Topic: Circuit Breaker Settings

User: 1965mt, Location: Virginia

Asked on: Friday, September 6, 2024 at 11:19 am EDT
Answered on: Thursday, March 6, 2025 at 2:06 am EST

Question: I have an ETU 350 LSI, 100A breaker that has four dial settings. It is located in an enclosure and serves as the panel disconnect as well. Is there a definitive guide as to how to set these? There must be an accredited way to set these dials.

You're right, properly setting the ETU (Electronic Trip Unit) dials on a breaker like that is crucial for safety and proper operation. Unfortunately, there isn't a single, universal "accredited" setting guide that applies to every ETU. The correct settings depend entirely on the specific application, the downstream load characteristics, and the applicable electrical codes. Here's a breakdown of what you need to do and why

Understanding the ETU 350 LSI Dials (Generally Speaking):
ETU = Electronic Trip Unit

This is the "brain" of the breaker. It monitors current and trips the breaker when certain thresholds and time delays are exceeded.


350

Likely refers to the frame size of the breaker. (This detail is important for finding the correct manual)

LSI

Usually indicates the types of protection provided:


L (Long-Time Delay)

Protects against sustained overloads. This is often your primary overload protection.

S (Short-Time Delay)

Protects against moderate fault currents that need to be cleared quickly, but not instantaneously. Helps with coordination between breakers.


I (Instantaneous)

Provides very fast tripping for high fault currents (e.g., short circuits very close to the breaker). Essentially, no intentional delay.

Steps to Setting the Dials Correctly


Identify the EXACT Breaker Model and Manufacturer



Critical

Look very closely at the breaker itself. There should be a model number and manufacturer's name (e.g., Eaton, Schneider Electric/Square D, ABB, Siemens). Record this information precisely. The model number might be slightly different from "ETU 350 LSI". It could include other numbers and letters after or before.


Why?
Each manufacturer and model has its own specific manual and settings. Using the wrong information could be dangerous.2. Obtain the Manufacturer's Instruction Manual



Primary Resource

The
most important step. Search online using the manufacturer's name and the EXACT model number of your breaker. Look for the instruction manual, installation guide, or trip unit programming guide.

Manufacturer's Website

Start with the manufacturer's website. They usually have online documentation.

Distributor

Contact a local electrical distributor that carries the brand. They often have access to manuals.


Example Searches

"Eaton ETU 350 LSI instruction manual" "Square D ETU 350 LSI trip unit programming guide" (if Square D/Schneider Electric) "ABB ETU 350 LSI setting guide" "Siemens ETU 350 LSI ETU adjustment instructions"3.

Understand the Load and the Electrical System



Full Load Amps (FLA)

Determine the actual, continuous current draw of the equipment being protected by this breaker. This information is often on the equipment's nameplate.


Inrush Current

Understand if the equipment has a high inrush current when starting (e.g., motors, transformers). This will influence the long-time delay setting.

Available Fault Current

Calculate or obtain the available fault current at the breaker location. This is the maximum current that could flow during a short circuit. This is critical for setting the instantaneous trip. An engineer will typically perform a short circuit study.


Coordination Study

If this breaker is part of a larger electrical system with other breakers in series, a coordination study should be performed by a qualified electrical engineer. This ensures that the downstream breakers trip before the upstream breaker, minimizing the impact of a fault.4.

Decipher the Dial Settings



The Manual is Key

The manufacturer's manual will explain
exactly what each dial controls and the range of settings available. It will provide formulas or guidelines for setting the dials based on the FLA, inrush current, and available fault current.

Typical Dial Functions (but ALWAYS refer to the manual)



Long-Time Pickup (Ir or LTPU)

Sets the current level at which the long-time delay function starts. Often expressed as a multiple of the breaker's rated current (e.g., 0.8xIn to 1.0xIn).


Long-Time Delay (tr or LTD)

Sets the time delay for the long-time function. A longer delay allows for temporary overloads (like motor starting) but will eventually trip the breaker if the overload persists.

Short-Time Pickup (Isd or STPU)

Sets the current level at which the short-time delay function starts. Higher than the long-time pickup.


Short-Time Delay (tsd or STD)

Sets the time delay for the short-time function. Shorter than the long-time delay. Coordination is vital here.

Instantaneous Pickup (Ii or IPU)

Sets the current level at which the instantaneous function trips. This should be set high enough to avoid nuisance tripping during normal inrush currents but low enough to quickly clear high-fault currents.5.

Setting the Dials (Following the Manual)



Precision

Use a screwdriver or tool appropriate for the dials to make adjustments. Be careful not to damage the dials.

Document

Record the final settings of each dial.


Testing (Optional, but Recommended)

Some advanced ETUs have testing features to verify the trip settings. Refer to the manual.

Important Considerations



Qualified Personnel



This work should only be performed by qualified and experienced electricians or electrical engineers who are familiar with power distribution systems and breaker settings.
Improper settings can create a significant safety hazard. NEC and Local Codes

Ensure that the breaker settings comply with the National Electrical Code (NEC) and any local electrical codes.

Coordination

In a system with multiple breakers, a coordination study is essential to ensure selective tripping (the breaker closest to the fault trips first, minimizing the impact on the rest of the system).


Documentation

Maintain a record of all settings, calculations, and the manufacturer's manual for future reference.

Arc Flash

Be aware of arc flash hazards when working on electrical equipment. Wear appropriate PPE (Personal Protective Equipment).

In Summary:


Finding the exact manufacturer's manual for your specific ETU 350 LSI breaker is
absolutely essential*. That manual will provide the definitive guidance for setting the dials based on your application. Do not guess or rely on general information. Contact the manufacturer or a qualified electrical professional for assistance if you are unsure. Safety is paramount. Flag for review