Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Transformer Primary Overcurrent Protection

User: muddyboots, Location: Florida

Asked on: Thursday, September 5, 2024 at 7:58 pm EDT
Answered on: Thursday, March 6, 2025 at 2:06 am EST

Question: I am a little confused on Primary OCPD for transformers, and I tend to second guess myself when questioning an engineered set of transformer/panel schedules. My understanding is Primary OCPD must be sized according to 125% of FLA of your transformer. I believe in certain cases you can or maybe even are required to round down to the next breaker size. But regardless that would still be based off of 125% of Primary FLA according to the nameplate of the transformer, correct?In my case I have a 45kVA 480 - 208Y/120 xfmr with a FLA on the nameplate of 54A, call it T1. According to the drawings they want to feed with a 50A breaker, 3-#6 and #10 ground (Cu). According to the secondary side load calc I was provided, there will only be about 15A per phase, so I understand the load on this panel is low but something still feels off. Secondary side is feeding a 150A MCB panel, with 4-2/0 and #2 SSBJ (AL).Not too sure why they called for aluminum on every secondary side xfmr, when the whole building is fed off copper, but that is beside the point I suppose.What is throwing me for a loop is the panel that is feeding T1 is also feeding a 30kVA 480 - 208Y/120 transformer in the adjacent room, call it T2, with a Primary OCPD of 70A. Fed by 3 - #4 and #8 ground (Cu). The secondary side of xfmr T2 is feeding a 100A MCB panel with 4 - #1 and #4 ground (Al). Calculated load for secondary side of T2 is only 5A per phase. It's a new construction manufacturing facility with planned provisions for future additions and manufacturing lines.My gut is telling me the breakers need to be swapped.T1 - 54 x 1.25 = 67.5 --> 70A Primary OCPD.T2 - 36 x 1.25 = 45A --> 50A Primary OCPD.My boss has insisted I install it as written on the plans so I am kind of in a pickle as he is seemingly trying to avoid sending an RFI as I suggested. Part me thinks I am making a mountain out of a mole hill, but it has been bugging me for weeks now and the other part is telling me not to energize until I have an answer. Anyways I apologize if any of this is confusing or poorly worded. I respect the heck outta this forum and I appreciate any and all feedback. Thanks for your time.

You're absolutely right to be concerned, and your calculations are correct. Let's break down why, and what you need to do.

Key Points from NEC (National Electrical Code) relevant to your situation



NEC 450.3(B) Primary Protection

This section dictates the overcurrent protection requirements for transformers, specifically when the primary current is over 9 amps. It refers you to Table 450.3(B) for maximum overcurrent protection based on the transformer impedance. This is typically what you're dealing with.


NEC 240.4(B) Next Higher Overcurrent Protective Device Rating

Allows you to round up to the next standard overcurrent device rating if the calculated value doesn't correspond to a standard rating. This is crucial. However, this is generally intended for conductor protection, which is dependent on the impedance and inrush characteristics.

NEC 450.3(B)(1) Notes

These notes are VERY IMPORTANT. Note 1 allows for an increase in the maximum primary overcurrent protection based on the transformer's impedance if the transformer's impedance is not listed on the nameplate.

Analyzing Your Situation


Your Calculations are Correct

T1 (45kVA, 54A primary FLA): 54A 1.25 = 67.5A. The next standard breaker size up is 70A. The proposed 50A is undersized and would likely trip due to inrush current. T2 (30kVA, 36A primary FLA): 36A 1.25 = 45A. The next standard breaker size up is 50A. The proposed 70A is significantly oversized.2.

Why this matters



Transformer Protection

The primary OCPD is not solely for protecting the conductors feeding the transformer. Its primary purpose is to protect the transformer itself from overcurrent conditions, including internal faults and excessive overload. An over-sized OCPD allows excessive current to flow through the transformer before tripping, potentially damaging the transformer's windings.

Coordination

The proper OCPD sizes ensure proper coordination within the electrical system. In the event of a fault on the secondary side, you want the
downstream breaker to trip first, isolating the fault while keeping the rest of the system operational. Over-sized primary OCPDs can defeat this coordination.

Code Compliance

The proposed breaker sizes do not comply with NEC 450.3(B).
3.


Aluminum vs. Copper Secondary

This isn't necessarily wrong, but it's unusual for a building primarily wired with copper. Aluminum conductors are fine for feeders and branch circuits as long as they are properly sized and terminated. The reason for using aluminum in this specific instance would need to be investigated. It could be cost-saving, or the designer may have had a specific reason. However, it needs to be properly sized and terminated, otherwise, it can pose a potential fire hazard.4.

Low Secondary Loads

The fact that the calculated secondary loads are low is irrelevant to the primary OCPD sizing. The OCPD must be sized based on the transformer's capacity, not the current connected load. Future additions and modifications could bring the load closer to the transformer's rating.

What You MUST Do


STOP and do NOT energize the circuits.
Energizing with improperly sized OCPD's poses a safety hazard and potential damage to equipment.2. Formally Document Your Concerns

Create a written record of your findings. Detail your calculations, the relevant NEC code sections, and the potential consequences of using the specified breaker sizes. This is crucial for your protection should anything go wrong.3.

Write a Formal RFI (Request for Information)

This is the correct procedure. Your RFI should: Clearly state your concerns about the primary OCPD sizing. Present your calculations based on NEC 450.3(B). Ask for clarification on the engineer's design basis. Why were these specific breaker sizes chosen? Ask for verification that the OCPD sizes comply with the NEC.4.

Insist on a Response

Your boss cannot simply ignore a legitimate safety concern backed by code. Insist that the RFI be submitted and a written response be provided by the engineer of record. If your boss continues to refuse, consider escalating your concerns to a higher level of management or, if necessary, to the AHJ (Authority Having Jurisdiction - the electrical inspector).5.

Do NOT Proceed Without a Written Resolution

You should not install the equipment in a manner that you believe to be unsafe or in violation of the electrical code.

Why is the Engineer Possibly Wrong?


There are a few possibilities: Error in Calculation

A simple mistake in calculating the primary FLA or misinterpreting the NEC.


Misunderstanding of NEC 450.3(B)

The engineer may be incorrectly focusing on conductor protection rather than transformer protection.*

Inadvertent Swap

A simple mix-up between the breaker sizes for the two transformers on the drawings.

In summary, you are right to question the design. The primary OCPD sizes appear to be incorrect and potentially dangerous. Follow the steps outlined above to formally document your concerns and obtain a written resolution before proceeding.
Flag for review

Previous Question Next Question