Topic: Cummins 20GSBB-6714A ATS replacement

User: IJB, Location: Seattle, WA

Asked on: Wednesday, September 4, 2024 at 10:39 pm EDT
Answered on: Thursday, March 6, 2025 at 2:03 am EST

Question: I am a residential electrical contractor in Seattle, WA and have never come across a Cummins generator. A client of mine lost a phase and I found it was lost in the ATS. I told them I don’t have a strong background in Cummins as I’ve always used Generac and found them a technician by calling Cummins directly.The technicians have been horrible and weren’t going to pull a permit and scared my client off so they asked if I’d be willing to give it a go and just replace the whole transfer switch. I’m confident in following the schematics and everything I’m just unsure of which model to buy and if I’ll have access to everything I need through online distributors or big box stores.The model number of the generator is 20GSBB-6714A which has been discontinued.Does anyone have some insight on this subject? I tried uploading a picture of the ATS as I imagine some of you may have an easier solution then replacing the whole ATS. Power comes in on the top of the switch and has both legs present, then the switch says phase A on phase b off.I appreciate any help on this subject, thank you!

Okay, I understand your situation. You're a seasoned residential electrician in Seattle, comfortable with Generac, but unfamiliar with Cummins ATS systems. You have a client with a 20GSBB-6714A generator (now discontinued) and a malfunctioning ATS, and you're considering replacing the whole unit due to poor service from Cummins techs. Here's a breakdown to help you decide on a path forward

Understanding the Situation
Lost Phase

The crucial detail is that you have power
into the ATS, but a phase is lost within the ATS. This narrows the problem down significantly. It means the generator itself is producing all three phases (assuming it runs at all). The problem is either the sensing of the phase, the ATS switching mechanism itself, or its control board.

Discontinued Generator

The 20GSBB-6714A being discontinued makes finding exact replacement parts for the ATS potentially challenging, but not impossible. This doesn't necessarily mean the entire ATS needs replacement.

Permitting

You're right to be concerned about the lack of a permit from the original Cummins techs. This is a red flag and you need to operate within code.


Client Trust

Your client's desire for you to handle this now highlights the importance of restoring their confidence.

Troubleshooting Before Replacement (Highly Recommended)


Before jumping to a full ATS replacement, try these steps. You might save your client significant money and avoid unnecessary work:1. Visual Inspection

Carefully (with power off and locked out) inspect the ATS for:

Burn Marks/Arcing

Look for any signs of overheating or electrical arcing, especially around the contactors/relays, wiring connections, and the control board. A burned component is a dead giveaway.


Loose Connections

Check every wire connection for tightness. Vibration can loosen connections over time, causing intermittent or complete failures.

Corrosion

Seattle's climate can lead to corrosion, especially on terminals and contacts. Clean any corrosion you find (with power off, of course, and using appropriate contact cleaner).


Foreign Objects

Debris or even insects can sometimes cause problems.2.

ATS Model Number

Locate the model and serial number of the ATS itself. This is crucial for finding compatible replacement parts or understanding the ATS's specific operation. It will be on a label on the ATS.3.

Voltage Testing (With Extreme Caution)

If you are comfortable and qualified to work on live equipment: With the generator running and the ATS in generator mode (and only with proper PPE and understanding the risks), carefully check the voltage at the output side of each contactor/relay for each phase. This will help pinpoint exactly where the phase is being lost. Is the voltage going into the ATS the same as the generator voltage? Are the voltage measurements consistent with the generator voltage?4.

Control Board Inspection



Capacitors

On the control board, look for bulging or leaking electrolytic capacitors. These are a common failure point in electronic devices.


Relays

Carefully inspect the relays on the board. Sometimes you can see physical damage or they might smell burnt.5.

Wiring Diagram/Schematics

Essential. You absolutely need the wiring diagram for the ATS. Search online using the ATS model number. Cummins might have it available on their website, or you might find it through online forums or parts suppliers.6.

Contactors/Relays

If the visual inspection shows damage, you can sometimes replace just the faulty contactor or relay if you can identify it and find a replacement. Bring the component number to an electrical supply house.7.

Sensing Circuit

ATS's have sensing circuits that monitor the voltage from the utility. Problems with the sensing circuit can cause a lost phase.8.

Control Board Reset

Sometimes, a simple reset can resolve issues. Check the ATS manual (if you can find one) for reset instructions.9.

Test The Switch

Make sure that the switch is not physically damaged. If the switch is damaged and you can find a replacement switch that is compatible, it may be the best option.

Choosing a Replacement ATS (If Necessary)


If troubleshooting fails, here's how to approach replacing the ATS:1. Determine Amperage and Voltage

The generator is likely rated for 20kW, but you need to confirm the amperage and voltage requirements of the ATS. This information is crucial for selecting a replacement.2.

Consider Compatibility

The new ATS must be compatible with the 20GSBB-6714A generator and your electrical service. This includes:

Voltage

Must match your service voltage (e.g., 120/240V single-phase).


Amperage

Must handle the generator's maximum output current and the peak load of the circuits it will be supplying.

Wiring

You'll need to adapt the wiring from the generator and the service panel to the new ATS.


Control Signals

The generator sends signals to the ATS to initiate transfer. Make sure the new ATS understands those signals (e.g., voltage sensing, dry contacts).3.

Brands

You don't have to stick with Cummins. Generac, Eaton, ASCO, and other manufacturers make excellent ATS units. Focus on compatibility and quality.4.

Features

Consider these features:

Service Entrance Rated

If the ATS is located
before the main breaker in your service panel, it needs to be service entrance rated.

Load Shedding

This feature can disconnect non-essential loads during generator operation to prevent overloading.

Digital Display

Can provide valuable information about voltage, current, and generator status.


Remote Monitoring

Some ATS units can be monitored remotely via an app or website.5.

Permitting and Inspection

Absolutely get a permit and have the installation inspected. This protects you and your client.6.

Sizing

You will need to size the ATS appropriately to the generator.

Where to Buy
Electrical Supply Houses

Your best bet for finding a suitable ATS is through a reputable electrical supply house. They can help you choose a compatible model and answer technical questions.


Online Distributors

Online distributors like Platt Electric, CED, and Graybar can offer competitive prices, but make sure you know what you're buying and that it's returnable if it's not compatible.

Big Box Stores

While big box stores may carry some ATS units, their selection is typically limited, and their staff may not have the technical expertise to assist you properly.

Important Considerations
Safety First

Always de-energize the circuits before working on electrical equipment. Follow proper lockout/tagout procedures.

Professional Liability

Replacing an ATS involves significant risk. Ensure you have adequate insurance coverage.


Documentation

Keep detailed records of all work performed, including the ATS model number, wiring diagrams, test results, and parts replaced.

In summary:
Don't immediately assume you need a complete ATS replacement. Thoroughly troubleshoot the existing unit first. If replacement is necessary, focus on compatibility, get a permit, and use a reputable supplier. Good luck! Flag for review