire) to the dryer frame (the green grounding screw) provides a low-impedance path for fault current to flow back to the service panel, tripping the breaker or blowing the fuse. This disconnects the circuit and prevents a sustained shock hazard. Flag for review