Question: A building load (Diversified Load) is 433kw, and all the attached load is 1-Phase load, not any single load is 3-phase in building! Should we divide load by 3 to make it 3-phase arrangement for transformer sizing or we should simply divide it P.F to size transformer? (3-ph VAC=415, 1-Ph VAC=230).
You've hit upon a crucial point regarding load balancing and transformer sizing for predominantly single-phase loads fed by a three-phase system. Here's a breakdown of how to approach this
Understanding the Problem
Unbalanced Load
A perfectly balanced three-phase system has equal loads on each phase, 120 degrees apart. If all your loads are single-phase, and they are not carefully distributed, the system will be significantly unbalanced. This leads to:
Increased Neutral Current
Large currents can flow in the neutral conductor, potentially overloading it and causing voltage drops.
Voltage Imbalance
Uneven voltage levels across the three phases. This can damage sensitive equipment, especially motors designed for three-phase operation (even if you don't have any now, you may in the future).
Transformer Derating
Transformers are designed to operate efficiently with balanced loads. An unbalanced load can cause increased heating and require you to derate the transformer (reduce its effective capacity).
Increased Losses
Unbalanced currents lead to higher I²R losses in the distribution system.
How to Approach Transformer Sizing1. Ideal Scenario: Balance the Load as Much as Possible The absolute first step is to try to balance the single-phase loads across the three phases as evenly as physically possible. This requires careful planning during the building's electrical design. Assign circuits to different phases to distribute the 433 kW roughly equally. Aim for as little difference between phase loads as possible (ideally within 10-15%). You can't achieve perfect balance, but minimizing the imbalance is critical.2. Calculate the Apparent Power (kVA) Total Apparent Power
Determine the total apparent power (kVA) demanded by the entire load. This is where the power factor (PF) comes in:
If you don't know the overall power factor for the building load, you'll need to estimate it. For a mix of lighting, computers, and other general building loads, a power factor of 0.8 to 0.9 is a reasonable starting point. Let's assume PF = 0.85:Total kVA = Total kW / Power Factor
3. Total kVA = 433 kW / 0.85 = 509.4 kVA
Addressing Load Imbalance Since you cannot have a perfectly balanced load, you should apply a imbalance factor for transformer sizing. IEC has defined a method, but the factor is from 1 to 1.15 depends on the unbalance load level. As you know it's all 1-phase load, assume the worst imbalance factor and apply 1.15 to the total kVA calculated in step #2:
Design kVA = 509.4 kVA x 1.15 = 585.8 kVA4. Select the Transformer Choose a standard transformer size that is at least equal to or slightly greater than your calculated Design kVA demand. You'll likely need a 600 kVA transformer. Future Growth