User: settwilliams, Location: New york
Asked on: Wednesday, September 4, 2024 at 5:59 pm EDT
Answered on: Thursday, March 6, 2025 at 2:02 am EST
Question: Hello all I’m new to the forum hopefully someone can help a poor apprentice out.Are locknuts required to be used with grounding bonding bushings? I’m asking because I made a boo boo and I left the locknut off thinking there wasn’t enough thread. Was that a huge mistake on my part ?
Yes, generally speaking, locknuts are required when using grounding/bonding bushings. Here's why, and what you should do
Why Locknuts are Required:
Mechanical Security
The locknut is the primary means of mechanically securing the bushing to the enclosure. Without it, the bushing could loosen over time due to vibration, movement, or thermal expansion/contraction. A loose bushing defeats its purpose.
Electrical Connection
While the grounding/bonding screw should make good contact, the locknut assists in maintaining a reliable electrical connection between the bushing, the enclosure, and ultimately, the grounding/bonding conductor. This is crucial for providing a low-impedance path for fault current. The locknut helps ensure that even if the screw loosens slightly, there's still a good ground connection via the physical contact of the bushing to the enclosure.
Code Compliance
Electrical codes (like the NEC in the US) typically require fittings and connectors to be installed according to their listing and instructions. Grounding and bonding is one of the most important aspects to electrical work, because it involves safety and proper function.
Why You Thought There Wasn't Enough Thread
It's possible the knockout was a little undersized or the bushing was exceptionally thick. Also it may be that you forgot to knock out the reducing rings.
What You Should Do
Correct the Issue Immediately
Do not leave it as-is. It's a safety and code violation.2.
De-energize the Circuit
Ensure the circuit you're working on is completely de-energized and properly locked out/tagged out.3.
Inspect the Installation
Check the size of the hole in the enclosure, the thickness of the enclosure wall, and the thread length on the conduit or fitting. Make sure all of the reducing rings on the knockout have been removed.4.
Install the Locknut
If possible, loosen the connections, install the locknut properly, and tighten everything securely. Use two wrenches – one to hold the bushing and one to tighten the locknut.5.
If There Truly Isn't Enough Thread
Use a Conduit Extension
If the thread length is insufficient to accommodate both the bushing and a locknut, you might need to use a short conduit extension (a "nipple") to provide more thread.
Change to a Different Type of Connector
If a nipple isn't practical, consider using a different type of connector or bushing that doesn't require a locknut in the same way, but only if it's specifically listed and approved for the application and provides equivalent grounding/bonding performance. This is less likely but possible.6.
Document the Correction
Note the issue and the corrective action taken in your work log.
Important Considerations
Listing and Instructions
Always install fittings and connectors according to the manufacturer's listing and instructions.
Grounding/Bonding is Critical
Never compromise on grounding and bonding. It's a matter of safety and ensures proper operation of the electrical system.
Talk to Your Journeyman/Supervisor:
This is a good learning opportunity. Discuss the situation with your journeyman or supervisor. They can provide guidance on the best way to correct the issue and help you understand the importance of proper grounding and bonding techniques.It's better to ask questions and correct mistakes than to leave a potentially dangerous situation. Good luck with your apprenticeship! Flag for review