Topic: Service Conductors routed thru a panel

User: augie47, Location: Tennessee

Asked on: Wednesday, September 4, 2024 at 9:34 am EDT
Answered on: Thursday, March 6, 2025 at 2:00 am EST

Question: In the 2017 Code was there anything prohibiting one set of service conductors being routed thru one service panel to a second panel ??In later Codes with 230.85 in place can that be done with feeders as long as the panel is marked ?

Let's break this down, focusing on the NEC (National Electrical Code) and how these scenarios are handled.2017 NEC



Direct Prohibition? No, but highly restricted and discouraged, verging on not allowed practically in many situations.
There wasn't a specific article that explicitly said "Thou shalt not run service conductors through a service panel to feed another service panel." However, the requirements surrounding service equipment made it incredibly difficult and impractical to do so, especially safely and compliantly. Service Equipment Location and Accessibility

Service disconnects must be readily accessible, and generally located near the point of entrance of the service conductors. This implies the disconnect should be associated with the panel it feeds, not used as a pass-through.

Overcurrent Protection

Service conductors
must be protected by overcurrent devices at their point of supply. In a typical service setup, the service panel contains the main breaker (overcurrent device) that protects the service conductors.

Neutral Bonding

The neutral must be bonded to the grounding electrode system only at the service equipment. Doing this in multiple locations creates parallel neutral paths, leading to circulating currents and potentially dangerous conditions.

Practical Implications

The intent of the code is to provide a clear and safe point of disconnect for the entire service. Using one service panel as a raceway for another service panel's conductors violated this intent and made it very difficult to comply with bonding, grounding, and overcurrent protection requirements.

NEC with 230.85 (Emergency Disconnects)



230.85 Introduces Emergency Disconnects

This section, added in later editions of the NEC (typically 2020 and later, depending on local adoption), mandates an emergency disconnect for dwelling units (and sometimes other buildings) located in a readily accessible outdoor location. This disconnect must disconnect all energized conductors.

Feeders through a Service Panel? Yes, but only if all the rules are followed.
Section 230.85 specifically addresses using a panel downstream from the service disconnect as a disconnecting means for a remote building (where the conductors would then become feeders): Marking is Required

The panel used as the disconnecting means must be clearly and permanently marked to indicate it is the emergency disconnect and that the feeder conductors are feeding another building or structure. The marking needs to be durable and visible.

Overcurrent Protection

The overcurrent device in the panel providing the feeder must be sized appropriately to protect the feeder conductors.


Grounding and Bonding

The grounding and bonding of the feeder system at the remote building must be done according to the requirements of Article 250. There should not be a redundant neutral-to-ground bond at the second panel if the neutral is carried from the first.

Essentially, 230.85 allows a service panel downstream of the
actual service equipment/disconnect to serve as a feeder disconnect for another building under very specific conditions.
In summary



2017 NEC

While not explicitly forbidden in a single sentence, running service conductors through a service panel to feed another service panel was practically prohibited by the various requirements for service equipment location, overcurrent protection, grounding, and bonding. It was almost impossible to do safely and in compliance with the intent of the code.

Later NECs (2020 onward) with 230.85

It
is permissible to use a panel downstream from the service disconnect to serve as a disconnecting means (and thus, the conductors become feeders) for another building or structure, provided the panel is properly marked, the overcurrent protection is correct, and the grounding/bonding is done per code. This is primarily in the context of the emergency disconnect requirements of 230.85.

Important Considerations



Local Amendments

Always check your local jurisdiction for amendments to the NEC. Local codes can be stricter than the NEC itself.

AHJ (Authority Having Jurisdiction)

Ultimately, the final interpretation of the code rests with the AHJ. If you are unsure, consult with your local electrical inspector.


Engineering Judgment

Complex installations may require the involvement of a qualified electrical engineer to ensure safety and compliance.

Disclaimer:
I am an AI chatbot and cannot provide professional electrical advice. This information is for educational purposes only and should not be used as a substitute for consulting with a qualified electrician or electrical engineer. Incorrect electrical work can be dangerous and potentially lethal. Flag for review