Topic: XFMR Single phase the 3 Phase

User: Zyb, Location: Maine

Asked on: Thursday, September 5, 2024 at 6:40 pm EDT
Answered on: Thursday, March 6, 2025 at 2:05 am EST

Question: Hi,I'm planning to buy a transformer, would the transformer (image below) work? and can you also verify my drawing. Thanksis there a single phase to three phase Y transformer?is my 20A fuse correct [(1.25 x 11,400) / (480 x 1.732)]?is the ground wire correct?on the 480V side how many conductors should be connected to the transformer?if there are two SE11400H-US inverter does this mean that 30kVA is enough?

Okay, let's break down your questions about the transformer and your planned setup.

Analyzing the Transformer (Image Required)



Please provide the image or specific details of the transformer.
I need to know things like: KVA Rating

(e.g., 15 kVA, 30 kVA, etc.) This is crucial.

Voltage Ratings (Primary and Secondary)

What are the input and output voltage ratings (e.g., 480V Delta Primary, 208Y/120V Secondary)?


Phase (Primary and Secondary)

Is it Single-Phase to Single-Phase, Three-Phase to Three-Phase, Three-Phase to Single-Phase, etc.?

Winding Configuration

(e.g., Delta, Wye (Star), Zig-Zag). This is often represented in a diagram.Without that information, I can only give general advice.

Drawing Verification



Please provide the drawing
so I can review the wiring diagram, connections, and grounding scheme.

Answering Your Specific Questions (Based on General Assumptions)


Single-Phase to Three-Phase Y Transformer



Yes, they exist, but they are not common.
It's more practical to use a rotary phase converter or a static phase converter. Phase converters are usually designed with additional components to perform the phase transformation, and not the transformer itself. A standard transformer will not turn single-phase power into 3-phase power. It can step down the voltage of single-phase, but not change the number of phases.2. 20A Fuse Calculation

Your calculation appears to be for the primary side (480V) assuming the inverter is a single-phase device. Ipri= (1.25 x 11,400) / 480 ≈ 29.68A

You should use 30A
Important Considerations



Fuse Type

Use the correct fuse type (e.g., time-delay/slow-blow) to handle inrush currents, especially with transformers and motor loads. Refer to the inverter manufacturer's recommendation.


NEC (National Electrical Code) Compliance

Always adhere to local and national electrical codes for fuse sizing and overcurrent protection. The NEC often has specific rules for transformer protection.

Safety Factor

While your calculation uses a 1.25 factor, you might need a slightly higher factor depending on the load characteristics and NEC requirements.
3.


Ground Wire



Yes, it is important.
Transformer grounding is critical for safety and proper operation. Grounding Practices (General)



Transformer Frame Grounding

The metal frame of the transformer must be grounded to the building's grounding electrode system.

Neutral Grounding (Secondary Side)

If the secondary is a Wye (Y) configuration, the neutral point of the Wye winding MUST be grounded. This creates a solidly grounded system, which is common for providing 120V to single-phase loads. The size of the neutral/grounding conductor is based on NEC tables.


Grounding Electrode Conductor

This connects the transformer's grounding point to the building's grounding electrode (e.g., ground rod, building steel).

Equipment Grounding Conductors

All metal enclosures of equipment connected to the transformer (inverters, panels, etc.) must be connected to the grounding system.4.

480V Side Conductors



For a 3-phase Delta connection, you'll have three phase conductors (A, B, and C) plus a grounding conductor. Total = 4 conductors.
For a 3-phase Wye (Star) connection, you'll have three phase conductors (A, B, and C), a neutral conductor (N), and a grounding conductor. Total = 5 conductors. The specific configuration depends on the transformer's design and the loads you're powering. You need to know if the 480V side is Delta or Wye. Conductor Sizing

Size the conductors according to the current they will carry, and following NEC guidelines.5.

30kVA Enough for Two SE11400H-US Inverters



Let's analyze

Each inverter has a capacity of 11,400 VA or 11.4 kVA. Two inverters have a total capacity of 2 x 11.4 kVA = 22.8 kVA.

A 30 kVA transformer should be sufficient, but with very limited headroom.
Important Considerations



Inverter Output Power Factor

Inverters rarely operate at a perfect power factor of 1. If the power factor is less than 1 (e.g., 0.9), the actual current drawn will be higher. You'll need to account for this in your calculations.


Other Loads

Are there any other loads connected to the transformer besides the inverters?

Future Expansion

Is there any possibility of adding more loads or inverters in the future? If so, you should consider a larger transformer.


Transformer Loading

It's generally recommended to keep transformer loading below 80% of its rated capacity for long-term reliability and to handle occasional overloads. In this case, 22.8 kVA / 30 kVA = 76%, so it's right at the edge of what is generally accepted as good engineering practice. I recommend bumping up to at least a 40kVA transformer to give you sufficient headroom.*

Inverter Efficiency

Consider the efficiency of the inverters. The input power to the inverters will be slightly higher than their output power.

Recommendations (Without Seeing Image/Drawing)


Provide the Transformer Specs

This is the most critical step. I need to know the kVA, voltage ratings, phase configurations, and winding types.2.

Provide Your Drawing

Show the connections, wiring, grounding, and all components.3.

Double-Check All Calculations

Carefully recalculate all current, fuse, and conductor sizing based on the actual load requirements and the NEC.4.

Consult with a Qualified Electrician

This is highly recommended. Working with transformers and high voltages can be dangerous. A qualified electrician can review your plans, ensure compliance with local codes, and perform the installation safely.5.

Consider a Larger Transformer:
Given the limited headroom with a 30 kVA transformer and the potential for future expansion, it's wise to consider a larger transformer (e.g., 40 kVA or 45 kVA).Good luck with your project! I'm here to help further once you provide the necessary information. Flag for review