User: Stubby, Location: Climax
Asked on: Friday, September 6, 2024 at 9:44 am EDT
Answered on: Thursday, March 6, 2025 at 2:06 am EST
Question: I got turn down for not phasing my ungrounded conductors on load side of disconnect. Voltage 120/208 3ph He. noted 210.5C. I don't think that applies to the load side of the disconnect
You're right to question this. Section 210.5(C) applies to branch circuits and feeders, not the load side of a disconnecting means unless that disconnecting means is feeding a new branch circuit or feeder.
Here's a breakdown: 210.5(C): Identification for Branch Circuits and Feeders
This section requires that branch circuits and feeders supplied from premises wiring systems have a specific and permanent means of identifying the different ungrounded conductors. This usually means color-coding.
Why it's generally about Branch Circuits and Feeders
The main reason for phasing is to ensure proper and safe connections throughout the electrical system, especially when dealing with multiwire branch circuits or feeders supplying multiple loads. It helps prevent accidentally connecting to the wrong phase, which can cause shorts, equipment damage, or even fires.
The Load Side of a Disconnect
The load side of a disconnect is simply the conductors going to the equipment the disconnect protects. Think of a disconnect feeding a motor. The conductors between the disconnect and the motor generally don't need to be re-phased (if the existing phasing is already correct). If the disconnect is merely serving as a means of isolation for existing equipment with existing wiring, and you are not modifying that existing wiring beyond the disconnect, then 210.5(C) wouldn't apply.
Where 210.5(C) Might Apply on the Load Side
If you are using the disconnect as a starting point for a new branch circuit or feeder, then
yes, 210.5(C) would absolutely apply to that new wiring originating from the load side of the disconnect.
To respond to the inspector, you need to understand the specifics of the installation
What is the disconnect feeding? Is it a single piece of equipment (like a motor, HVAC unit, etc.) with pre-existing internal wiring? Or is it feeding a panelboard or other distribution point from which new branch circuits will be run?2. Are you changing the existing wiring between the disconnect and the equipment? If the wiring is unchanged and the equipment is simply being reconnected, phasing might not be required.3. Are you adding new branch circuits or feeders from the load side of the disconnect? If so, those new conductors must be phased according to 210.5(C).
Here's a possible approach when talking to the inspector
"I understand the concern for proper phasing, and I agree that 210.5(C) is important for branch circuits and feeders. However, in this installation, the disconnect is simply serving as a disconnecting means for [describe the equipment, e.g., 'an existing HVAC unit']. The existing wiring on the load side of the disconnect is unchanged, and I am not adding any new branch circuits or feeders from this point. Therefore, I believe 210.5(C) does not apply to the wiring between the disconnect and the equipment, as this is not a branch circuit or feeder itself. If I were to add a new branch circuit or feeder from the load side of the disconnect, I would certainly ensure proper phasing according to 210.5(C)."
Important Considerations
Local Amendments
Double-check your local electrical codes. Some jurisdictions have stricter interpretations or amendments to the NEC.
Best Practice
Even if not strictly required, phasing conductors on the load side of a disconnect (especially for 3-phase systems) is generally a good practice for safety and future troubleshooting. It can prevent confusion and potential hazards later on.*
Documentation: If the existing wiring is already phased correctly (e.g., properly colored or labeled), document this with photographs before and after you reconnect. This can help demonstrate compliance to the inspector.By carefully considering these points and communicating clearly with the inspector, you can likely resolve this issue. Good luck! Flag for review