Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Step up transformer grounding

User: TXMaster, Location: Texas

Asked on: Wednesday, September 4, 2024 at 6:05 pm EDT
Answered on: Thursday, March 6, 2025 at 2:02 am EST

Question: I have a situation that requires a step-up transformer from 3ph 208V to 3ph 480V. The transformer proposed is wye input and delta output. The load does not use a neutral. How can I meet code without intentionally grounding one leg of the delta output? The load cannot handle a corner ground. Is there any advantage to using a wye input? The load is a VFD with a dual motor output for A/C fans in an air handler.

Okay, let's break down this situation with a 208V-to-480V step-up transformer for a VFD-driven fan application, considering NEC code and grounding requirements.

Understanding the Situation



Input

3-phase 208V, Wye.


Transformer

Wye primary (208V), Delta secondary (480V).

Output

3-phase 480V, Delta.


Load

VFD powering A/C fans in an air handler (no neutral required).

Requirement

Avoid corner-grounded delta, and comply with NEC.


Concern

Using a corner-grounded delta is unacceptable for the load.

The Core Problem: Grounding the Delta Secondary


The NEC (National Electrical Code) generally requires that electrical systems be grounded, but the specifics of how to ground a delta secondary can be tricky. A corner-grounded delta is one solution, but as you pointed out, that won't work for your load (VFD).

Acceptable Grounding Method: Grounded System (Impedance Grounding) Overview

To meet code without corner grounding, you
must establish a grounded system. The standard solution is to use an impedance grounding system. This involves connecting a grounding impedance, typically a resistor, between one point of the delta (often a derived neutral point) and ground.

Implementation


Derived Neutral (if needed)

A "derived neutral" can be created artificially (e.g., using zigzag grounding transformer or resistors) if the system doesn't naturally have a neutral point suitable for impedance grounding. In your case, with a delta secondary, you will always need a derived neutral.2.

Grounding Impedance (Resistor)

The neutral is connected to ground through an impedance, usually a resistor. The value of the resistor is carefully chosen to limit the ground fault current to a specific level (often in the range of a few amps).3.

Ground Fault Protection

The limited ground fault current allows you to implement sensitive ground fault protection. This can be done with ground fault relays that detect even small ground fault currents and quickly trip the upstream breaker to clear the fault.

Advantages of Impedance Grounding



Reduced Fault Current

Limits the magnitude of ground fault currents, minimizing damage to equipment and reducing arc flash hazards.

Improved System Reliability

By limiting the fault current and clearing ground faults quickly, you reduce the stress on the system and improve overall reliability.


Controlled Overvoltages

Helps to dampen transient overvoltages during ground faults.

NEC Compliance

This method complies with NEC requirements for grounding electrical systems, specifically those sections related to impedance grounding. Refer to NEC Article 250 for detailed requirements.


Calculating the Grounding Resistor

The proper sizing of the grounding resistor is crucial. You'll need to perform calculations to determine the appropriate resistance value based on the desired ground fault current and the system voltage. Consult with a qualified electrical engineer for these calculations.

Why Not Ungrounded?
While technically an ungrounded delta might seem like a solution, it presents several significant problems and is generally not permitted by the NEC for most power distribution systems: Overvoltages

Ungrounded systems can experience significant transient overvoltages during ground faults. This can damage equipment insulation.

Difficult Fault Location

Locating a ground fault in an ungroundded system can be extremely challenging and time-consuming.


First Fault Becomes Second Fault

A first ground fault on an ungrounded system doesn't immediately trip a breaker. However, the entire system voltage will appear between the faulted phase and ground. The first fault effectively "grounds" that phase. If a second ground fault occurs on a different phase, it becomes a phase-to-phase fault, which can be very destructive.

Safety Concerns

The presence of potentially high voltages to ground can pose a significant safety hazard.

Advantages of Wye Input (208V Side)



Common Mode Voltage Reduction

VFDs can generate common mode voltage noise that can couple back into the input power source. A wye input offers a path for common-mode currents to flow back to the source through the neutral, which can reduce the level of common-mode voltage impressed upon the incoming 208V source. This isn't always necessary, but it can be helpful in sensitive environments where you want to minimize noise on the 208V system.

Impedance Matching

If the 208V source has a relatively high impedance, the wye connection can provide better impedance matching for the transformer, leading to improved voltage regulation and reduced harmonic distortion.

Delta-Wye Transformer Not Recommended

The reverse of the proposed transformer (delta primary, wye secondary) is not recommended. In the event of a 208v power outage, there can be backfeed from the transformer and VFD.

Recommendations and Next Steps


Consult with an Electrical Engineer

This is crucial. They can perform the necessary calculations for the grounding impedance, select appropriate protective devices, and ensure compliance with all applicable codes.2.

Implement Impedance Grounding

Design and install a proper impedance grounding system for the delta secondary. This is the recommended and code-compliant approach.3.

Specify Appropriate Ground Fault Protection

Select and install ground fault relays that are sensitive to the limited ground fault current. These relays should trip the appropriate upstream breaker to quickly clear ground faults.4.

Verify VFD Compatibility

Double-check that the VFD is compatible with an impedance-grounded system. Most modern VFDs are, but it's always best to confirm.5.

Consider Harmonics

VFDs are non-linear loads that generate harmonics. You may need to consider harmonic filtering to mitigate the impact of these harmonics on the power system.6.

Proper Installation

Ensure that the transformer, grounding system, and protective devices are installed correctly by qualified electricians.7.

Wye-Delta Transformer

Keep the wye primary/delta secondary configuration for your transformer.8.

Check Local Codes:
Be sure to check local electrical codes, as they may have specific requirements beyond the NEC.In summary, you cannot* simply leave the delta secondary ungrounded. Impedance grounding with appropriate ground fault protection is the standard, safe, and code-compliant solution. Consult with a qualified electrical engineer to design and implement the grounding system. Flag for review

Previous Question Next Question