User: solarken, Location: Hudson, OH, USA
Asked on: Thursday, September 5, 2024 at 11:10 am EDT
Answered on: Thursday, March 6, 2025 at 2:04 am EST
Question: Does anyone have experience with or know of a commercial inverter with PCS control that I should look at for a site with 480Y 3ph service? Need approx 125kW of inverter capacity. Would like to land it on a 200A backfed breaker in an 800A Eaton panelboard, and avoid downsizing the main breaker. 2023 NEC.
You're looking for a UL 1741-SA certified inverter with Power Control System (PCS) functionality, capable of 125kW output at 480V, 3-phase, and compatible with a 200A backfed breaker under the 2023 NEC. This requires careful consideration of Article 705 and related sections. Here's a breakdown of what to consider and some potential inverter options
Key Considerations (NEC 2023 Relevant Articles):
Backfeed Breaker Size (NEC 705.12(B))
The 200A backfed breaker must comply with the 120% rule. The sum of the overcurrent protection devices supplying power to a busbar or conductor shall not exceed 120 percent of the rating of the busbar or conductor. In your case, 800A 1.2 = 960A. Since 800A (main) + 200A (backfed) = 1000A > 960A, you need a PCS.
Power Control System (PCS) (NEC 705.30)
A PCS is MANDATORY in your situation if you can not comply with 705.12(B). The PCS will control the inverter's output to prevent the combined currents from exceeding the 120% busbar limit. This requires the inverter to be UL 1741-SA certified and have the necessary communication and control interfaces.
UL 1741-SA Certification
This certification is crucial for grid support functions and compliance with modern interconnection standards. Verify that the inverter's datasheet explicitly states UL 1741-SA compliance.
Nameplate Rating vs. Output Power
Pay close attention to the inverter's nameplate rating. You might need a slightly larger inverter than 125kW (e.g., 130-140kW) to ensure it can reliably deliver 125kW under various operating conditions. Check the inverter's continuous power output capabilities.
Communication and Control Interfaces
The PCS needs to communicate with the inverter and potentially other grid assets (e.g., meters, utility equipment). Ensure the inverter has the necessary communication ports (e.g., Ethernet, Modbus, SunSpec Modbus).
Harmonic Distortion
Ensure the inverter meets harmonic distortion limits specified by IEEE 519. Lower THD is better for grid stability.
Monitoring
Inverters often have built-in monitoring for voltage, current, power, and other parameters. Verify remote monitoring capabilities.
Agency Approvals
Beyond UL 1741-SA, ensure the inverter is approved by your local utility and jurisdiction.
Potential Inverter Options (Check for UL 1741-SA)
Important Note
Always verify the latest specifications and compliance with your local utility before making a purchase. Consult with a qualified electrical engineer for your specific site.
SMA Sunny Tripower CORE2 (STP 125-60)
SMA is a reputable manufacturer, and the CORE2 series is known for its reliability and grid support features. The 125kW model (STP 125-60) should be examined for UL 1741-SA compliance and PCS capabilities.
Sungrow SG125CX-US
Sungrow is a major player in the inverter market. The SG125CX-US is a 125kW inverter. Check for UL 1741-SA and built-in PCS.
Fronius Eco 27.0-3 480
Fronius is known for high-quality, transformerless inverters. You will likely need multiple units to reach 125kW. They are generally more expensive but have a good reputation. Confirm UL 1741-SA and PCS functionality.
Chint Power Converters CPS SCA125KTL-DO/US
Chint is a large global manufacturer. They provide economical solutions, so check to see if their units are UL 1741-SA compliant and meet performance requirements.
Yaskawa Solectria XGI 1500 Series
Yaskawa Solectria is a well-established industrial automation company with a PV inverter division. The XGI 1500 is a string inverter, but may meet your needs.
Steps to Take
Contact Inverter Manufacturers
The best way to get accurate information is to contact the technical support or sales teams of the inverter manufacturers listed above (or others you find). Specifically, ask about: UL 1741-SA certification PCS functionality and how it integrates with your site Communication protocols and interfaces Local utility approvals Reference installations in your area2.
Consult with a Qualified Electrical Engineer
Engage a professional electrical engineer familiar with PV system design and NEC requirements. They can perform a load calculation, analyze the site-specific conditions, and ensure compliance with all applicable codes and standards. The engineer will also help with selecting the appropriate overcurrent protection and conductors.3.
Contact Your Local Utility
Discuss your project with your local utility before purchasing any equipment. They may have specific interconnection requirements and preferred inverter models. They might also have incentives or rebates available.4.
Review Datasheets Carefully
Thoroughly review the datasheets for any inverter you are considering. Pay close attention to the electrical specifications, protective features, and communication interfaces.
Important Considerations for PCS Implementation
Setpoint Communication
The PCS must have a way to receive power export setpoints (usually from a site controller, energy management system, or directly from the utility).
Response Time
The PCS should have a fast response time to quickly reduce power output when necessary to avoid exceeding the busbar rating.
Metering: Consider installing accurate metering at the point of interconnection to monitor power flow and verify the PCS is working correctly.By carefully researching inverter options, consulting with qualified professionals, and communicating with your local utility, you can successfully integrate a 125kW inverter into your 480V, 3-phase system while complying with the NEC and ensuring safe and reliable operation. Remember to prioritize UL 1741-SA certification and robust PCS functionality. Flag for review