Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 90 degree column

User: Choice_Gorilla, Location: New England

Asked on: Wednesday, September 4, 2024 at 8:24 am EDT
Answered on: Thursday, March 6, 2025 at 1:59 am EST

Question: Maybe a stupid question but is there ever a situation where wire can be sized using the values in this column? I was always under the impression I could use it for derating purposes but when it came to actually sizing wire I was to use the 75 or 60 degree column. I’ve got an engineer telling me I can use the 90 degree column because I’m terminating directly to bus bar with 90 degree rated lugs or crimps. Never sized wire this way so it seems wrong. I’m not one to argue unless I can back it up with code references. If it matters, one side is a MCC and the other is a large motor. I can’t find anything on either that has a temperature rating.

You're right to be cautious. Using the 90°C ampacity column for wire sizing requires very specific conditions to be met, and it's often misinterpreted. Here's a breakdown of when you can use the 90°C column, when you can't, and why your engineer's rationale may or may not be valid

When You CAN Use the 90°C Column (with strict caveats):
Ampacity Calculation ONLY for Derating/Adjustment

The 90°C ampacity column is primarily used as a starting point for derating and adjustment calculations (like ambient temperature correction or multiple conductors in a raceway). You start with the 90°C ampacity, apply the derating factors, and
then you must ensure that the final, adjusted ampacity doesn't exceed the ampacity values found in the 75°C or 60°C column, depending on the termination temperature ratings.

Continuous Load is 100 Amps or Less

Table 310.16 has certain conditions that can override this.

Specific Equipment Approvals

Some equipment manufacturers may specifically list that their equipment is suitable for connection to conductors rated at 90°C, and
only then can you utilize that rating for the conductor sizing.

When You CANNOT Use the 90°C Column for Wire Sizing (the most common scenario)



Termination Temperature Limitations

NEC 110.14(C)(1) is the crucial section. It generally requires conductors to be selected and installed such that their ampacity does not exceed the lowest temperature rating of any connected termination, conductor, or device. This is often the limiting factor.

110.14(C)(1)(a)

For equipment rated 100 amps or less, or marked for 14 AWG through 1 AWG conductors, you must use the 60°C ampacity column (unless the equipment is specifically listed and marked otherwise).


110.14(C)(1)(b)

For equipment rated over 100 amps, you must use the 75°C ampacity column (unless the equipment is specifically listed and marked otherwise).

Analyzing Your Engineer's Rationale

Your engineer is arguing that because you're terminating directly to a bus bar with 90°C-rated lugs or crimps, you can use the 90°C ampacity column. Here's why that might be flawed:1.

MCC and Motor Temperature Ratings

You're right to question this. The most common limiting factor is the termination temperature rating of the MCC and motor. If the MCC or motor isn't specifically marked as being suitable for 90°C terminations, you must use the 75°C column (if the equipment is over 100A) per 110.14(C)(1)(b). It doesn't matter that the lug is rated for 90°C; the weakest link determines the overall rating. The MCC could have a main breaker rated at 75°C, the motor could be marked for 75°C, or anything else.
2.


Bus Bar Itself

While the lug may be rated for 90°C, what about the bus bar material in the MCC? It could have a lower temperature rating.3.

Manufacturer's Instructions

You MUST follow the manufacturer's instructions for the MCC and motor regarding conductor termination temperature ratings. These instructions will take precedence.

How to Verify and Justify


Inspect the Equipment

This is the most important step.



MCC

Look for markings inside the MCC (on breakers, starters, etc.) that specify the conductor termination temperature rating. Look at the MCC's nameplate data. It should be listed there.


Motor

Check the motor nameplate and motor terminal box for termination temperature ratings.

Lugs/Connectors

Ensure the lugs and connectors are UL-listed and suitable for the conductors you're using. Verify the temperature rating of the lug.


Manufacturer's Documentation

Obtain and review the manufacturer's specifications and installation instructions for both the MCC and the motor. This will often contain critical information about termination temperature ratings.2.

Document Everything

Keep a record of your findings, including photographs of nameplates and manufacturer's documentation.3.

Code References to Back You Up



NEC 110.14(C)

This is the primary code section governing termination temperature limitations.


NEC 310.15(B)(1)

This section explains the general rules for conductor ampacity and refers back to 110.14(C).

NEC Table 310.16

The ampacity table itself.

In summary

Unless you can
definitively prove that both the MCC and the motor are specifically designed and marked for 90°C terminations, you must use the 75°C ampacity column for conductors connected to equipment rated over 100 amps per NEC 110.14(C)(1)(b). Just because the lugs are 90°C-rated doesn't override the limitations imposed by the equipment's temperature rating.

Recommend:
*Respectfully ask your engineer to provide documentation and manufacturer's specifications showing that both the MCC and the motor are approved for 90°C terminations, otherwise you will have to size it with the 75 degree column to comply with NEC 110.14(C)(1)(b). Flag for review

Previous Question Next Question