Topic: FMC allowed to penetrate concrete?

User: elecshop, Location: FL, USA

Asked on: Thursday, September 5, 2024 at 10:53 am EDT
Answered on: Thursday, March 6, 2025 at 2:04 am EST

Question: According to 348.12(6) FMC shall not be used underground or 'embedded' in poured concrete or aggregate.Does this translate into FMC not being allowed to penetrate concrete?Assume after penetrating it runs horizontally under the concrete slab then penetrates upward. Sealing and concrete slab infill will be provided after. I assume this is not allowed by code?

You're right to be concerned. Let's break down why your interpretation is accurate and why the scenario you describe is likely a violation of 348.12(6). Understanding 348.12(6)

The phrase "embedded in poured concrete or aggregate" is the key. It means the FMC is completely surrounded and encased within the concrete. The concern is the potential for moisture and chemicals from the concrete to corrode the flexible metal conduit over time. Also, repairs and replacements are practically impossible.


Penetration vs. Embedding



Penetration

A single entry or exit through concrete.


Embedding

Being surrounded by concrete throughout a length of the conduit.

Your Scenario - Likely a Violation

Your description of the FMC penetrating down through the concrete, running horizontally
under the slab, then penetrating up through the slab would constitute embedding the FMC. The section running horizontally under the concrete is where the code violation would occur. Even with sealing, you are not likely to satisfy the intent of 348.12(6).

Why the Horizontal Run Under the Slab is Problematic



Continuous Contact

The horizontal run means a significant length of the FMC is in constant contact with the concrete or the ground beneath the slab. This prolonged contact increases the risk of corrosion.

Difficulty in Repair

If the FMC needs repair or replacement, accessing the horizontal section under the slab would be extremely difficult and expensive, possibly requiring breaking up the concrete.

Alternative Solutions to Consider (To avoid violating 348.12(6))


Rigid Conduit (RMC or IMC)

These are permitted for embedding in concrete. Transition to FMC only
after exiting the concrete.2.

PVC Conduit

Schedule 40 or Schedule 80 PVC conduit is also permitted for embedding. Again, transition to FMC
after exiting the concrete.3.

Running Wiring
Above the Slab

If possible, design the wiring run so it stays
above the concrete slab, perhaps using surface-mounted raceway.4.

Sleeving

If you absolutely must pass through the concrete, consider using a larger diameter rigid conduit sleeve through the concrete. This allows the FMC to run
through the sleeve, but is not embedded in the concrete itself. The sleeve would have to be large enough to allow easy insertion and removal of the FMC. It may be difficult to use a sleeve large enough to allow for replacement of the conductors in the FMC as the FMC is restricted in the fill allowed.

Important Considerations



Local Amendments

Always check with your local electrical inspector for any local amendments to the NEC. Some jurisdictions may have stricter interpretations or additional requirements.

Proper Fittings

When transitioning between different types of conduit (e.g., RMC to FMC), use the appropriate listed fittings for that purpose.


Professional Consultation:
If you're unsure, consult with a licensed electrical contractor or engineer. They can assess your specific situation and recommend the best solution to meet code requirements.In summary, while FMC can penetrate concrete, it cannot be embedded within it. The horizontal run under the slab in your scenario would be considered embedding, and is likely a code violation. Using RMC or IMC, PVC conduit, or rerouting the wiring above the slab are better alternatives. Always consult with local authorities. Flag for review