Topic: Detached building sub panel replacement

User: Dsg319, Location: West Virginia

Asked on: Wednesday, September 4, 2024 at 8:11 pm EDT
Answered on: Thursday, March 6, 2025 at 2:02 am EST

Question: Replacing a Main lug only sub panel in a garage.#2awg aluminum is existing. Hoping the feeder is on a 90amp breaker as it’s already existing.Customer wants a main breaker in garage for ease of adding stuff and working in panel.I plan to just use a sub panel with a 100amp main as that is a standard size in the big box stores with the amount of spaces I need.To keep from a fused or knife switch disconnect or other methods is anybody else seen #2awg aluminum feeding a 100amp subpanel if the feeders protected at 90amps.I know the conductors are properly protected with the feeder breaker but just wondering if this is the norm for this scenario.

You've got a solid plan. Here's a breakdown of why it's acceptable and some additional considerations

Why #2 Aluminum to a 100A Main Subpanel, Protected by a 90A Breaker, is OK:
Conductor Ampacity

#2 AWG aluminum has an ampacity of 75 amps at 75°C and 90 amps at 90°C per NEC Table 310.16 when installed per NEC 310.15(B)(3)(a). As long as the terminals on the subpanel and the feeder breaker are rated for 75°C, you are compliant with the NEC.


Overcurrent Protection

The 90A breaker in the main panel is properly protecting the #2 AWG aluminum conductors. You are meeting the basic requirement of overcurrent protection for the wire size.

Subpanel Main Breaker

The 100A main breaker in the subpanel
does not need to match the feeder breaker size. The subpanel main breaker is primarily a disconnect. It's there to de-energize the entire subpanel quickly and easily for safety. It also provides overcurrent protection for the subpanel itself (its bus bars and internal components), not the feeder conductors.

Series Ratings

You are not trying to use the main panel as a series rated device so there is not an issue with that.

Standard Practice

This is a very common and acceptable practice. Using a slightly larger main breaker in the subpanel (e.g., 100A) than the feeder breaker (e.g., 90A) offers convenience and doesn't violate the NEC as long as the feeder conductors are properly protected.

Key Considerations



Terminal Temperature Ratings

Crucially, verify that the terminations at both the main panel breaker and the subpanel main breaker are rated for use with aluminum conductors and rated for 75°C. This is usually indicated on the device. Using the wrong terminals can lead to overheating and failure.

Proper Termination

Use anti-oxidant compound (e.g., Noalox) on the aluminum conductors at all termination points. Torque all connections to the manufacturer's specified torque value. Loose connections are a major cause of problems with aluminum wiring.


Grounding and Bonding

Ensure proper grounding and bonding of the subpanel. Separate the neutral and ground at the subpanel since it's a subpanel. Use a grounding electrode conductor (GEC) to bond the subpanel enclosure to the grounding electrode system (GES).

Future Load Calculations

Make sure you inform the customer that even though they now have a 100A main breaker in the garage, the
actual capacity of the feeder is limited by the 90A breaker in the main panel. Advise them to consider a larger service upgrade if they anticipate significant future load increases.

Labeling

Label the subpanel clearly, indicating the feeder breaker size (90A) in the main panel and the location of the main panel. This helps future electricians and homeowners.

In summary:


Your plan is good. Just double-check those terminal temperature ratings and ensure proper termination practices. Flag for review