Question: Hi all,Bidding out the repair of existing outdoor sports field lighting.Lights were wired with UF and it has degraded to the point of bare conductors.Any recommendations on a better cable to survive the UV? Also a quality junction box to also withstand the elements.Thanx in advance.Dj
Okay, this is a common problem. UF cable is not ideal for direct, extended sun exposure, especially when it's buried and potentially exposed to moisture and temperature fluctuations. Here's a breakdown of recommendations for cable and junction boxes
Cable Recommendations (UV Resistant and Suitable for Direct Burial):
Direct Burial Rated, UV Resistant, THHN/THWN conductors in PVC Conduit
This is generally considered the best practice and will provide the longest life and best protection.
Why
THHN/THWN conductors are already designed to withstand moisture and heat within a conduit. PVC conduit provides a physical barrier against UV, physical damage, and moisture. Using Direct Burial rated conduit is critical for safety and longevity.
Conduit Type
Schedule 40 PVC is the most common choice for direct burial. Consider Schedule 80 if there's a high risk of physical damage (heavy traffic, equipment, etc.).
Ground Wire
Include an appropriately sized insulated grounding conductor inside the conduit.
Example
Three #8 THHN/THWN conductors (for single-phase 240V circuit with neutral) and a #8 insulated grounding conductor, all run inside 1" Schedule 40 direct burial PVC conduit.
Direct Burial Rated, UV Resistant Cable (e.g., USE-2)
This is a direct burial, sunlight resistant cable that can be directly buried without the need for conduit.
Why
Specifically designed for direct burial applications and will offer better UV protection compared to UF cable.
Considerations
While tougher than UF, it's still susceptible to physical damage if not buried deep enough or if the ground shifts. Rodents can be a concern. It also doesn't offer the same level of protection as conduit.
Example
USE-2 cable with appropriate gauge conductors for the lighting load.
RHH/RHW-2 in PVC Conduit (Direct Burial Rated)
Similar to THHN/THWN in conduit, RHH/RHW-2 is another type of wire commonly used for direct burial in conduit.
Important Considerations for Cable Selection
Amperage
Calculate the amperage of the lighting load. Then, use the NEC (National Electrical Code) ampacity tables (Table 310.16 is a good starting point) to determine the appropriate conductor size for the cable you choose. Remember to factor in voltage drop.
Voltage Drop
Long runs to sports field lighting can cause significant voltage drop, affecting light output and potentially damaging equipment. Calculate voltage drop and upsize the conductors if necessary. Online voltage drop calculators can be helpful.
Burial Depth
Follow local codes and the NEC requirements for burial depth. Generally, 18" is a common minimum depth for direct burial cables, but check your local regulations. Conduit can reduce the required depth in some cases.
Marking
Clearly mark the buried cable route with warning tape (buried a foot above the cable) to prevent accidental digging.
Junction Box Recommendations (Weatherproof & Durable)
Fiberglass or Polycarbonate Enclosures
These materials are excellent for outdoor use. They're resistant to UV degradation, corrosion, and impact.
Brands
Hoffman, Hubbell Wiegmann, Carlon (for smaller boxes).
Features
NEMA Rating
Look for a NEMA 4X rating. This indicates that the box is waterproof, dust-tight, and corrosion-resistant. NEMA 4 is acceptable in most cases where corrosion is not a major concern.
Gasketed Lid
A tight-fitting, gasketed lid is essential to keep out moisture.
UV Resistance
Ensure the enclosure material is specifically rated for UV resistance.
Lockable
Consider a lockable enclosure to prevent tampering.
Stainless Steel Enclosures
A very robust option, especially in harsh environments (coastal areas, areas with chemical exposure).
Grade
Use 304 or 316 stainless steel for the best corrosion resistance.
NEMA Rating
Again, NEMA 4X is ideal.
Avoid
Standard metal junction boxes are prone to rust and corrosion, especially if scratched or exposed to moisture.
Important Tips for Junction Box Installation
Proper Sealing
Use weatherproof fittings and sealants to prevent water from entering the box through conduit entries or cable glands.
Drip Loops
Create drip loops in the cables entering the box to prevent water from running directly into the enclosure.
Grounding
Properly ground the junction box. Connect the grounding conductor from the cable to the grounding lug inside the box.
Location
Mount the junction box in a location where it is protected from direct impact and water accumulation. If possible, orient the box so that the lid is angled downwards to shed water.
Filler/Sealant
Use a duct seal compound to seal the inside of the conduit to prevent water from entering the enclosure.
Additional Considerations
Local Codes and Permits
Always comply with local electrical codes and obtain necessary permits before starting the work.
Qualified Electrician
This type of work should be performed by a licensed and experienced electrician. Outdoor electrical work can be dangerous if not done correctly.
Inspection
Have the completed work inspected by a local electrical inspector to ensure it meets safety standards.
Lightning Protection
Depending on the location and soil conditions, consider lightning protection measures for the lighting system. Consult with a lightning protection specialist.*
Surge Protection
Install surge protectors at the panel and potentially at the light fixtures to protect the electronics from voltage spikes.
In summary, the best approach is generally to use THHN/THWN conductors run in direct burial rated PVC conduit to the light poles, terminating in a NEMA 4X rated fiberglass or stainless steel junction box at the base of each pole. This provides the best combination of UV resistance, physical protection, and moisture resistance. Flag for review