Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 100 amp Sub-Panel wire size

User: Hard2bej, Location: Wisconsin

Asked on: Wednesday, September 4, 2024 at 8:14 pm EDT
Answered on: Thursday, March 6, 2025 at 2:02 am EST

Question: Hey all, I’m running into a few of different answers on this. I need to know what size wire I need to complete the install. It’s a 100 amp sub panel in a detached garage 110’ away (total wire length) fed from a 200 amp main house panel. I have 1 1/4 pvc buried. I need 3 current carrying conductors and the ground. The garage will have a main breaker as the disconnect. I’ve heard #4 cu unless far away then #2 cu, prefer alum as its wayyy cheaper, then I read in the code that you could apply the 83% of rated amps. Can someone point me in the right direction? Also #8 ground? I don’t size conductors much as it’s done for me. Thanks in advance!!

Okay, let's break this down step-by-step to get you the correct wire size for your 100-amp subpanel feed. You're right, there are several factors involved, and understanding them is key.

Here's what we need to consider


Ampacity Requirements (NEC 310.15)
: The wire needs to be able to handle at least 100 amps.2. Voltage Drop (Informative Annex I): Crucially important, especially at 110 feet. Excessive voltage drop can damage equipment and cause lights to dim.3. Conductor Material (Copper vs. Aluminum): Aluminum has a lower ampacity for the same gauge wire compared to copper.4. Wiring Method & Temperature Rating (NEC 310.16): Your PVC conduit (assuming it's buried) is likely rated for 90°C, but termination limitations often mean you have to use the 75°C column in the ampacity tables.5. 83% Rule (NEC 310.15(B)(7)): This residential dwelling derating only applies when you are using the subpanel to feed the entire load of a dwelling unit. This is not the case.6. Grounding Conductor Size (NEC 250.122): This depends on the overcurrent protection device (your 100A breaker).

Here's the breakdown



Distance

110 feet (This is significant for voltage drop calculations)


Subpanel

100 amps

Conduit

1 1/4" PVC (buried)


Conductors

3 current carrying, 1 ground

Main Panel

200 amp breaker feeding the subpanel


Termination Temp

75C

1. Ampacity and Conductor Size



Aluminum

To carry 100 amps at 75°C, you'd typically need at least #1 AWG aluminum. See NEC Table 310.16.


Copper

To carry 100 amps at 75°C, you'd typically need at least #4 AWG copper. See NEC Table 310.16.

2. Voltage Drop Calculation is CRITICAL

This is where the length comes into play. We need to calculate the voltage drop to ensure it's within acceptable limits (typically 3% for the feeder). I'm going to use a conservative approach and aim for under 3%.Here's a simplified voltage drop calculation (you can use online calculators for more precise results, like Southwire's or similar):

Voltage Drop (Aluminum)
: A rough calculation shows that using #1 AWG aluminum for 100 amps over 110 feet will likely result in a voltage drop exceeding 3%. This means #1 AWG aluminum is likely insufficient. We need to increase conductor size. Voltage Drop (Copper): Using #4 AWG copper is also likely to result in voltage drop exceeding 3%. We need to increase conductor size. Voltage Drop (Aluminum Option 2): Upgrading to a #1/0 AWG aluminum would likely bring the voltage drop well within acceptable limits (under 3%). Voltage Drop (Copper Option 2): Upgrading to a #2 AWG copper would likely bring the voltage drop within acceptable limits (under 3%).3. Grounding Conductor Size

Since your overcurrent protection is 100 amps, according to NEC Table 250.122, you'll need at least an #8 AWG copper grounding conductor or a #6 AWG aluminum grounding conductor.

4. Conduit Fill

Your 1 1/4" PVC conduit should easily accommodate (3) #1/0 AWG aluminum conductors and (1) #6 AWG aluminum grounding conductor (or (3) #2 AWG copper conductors and (1) #8 AWG copper grounding conductor) Refer to NEC Chapter 9, Tables 4 and 5 for conduit fill calculations if you want to verify.

5. Recommendation

Considering the ampacity requirements, voltage drop, and grounding conductor size, here are your options:


Option 1 (Aluminum)

Use #1/0 AWG aluminum conductors for the three current-carrying conductors and #6 AWG aluminum for the grounding conductor.

Option 2 (Copper)

Use #2 AWG copper conductors for the three current-carrying conductors and #8 AWG copper for the grounding conductor.

Important Considerations and Cautions



Local Codes

Always check with your local electrical inspector or building department for any specific requirements or amendments to the NEC. They have the final say.

Terminations

Ensure that the equipment you're connecting to (breakers, panel lugs) are rated for the size and type of conductor you're using (especially important for aluminum). Use appropriate antioxidant paste for aluminum connections.


Professional Installation

If you're not completely comfortable with electrical work, it's best to hire a qualified electrician to ensure the installation is safe and code-compliant. Mistakes can be dangerous!

Digging Safety

Before digging, call 811 to have underground utilities located and marked.

In Summary

For your situation,

#1/0 AWG Aluminum or #2 AWG Copper
conductors are the proper size to deliver 100 amps to your subpanel 110ft away while still maintaining a proper voltage drop.Disclaimer: This information is for educational purposes only and is not a substitute for professional electrical advice. Always consult with a qualified electrician for any electrical work.* Flag for review

Previous Question Next Question