Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Multi-family load calculation question

User: KBot9, Location: NYC

Asked on: Wednesday, September 4, 2024 at 4:26 pm EDT
Answered on: Thursday, March 6, 2025 at 2:01 am EST

Question: Say an existing 200 unit building has determined the existing maximum demand for the entire building via a years worth of utility statements and metering at 1500 AmpsThey seek to add three circuits per unit : Laundry, Dryer, and electric range.Can the calculation be :Starting with the existing max demand load of 1500 amps then as per 220.87 times 125% (The calc satisfies all 3 caveats of 220.87) so 1875 Amps.THEN, add the three new proposed devices, calculating their total demand per either via 220.42/54/55 or 220.82 or 220.84 and plug in and to existing max (plus 25%) 1875 Amps whichever of those three options are lowest?

You're on the right track, but let's break down the nuances and ensure compliance with the NEC

Understanding the NEC Sections
220.87 (Existing Dwelling Unit)

This section
allows you to use actual measured demand for existing installations. It doesn't require you to use 125% of the existing demand. It's a calculation shortcut.

220.82 (Electric Ranges)

This covers calculating the demand load for electric ranges. Table 220.55 (note 1) allows for a reduction if there are more than five ranges.

220.54 (Electric Clothes Dryers)

Sets the demand factor for electric clothes dryers.


220.53 (Laundry Circuit)

Sets the minimum load requirement for laundry circuits.

The Process – Two Acceptable Approaches
Approach 1This is a Load Increase to an existing installation. NEC Article 220.87 allows for the "Existing Dwelling Unit" method, which is a calculation shortcut.

Step 1

Existing Load Determine the existing maximum demand. You've stated it's 1500 Amps, which is based on a year's worth of data and metering.

Step 2

Calculate the load increase.
Use the existing max demand (1500amps) and times it by 125% for 1875 Amps

Step 3

Calculate the

Demand Load
of each added device. Electric Range (220.55 or 220.82)

Use the method that results in the

lower
demand load
Use Table 220.55. Note 1 applies when you have more than five ranges. This likely offers the most significant reduction. If this option is taken this is the value of the device's load contribution. Electric Clothes Dryer (220.54)

The demand load for each dryer is 5 kVA.


Laundry Circuit (220.53)

Minimum 1500 volt-amperes per laundry circuit.

Step 4

Sum the Device's Load Contribution.Add the demand of the added device(s), calculated in Step 3, to the existing max demand (existing max demand 125%).
Step 5: Determine that the existing system can handle the new load
This will be the final figure for all added load in the existing building, and must be factored into all OCPD and distribution equipmentKey Considerations and Cautions Local Amendments

Always check for local code amendments, as some jurisdictions may have more restrictive requirements or specific interpretations.

Feeder Overcurrent Protection

The final calculated load must be used to ensure the existing feeder overcurrent protection is adequate. If the load exceeds the existing feeder's rating, you will need to upgrade the feeder and overcurrent protection.


Available Fault Current

Increasing the load on the system can also increase the available fault current. Verify that all existing equipment is properly rated to withstand the increased fault current.

Voltage Drop

Check the voltage drop for the new circuits and the existing feeder. Excessive voltage drop can lead to equipment malfunction and overheating.


Neutral Conductor Sizing

Ensure that the neutral conductor is properly sized for the unbalanced load. Pay particular attention to the electric ranges and dryers, as they can create significant neutral current.

Example (Illustrative)


Let's make some assumptions: Existing Max Demand

1500 Amps


Ranges (Table 220.55 with Note 1 applied)

Demand per range is 3 kVA.

Dryers (220.54)

Demand per dryer is 5 kVA.


Laundry Circuit (220.53)

Demand per laundry circuit is 1.5 kVA.

Calculation


Existing Load

1500 Amps 125% = 1875 Amps2.

Added Load Per Unit

Range: 3 kVA / 240V = 12.5 Amps per range Dryer: 5 kVA / 240V = 20.83 Amps per dryer Laundry: 1.5 kVA / 120V = 12.5 Amps per laundry circuit

Total per Unit

12.5 + 20.83 + 12.5 = 45.83 Amps3.

Total Added Load (200 Units)

45.83 Amps/unit
200 units = 9166 Amps4.

Total New Load

1875 Amps + 9166 Amps = 11,041 Amps

Disclaimer:
This is a simplified example for illustrative purposes only. A qualified electrical engineer or licensed electrician must perform a thorough load calculation and verify compliance with all applicable codes and standards before making any electrical modifications.I hope this comprehensive explanation and example help you with your calculations! Remember to always consult with qualified professionals and local authorities to ensure the safety and compliance of your electrical installations. Flag for review

Previous Question Next Question