User: new-master, Location: MARYLAND
Asked on: Wednesday, September 4, 2024 at 9:02 am EDT
Answered on: Thursday, March 6, 2025 at 1:59 am EST
Question: I got a call from Customer who said that their transformers going bad and it’s not putting out the 208v as it should only 193vBut also the room temperature really warm about 95°F top of transformer enclosureThere are three water heaters & a furnace in this room.Could the heat be the cost of the voltage drop.I put a fan on the transformer and the voltage has risen 200volts and temperature above transformer enclosure 93.5°FUtility voltage coming in each phase is 267-269vA-B= 463vB-C= 463vA-C= 468vPlease help what should I do on this situation?
Okay, let's break down this situation and figure out the next steps. It sounds like you're on the right track with your initial observations.
Summary of the Problem
Low Output Voltage
The transformer is only outputting 193V instead of 208V.
High Temperature
The top of the transformer enclosure is at 95°F.
Voltage Improvement with Fan
Adding a fan has increased the output voltage to 200V and slightly decreased the temperature.
High Incoming Voltage
Incoming voltage to the transformer is within normal range.
Heat Sources
The room contains water heaters and a furnace, contributing to the high ambient temperature.
Analysis
The evidence strongly suggests that
heat is contributing significantly to the voltage drop. Transformers are less efficient at higher temperatures. Here's why: Increased Resistance
Higher temperatures increase the resistance of the copper windings in the transformer. This increased resistance leads to greater voltage drop under load.
Core Losses
Elevated temperatures can also increase core losses in the transformer, further reducing its efficiency.
Capacity Reduction
Transformers are typically rated with a certain kVA capacity at a specific ambient temperature. When the ambient temperature exceeds this rating, the transformer's capacity is effectively derated.
Immediate Actions and Next Steps
Verify Transformer Load
Measure Current on Each Phase
Use a clamp meter to measure the current (amps) on each of the three phases on both the input (primary) and output (secondary) sides of the transformer. This will tell you how heavily the transformer is loaded. Note these values for each phase.
Calculate kVA Load
Calculate the approximate kVA load using the measured voltage and current: For three-phase: kVA = (Voltage (line-to-line) Current √3) / 1000 Calculate both input and output kVA. They should be relatively close, with the output being a bit lower due to transformer losses.
Compare to Transformer Rating
Compare the calculated kVA load to the nameplate kVA rating of the transformer. Is the transformer operating near or above its rated capacity? If so, you've found a major contributing factor.2.
Verify Transformer Nameplate Information
Voltage Ratio
Confirm that the transformer's input and output voltage ratings match the actual voltages in the system (267V input, 208V output). A mismatch here would explain the issue.
kVA Rating
Verify the transformer's kVA rating.
Insulation Class
Note the insulation class (e.g., Class A, Class B, Class F, Class H). This indicates the maximum allowable operating temperature of the transformer's insulation.3.
Investigate Ventilation
Airflow
The primary issue is the heat. Evaluate the room's ventilation. Is there adequate airflow to remove the heat generated by the water heaters, furnace, and transformer?
Blockages
Check for any obstructions that might be blocking vents or airflow around the transformer.
Consider Additional Ventilation
If the ventilation is inadequate, consider adding:
Exhaust Fan
Install an exhaust fan to remove hot air from the room. Place it high in the room as heat rises.
Intake Fan
Install an intake fan to bring in cooler air from outside.
Louvers
Ensure that louvers, if present, are open and clean.
Remember
Forced air needs to be balanced. You need both an adequate intake and an adequate exhaust.4.
Monitor Transformer Temperature and Voltage Over Time
Data Logging
If possible, use a data logger to record the transformer's output voltage and temperature over a 24-hour period. This will help you understand how the load and temperature fluctuate throughout the day. This data can be invaluable for identifying peak load periods and the effectiveness of any ventilation improvements.
Baseline
Measure the temperature of the transformer surface (top, sides) and the ambient temperature near the transformer at different times of the day.5.
Check Transformer Connections
Loose Connections
Loose connections can create resistance and generate heat. Carefully inspect all connections on the transformer, both on the primary and secondary sides. Tighten any loose connections.
Important: De-energize the transformer before doing this!6. Evaluate the Load
Load Profile
Understand the load connected to the transformer. Are there any large or intermittent loads that could be causing voltage sags? What is the diversity of the loads?
Power Factor
A poor power factor can increase the current drawn by the load, putting more strain on the transformer. Evaluate the power factor of the load.
Harmonics
Harmonics can also cause transformers to overheat. If there are non-linear loads (e.g., variable frequency drives, computers, electronic ballasts), consider using a harmonic analyzer to check for harmonic distortion.7.
Consider a Larger Transformer
If the load is consistently high and the ventilation cannot be improved adequately, replacing the transformer with a larger kVA rating may be necessary.
Troubleshooting Steps
Confirm the Voltage is the Correct Voltage
Check to ensure the output voltage the transformer is meant to be 208v by checking the sticker or plate on the transformer
Important Safety Considerations
De-energize Equipment
Always de-energize equipment before performing any electrical work.
Lockout/Tagout
Follow proper lockout/tagout procedures to prevent accidental re-energization.
Qualified Personnel
All electrical work should be performed by qualified and licensed electricians.
PPE
Wear appropriate personal protective equipment (PPE), such as safety glasses, gloves, and insulated tools.
In Summary
The combination of low output voltage, high temperature, and voltage improvement with a fan strongly suggests that heat is a major contributing factor. Focus on:1.
Quantifying the Load
Measure current and calculate kVA load.2.
Improving Ventilation
Add exhaust and/or intake fans.3.
Monitoring Performance
Track voltage and temperature over time.4.
Checking Connections
Inspect and tighten all connections.5.
Evaluating the Load: Understand the load profile and power factor.By following these steps, you should be able to diagnose the problem and implement the appropriate solution. If the transformer is severely overloaded or damaged, replacement may be the only option. Flag for review