Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Transfer Switch for Main Service Disconnect

User: bbell, Location: Tuolumne County

Asked on: Wednesday, September 4, 2024 at 3:50 pm EDT
Answered on: Thursday, March 6, 2025 at 2:01 am EST

Question: We are having situations where the installer is taking the service conductors, after the meter in a combination meter main service panel (main bus with combined neutral/equipment grounds) condition and routing the conductors to an ATS. They then run the conductors back to the "main service panel" (the location in which the service entrance conductors originated before and after the meter with the main bussing) with no main disconnect in this panel. The installer is then attempting to claim the ATS is the main service disconnect and is bonding the grounds/neutrals with the jumper wire.I am finding this to be a direct violation of NEC (CEC in CA) of 250.142 (1) for the required bonding of the grounded conductor. Any thoughts or feedback on this would be appreciated.

You're right to be concerned. Your interpretation is sound, and the installer's justification is problematic. Here's a breakdown of the issues and why your assessment is likely correct

Understanding the Problem:

The core issue is the misapplication of the ATS as the service disconnect and improper neutral-ground bonding location after the meter. Here's the typical (and code-compliant) scenario versus the problematic installation: Typical, Code-Compliant Setup

1. Service conductors enter the meter main.
2. Neutral and ground are bonded
only at the meter main (this is the service disconnect).3. Feeders (or branch circuits) leave the meter main and go to subpanels. Neutral and ground are not bonded in these subpanels.

Problematic Installation

1. Service conductors enter the meter main.
2. Conductors routed after the meter to an ATS.3. Conductors routed back to the original meter main location (now without a main disconnect).4. The installer incorrectly claims the ATS is the service disconnect and bonds neutral/ground at the ATS.5. There is now an additional grounding bond in a "subpanel" (which is not allowed).


Why This is a Violation


250.24(A)(5) - Single Point of Connection

The grounded conductor (neutral) must be connected to the grounding electrode conductor system at only one point. This is typically at the service disconnect. By bonding at the ATS after the meter, you've created a second point of connection, leading to circulating neutral currents on the grounding system. This can cause nuisance tripping, equipment malfunction, and even pose a shock hazard.2.

250.142(1) - Use of Grounded Conductor for Grounding Equipment

This section strictly defines when you can use the grounded conductor (neutral) for grounding non-current-carrying metal parts of equipment. It's generally only allowed at the service equipment. After the service disconnect, the grounding and grounded (neutral) conductors must be kept separate. By bonding at the ATS, you're violating this principle.3.

ATS Not a Service Disconnect

An ATS's primary function is to switch between power sources (utility and generator/backup). It's not designed or intended to be the main service disconnect unless specifically listed and labeled as such (and even then, the overall configuration would need to be carefully scrutinized). In most residential or light commercial applications, the meter main panel is the designated service disconnect, containing the main breaker.4.

Lack of Main Disconnect

By routing conductors through the ATS and back to the original panel, that panel now lacks a true "main disconnect". While individual breakers exist, there's no single point to de-energize the entire panel, which violates the spirit (and likely the letter) of NEC rules regarding service equipment.5.

Potential for Parallel Paths for Neutral Current

Bonding the neutral and ground at the ATS creates a parallel path for neutral current. Some neutral current will now flow on the grounding conductor, which is a safety hazard and violates the principle of keeping neutral current confined to the neutral conductor.

Specific Code Sections to Cite



NEC 250.24(A)(5)

Grounding of Systems Supplying Premises. (Single point grounding)


NEC 250.142(1)

Use of Grounded Circuit Conductor for Grounding Equipment. (Restrictions on using the neutral for grounding after the service.)

NEC 230.70

General. (Location, all service disconnecting means shall be located at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors. )

How to Address the Situation


Documentation

Take clear photos of the installation
before discussing it. Document everything in writing, including the installer's reasoning.2.

Formal Rejection

Issue a formal written rejection of the installation, citing the specific NEC (or CEC in CA) code violations.3.

Correct Installation

The correct installation approach depends on the specific goals:


Option 1 (Recommended)

Keep the existing meter main as the service disconnect. Run a feeder from the meter main to a separate distribution panel fed from the ATS. In this separate panel, keep the neutral and ground separate.

Option 2

Replace the Meter Main with a Listed Metered ATS: Install a single piece of equipment that acts as both the meter enclosure, the service disconnect, and the ATS. This equipment MUST be listed and labeled for this purpose.

Important Considerations for California (CEC)



Amendments

California often has amendments to the NEC. Check the California Electrical Code (CEC) for any specific modifications or additions that might be relevant.

Local Authority

Consult with your local electrical inspector. They have the final authority on code interpretations and can provide guidance specific to your jurisdiction.


Permits

Make sure that all work has been permitted and inspected.

In summary, your assessment is correct. The installer's attempt to use the ATS as the service disconnect and bond neutral/ground there violates fundamental principles of electrical safety and the NEC/CEC. The system needs to be re-configured for safety and code compliance.
Flag for review

Previous Question Next Question