Question: scenario-- blk, red, blu & wh and another red( or any phase) & wh in a conduit off to wherever........ What actually occurs if the two neutrals are mixed up ? anything?AND I know its different now with "common ties" but theoretically could two or even three families share a neutral ? a huge one of course. Thanks for any insight--- Doug
Okay, let's break down these scenarios.
Scenario 1: Black, Red, Blue, White & another Red (or any phase) & White in a Conduit - Neutrals Mixed Up
This is a dangerous situation and the consequences depend on exactly how the neutrals are mixed up. Here's why and what can happen: The Core Problem: Unbalanced Neutral Current. The neutral wire is supposed to carry the imbalance of current between the hot legs (black, red, blue). If the load on each hot leg is perfectly balanced, the neutral current is zero. When you have two separate circuits with their own intended neutral wires, but connect the neutrals together at any point while the hot conductors are kept separate, this is what we will see. Consequences
Overloaded Neutral
If the two circuits aren't perfectly balanced, the shared neutral wire will carry all the current from both circuits. If the neutral conductor is sized only for one circuit, it can become severely overloaded.
Overheating and Fire Hazard
An overloaded neutral wire will heat up. This can melt insulation, potentially causing a short circuit or a fire.
Voltage Fluctuations
The voltage on the circuits can fluctuate. When the shared neutral conductor resistance creates a voltage drop due to excessive current, this voltage drop affects the voltage available to the loads on both circuits. Equipment may malfunction or be damaged.
Equipment Damage
The overvoltage on the circuits can damage sensitive electronics or appliances.
Nuisance Tripping
Overcurrent protective devices (circuit breakers) may trip due to the overloaded neutral.
Electric Shock Hazard
In some cases, a failed or overloaded neutral can create a shock hazard.
Phantom Voltage/Current
You might see odd readings with a multimeter, even when things appear to be turned off. This is because the neutral is carrying current from one circuit to the other.
Example
Let's say one circuit (Black/White) is powering a 10A load, and the other circuit (Red/White) is powering a 8A load. If the neutrals are mixed, the "shared" neutral wire will carry the current from both loads (10A + 8A = 18A). If that neutral wire is only sized for 15A, it's overloaded.
How it might happen
Carelessness during wiring. Sometimes, in crowded junction boxes, it's easy to accidentally connect the wrong neutral wires. Lack of testing.
How to Prevent
Proper Wiring Practices
Meticulous attention to detail when making connections. Clearly labeling wires.
Testing
Use a multimeter to verify the voltage and continuity of each circuit before energizing it. Specifically, verify that the neutral is only connected to its intended circuit.
Scenario 2: Two or Three Families Sharing a Neutral (Theoretically) The Short Answer: No. Generally Prohibited. Why it's a Bad Idea (even with a "Huge" Neutral)
Load Imbalance is Unpredictable
You can't reliably predict or control how each family will use electricity. This makes it nearly impossible to properly size the neutral conductor. One family might use a lot of power while the others use very little, leading to the same overloaded neutral problems as above.
Safety Concerns
If one family's neutral connection fails, the other families could experience dangerous voltage fluctuations and shock hazards. It essentially puts their electrical safety at risk based on the wiring condition of their neighbors.
Code Violations
Modern electrical codes explicitly prohibit sharing a neutral between different dwelling units. The National Electrical Code (NEC) requires each dwelling unit to have its own dedicated neutral conductor. This is a fundamental safety requirement.
Metering/Billing Issues
How would you accurately meter and bill each family for their electricity usage if they share a neutral? This would be a logistical nightmare and likely inaccurate.
Why "Common Ties" are Different
You're likely referring to situations where multiple services (say, from different buildings) are all supplied by the same utility transformer. While there may be a common "grounding electrode conductor" connecting all of the buildings to earth, each building still has its own dedicated neutral conductor back to the transformer. They aren't sharing the actual neutral current-carrying conductor.
"Theoretically" (and Historically)
Before modern electrical codes, it might* have been done in some very old buildings, but this would be considered extremely unsafe and non-compliant with any current standards. Even if you found such a setup, you would be required to bring it up to code if you were making any significant modifications.
In Summary
Mixing neutrals is a recipe for electrical problems and potential hazards. Always ensure that each circuit has its own dedicated neutral. Sharing neutrals between different dwelling units is strictly prohibited by modern electrical codes for very good reason. Flag for review