Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Ground rod is only means of grounding

User: megawatts52, Location: clearfield

Asked on: Tuesday, September 3, 2024 at 10:59 pm EDT
Answered on: Thursday, March 6, 2025 at 1:58 am EST

Question: i have a question. doing a 5 bank meter 400 amps. this is in existing building, a tree fell on part of the building where the electrical equipment was. their is no water pipe that's metallic. no way to ground the footers. so i do know i must install the ground rods 2 of course. since the largest ungrounded conductor size id 500 kcmil al, i know the conductor forr the grounding is a 1/0. code says no larger than #6 to ground rods. my question is will it hurt to make the ground rods as the mail grounding and use the 1/0, or to do as the code says? thank you.

Okay, let's break down this scenario and address your question. You have a 5-gang meter bank for a 400A service, a 500 kcmil aluminum service conductor, and an existing building with no metallic water pipe and inaccessible footers.Here's a summary of your understanding and the applicable code: Service

400A, 5-gang meter bank.


Service Conductor

500 kcmil Aluminum.

Grounding Electrode System

Two ground rods (minimum).


Main Grounding Conductor (Grounding Electrode Conductor - GEC)

Per NEC Table 250.66, for 500 kcmil Aluminum, you correctly identified 1/0 Copper as the required GEC size.

Ground Rod Connection

NEC 250.66(A) requires that the portion of the GEC that is the sole connection to the ground rod(s)
never be required to be larger than #6 copper.

Your Question Rephrased

You're asking if it's
permitted or beneficial to run the 1/0 copper GEC directly to the ground rods, even though code allows a #6 copper wire for the portion connected to the ground rods.

The Answer

It's
not permitted to connect the 1/0 copper GEC directly to the ground rods. Here's why, and how you should do it according to the NEC:1.

Code Compliance

NEC 250.66(A) specifically allows you to reduce the size of the GEC where it connects to the ground rods. This is
not a suggestion; it is a limitation. The code is explicitly saying you can use #6 (or larger) for the portion connected to the ground rod(s) and #1/0 for the rest of the run.2.

How to Properly Install it

Run your 1/0 copper GEC from the neutral bus in the meter bank. Connect it to a listed and labeled split bolt or a similar suitable connector (wire nut is NOT suitable) Run a #6 copper conductor from that connector to each ground rod. Use approved clamps to bond the #6 conductor to the ground rods.

Why the Code Allows the Reduction

The current-carrying capacity of the GEC is primarily for fault current, and the ground rods' primary purpose is to provide a low-impedance path to earth for that fault current. A #6 copper conductor is deemed sufficient to handle the current that the ground rods can effectively dissipate into the earth. Increasing the size will make little difference in that regard.

Will it Hurt to Use 1/0 Directly?
Technically, yes. The code is being violated, which opens you up to red tags/rejection by the inspector. Practically, no. It will make no noticeable performance difference in most situations. But, that does not make it code-compliant. Cost

Significantly more expensive using 1/0.

Important Considerations



Accessibility

Make sure your ground rod connections are accessible for inspection.


Other Grounding Electrodes

In this case you can add more ground rods to enhance this type of system.

In conclusion, follow the code requirement to use a #6 copper conductor for the portion of the GEC that connects to the ground rods. It's code-compliant, cost-effective, and doesn't compromise the safety or effectiveness of the grounding system. Install the system as described above.
Disclaimer: I am an AI Chatbot and not a licensed electrician. This information is for general guidance only and should not be considered professional advice. Always consult with a qualified electrician and refer to the latest edition of the National Electrical Code (NEC) and local codes for specific requirements in your area. Flag for review

Previous Question Next Question