Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 230.85 on 400 amp services

User: augie47, Location: Tennessee

Asked on: Wednesday, September 4, 2024 at 10:19 am EDT
Answered on: Thursday, March 6, 2025 at 2:00 am EST

Question: We have had our 1st AHJ adopt 230.85 (this area has been on the '2017 NEC previously)On 400 amp services (dual 200 amp panels) what is the most common method of addressing this requirement in your area ??

Okay, let's break down how 230.85 is typically addressed for a 400 amp service with dual 200 amp panels, and the common practices.

Understanding 230.85 (Emergency Disconnects) The Requirement

NEC 230.85 essentially mandates an outdoor emergency disconnect for dwelling units. The goal is to provide first responders (firefighters, etc.) with a readily accessible way to de-energize the entire electrical system of the dwelling.


Key Considerations



Readily Accessible

This is crucial. The disconnect must be easily found and operated.


Outdoor Location

Must be outside the building.

Clearly Marked

It needs clear, durable labeling that indicates its purpose (e.g., "EMERGENCY DISCONNECT - SERVICE").


Suitable for the Environment

The disconnect enclosure must be rated for outdoor use (NEMA 3R or better).

Ability to Disconnect
All Ungrounded Conductors

The disconnect must interrupt all hot wires.

Common Methods for 400 Amp Service (Dual 200 Amp Panels) to Meet 230.85


Here's a breakdown of typical approaches, ranked from most common to less common, along with considerations:1. Main Disconnect at the Meter (Meter-Main Combo with Disconnect)



Description

This is often the most straightforward and preferred method. You replace the standard meter enclosure with a meter-main combination unit that includes a 400 amp rated disconnect switch (or a pair of 200 amp disconnects). The line conductors feed into this meter-main combo, the meter is connected within, and then the load side of the disconnect feeds your two 200 amp panels inside the house.

Pros

Simplest installation. All components are in a single, readily accessible location. Typically the most cost-effective option. Provides a single point of disconnection. Easy to label appropriately.

Cons

Requires replacing the existing meter enclosure (if there is an existing service). Might require coordination with the utility company for meter relocation and approval of the meter-main.

Common Brands

Milbank, Siemens, Eaton, Square D2.

Separate 400 Amp Disconnect Enclosure (Between Meter and Panels)



Description

You install a separate, outdoor-rated 400 amp disconnect enclosure between the meter and the interior 200 amp panels. The service conductors from the meter run to this disconnect, and then conductors from the disconnect run to each of the 200 amp panels.


Pros

Can be used if a meter-main isn't feasible or preferred. Allows for more flexibility in placement of the disconnect.

Cons

More expensive than a meter-main combo (separate enclosure, disconnect switch, and labor). Requires more conduit and wiring. Takes up more space on the exterior of the building.3.

Two 200 Amp Disconnects in a Single Enclosure



Description

Install an enclosure that houses TWO 200 amp disconnects. Service conductors would feed into this enclosure, and then each disconnect would feed one of the 200 amp panels inside.


Pros

Potentially slightly cheaper than a single 400 amp disconnect (depending on component costs).

Cons



AHJ Scrutiny

Some AHJs may not accept this approach, arguing that it doesn't provide a
single readily accessible disconnect for the entire dwelling. It could be argued that an emergency responder might only disconnect one, thinking they have de-energized the entire house, which would still leave half of the dwelling energized. Check with your AHJ on this approach before using it. More complicated wiring within the enclosure. More potential for confusion during an emergency.

NEC Code Concerns

While technically compliant if interpreted strictly, it can go against the intent of providing a clear and simple emergency shutoff.

Important Considerations and Best Practices



Coordination with the Utility

Always involve the utility company early in the process. They will have specific requirements for meter enclosures, disconnect placement, and service entrance wiring. They may even have a list of approved meter-main combo units.

AHJ Approval

Get approval from the local AHJ before starting any work. Discuss your proposed solution and ensure it meets their interpretation of 230.85.

Clear Labeling

Use durable, weather-resistant labeling that clearly states "EMERGENCY DISCONNECT - SERVICE". Use appropriately sized lettering that is easily visible.


Placement

Consider accessibility for people of all abilities. Avoid placing the disconnect behind obstructions (bushes, fences, etc.). A common height is between 4 and 6 feet above ground level.

Wiring Methods

Use appropriate wiring methods for outdoor applications (e.g., RMC conduit, wet-rated conductors).


Professional Installation

This work should always be performed by a licensed and qualified electrician.

In Summary:


The meter-main combo with an integrated 400 amp disconnect is usually the easiest and most cost-effective solution for a 400 amp service with dual 200 amp panels. However, always consult with your utility and AHJ to ensure compliance with their specific requirements. Clear communication and planning will help ensure a safe and code-compliant installation. Flag for review

Previous Question Next Question