Topic: 215.18 surge protection

User: Jpflex, Location: Victorville

Asked on: Wednesday, September 4, 2024 at 10:17 am EDT
Answered on: Thursday, March 6, 2025 at 2:00 am EST

Question: To be clear a surge protection device is NOT required at a dwelling service panel but is required at each downstream sub panel supplied by a FEEDER (that are installed after this code)Since the code says where a feeder (not service entrance cables) supplies dwelling units, etc we would not have to have a SPD in service panels for dwellings correct?Also what is the best way to meet this requiremeny such as SPD placement and location? Thanks

Okay, let's break down the surge protection device (SPD) requirements and address your questions. You are referring to the 2020 NEC (National Electrical Code) and the 2023 version.

Understanding the SPD Requirement (Specifically focusing on Dwellings)

You're pointing to a common area of confusion. Here's the core principle: 2020 NEC

Section 230.67 requires a surge protection device to be installed in dwelling units. A new provision in Section 230.67(C) requires the SPD to be an integral part of the service equipment or located immediately adjacent thereto.


2023 NEC

The requirements have been updated and expanded. Article 230.67 still applies for dwellings.

Your Specific Questions Answered
1. Service Panel SPD Requirement

You are correct that the wording focusing solely on "feeders" might initially seem to exclude service panels. However,

NEC 230.67 mandates SPD protection at the service equipment for dwelling units.
The "feeder" requirement (if the home has subpanels) is in addition to the service equipment requirement. Therefore, you are required to have a surge protection device installed at the service panel for a dwelling unit in accordance with NEC 230.67. This is the primary point of protection.2. Subpanel SPD Requirement (Supplied by a Feeder)

You are also correct. In addition to the service panel, if a subpanel is supplied by a feeder to a dwelling unit, it also requires an SPD. This provides layered protection. The intent is to protect sensitive electronics throughout the home.

Best Practices for SPD Placement and Location
Service Panel



Location

As close to the service disconnect as possible. The shorter the wiring between the SPD and the service disconnect, the more effective the surge protection will be.


Types



Integral to Service Equipment

Some service panels come with an SPD built-in. This is often the cleanest and most convenient solution.


Immediately Adjacent

If not integral, mount the SPD in an enclosure immediately next to the service panel.

Connection

Make a solid, low-impedance connection to the service panel's busbars or main lugs. Use the shortest possible conductors and follow the manufacturer's instructions carefully.


Subpanels (Fed by Feeders)



Location

As close as possible to the point where the feeder lands in the subpanel.


Connection

Similar to the service panel, use short, low-impedance connections to the subpanel's busbars.

Key Considerations for SPD Selection and Installation
SPD Type



Type 1

Suitable for installation before the main overcurrent protective device (service entrance). Often used in commercial or industrial settings but can be used in residential.

Type 2

Suitable for installation
after the main overcurrent protective device (service panel or subpanel). This is the most common type for residential applications.

Type 3

Point-of-use SPDs (e.g., surge strips). These are supplementary and do not replace the requirement for SPDs at the service panel and subpanels.

Voltage Protection Rating (VPR) or Suppressed Voltage Rating (SVR)

Lower is better. This indicates the maximum voltage the SPD will allow to pass through during a surge. Choose an SPD with a VPR or SVR appropriate for your system voltage (e.g., 120/240V).


Surge Current Capacity (kA)

Higher is generally better. This indicates the amount of surge current the SPD can handle. A higher kA rating means the SPD can withstand larger surges and may last longer. 40kA is a common minimum recommendation for residential applications, but consider higher ratings (e.g., 80kA or 100kA) in areas prone to frequent or severe surges.

UL Listing

Ensure the SPD is UL listed to UL 1449.


Manufacturer's Instructions

Always follow the manufacturer's instructions for installation.

Professional Installation

It is highly recommended to have a qualified electrician install SPDs. This ensures proper connection, grounding, and compliance with all applicable codes.

In summary:
NEC 230.67 requires an SPD at the service equipment for dwelling units. If there are subpanels supplied by feeders, those also require SPDs. Proper SPD selection and installation are critical for effective surge protection. Consult with a qualified electrician for the best solution for your specific situation. Flag for review