Topic: 705.12(B)(3)(6)

User: Gridtied, Location: Colorado

Asked on: Friday, September 6, 2024 at 11:25 am EDT
Answered on: Thursday, March 6, 2025 at 2:07 am EST

Question: I need a little help on this 2020 NEC 705.12(B)(3)(6). I am reviewing plan sets where the customer has a 200A MMC with a 150A MB and feed through lugs that feed a 200A ML panel through 3/0 AL @ 155A. The customer wants to add a 40A CB for the PV (31.05A x 125% = 38.8A) to the ML panel. The meter/main currently does not have loads in it, but could have them added later. I believe that an OCPD is needed t either end of the 3/0 AL feeder to protect the feeder. I saw a video from Mayfield renewables that does a decent job of explaining a similar scenario, but only when the POC is in the MMC. The 2023 NEC seems to agree with my interpretation, but the 2020 NEC just seems to lean towards the POC in the MMC. See the image below, but move the PV POC to the distribution panel.

You're right, that 2020 NEC 705.12(B)(3)(6) section can be tricky and is much clearer in the 2023 NEC. Let's break down why you're likely correct and how to interpret the 2020 code in this scenario.

Understanding the Problem and the Relevant Code

The core issue is the potential for overcurrent on the 3/0 AL feeder between the meter/main (MMC) and the distribution panel (ML panel). The feeder is only rated for 155A. Adding PV backfeed to the ML panel can increase the current flowing towards the MMC, potentially exceeding the 155A rating of the 3/0 AL.2020 NEC 705.12(B)(3)(6) - Interpretation and Application

The 2020 NEC 705.12(B)(3)(6) deals with backfed breakers and the busbar rating. While it's true that many examples focus on the connection at the service (your MMC), the underlying principle still applies: the busbar (or conductor) must be adequately rated for the potential current flowing through it.Here's how it applies to your scenario: ML Panel Busbar

First, the busbar in the ML panel itself needs to meet the 120% rule. If the ML panel is rated for 200A, the maximum backfed breaker size is (200A
120% - 200A = 40A). Your proposed 40A breaker is fine from the perspective of the ML panel busbar.

Feeder Protection (The Key Issue)

The crucial point is the 3/0 AL feeder. You can't simply look at the ML panel busbar limitations. The feeder connecting the MMC to the ML panel becomes part of the
overall system and must be protected.

705.12(B)(3)(6) Implied Extension

While 705.12(B)(3)(6) doesn't explicitly state "you must protect the feeder," the implication is that the entire system, including the feeder, must be adequately rated. If the feeder is a weak link in the overall system, you must address it. If the feeder rating is less than the supply side overcurrent device, a OCPD is required on the distribution panel to protect the feeder.

Why You Likely Need Overcurrent Protection


You are likely right that you need an overcurrent protective device (OCPD) at the distribution (ML) panel to protect the 3/0 AL feeder. Here's the reasoning:1. Potential for Overcurrent

Even if the MMC currently has no loads, it could have loads added in the future. If the MMC has 150A Main Breaker and loads are added, the potential for the 3/0 AL to be overloaded increases. This is especially true if the PV system is producing its maximum output.2.

Feeder Rating vs. Supply

The 3/0 AL is rated for 155A. The 150A main breaker in the MMC is adequately protecting the feeder from the supply side. But the PV backfeed from the distribution panel can cause current to flow "backwards" and exceed 155A.

Solutions Under the 2020 NEC


Given these conditions, here are a few ways to address the situation while conforming to the spirit and intent of the 2020 NEC (understanding it's less explicit than the 2023 code):1. Reduce the PV Breaker Size

This is the simplest solution if possible. If you can downsize the PV breaker in the distribution panel to a value that, even with maximum MMC loads, would not exceed 155A on the 3/0 AL, it becomes more palatable.2.

OCPD at the Distribution Panel (Your Preferred Solution)

This is the most robust and safest approach. Install a suitably sized OCPD at the distribution panel end of the 3/0 AL feeder. This OCPD would protect the feeder from overcurrent due to PV backfeed. Size this OCPD so it would trip before the 3/0 AL is overloaded. This OCPD should be on the line side of the 40A PV breaker in the ML panel. Be mindful of selective coordination if other OCPDs are involved.3.

Feeder Upgrade

Replace the 3/0 AL with a conductor that can handle the maximum potential current. This is often the most expensive solution.

Important Considerations
AHJ Approval is Key

This is a gray area in the 2020 NEC. The Authority Having Jurisdiction (AHJ) has the final say. Be prepared to discuss your reasoning and demonstrate how your proposed solution ensures safety and prevents overcurrent on the feeder.


Future Loads

Make sure to factor in potential future loads on the MMC when determining the maximum allowable PV backfeed.*

Voltage Drop

Always calculate voltage drop for the feeder to ensure it's within acceptable limits.

In Summary


While the 2020 NEC isn't as crystal clear as the 2023 version, the fundamental principle of protecting conductors from overcurrent still applies. The 3/0 AL feeder is the weak link in your system, and you need to address it. Your assessment that an OCPD at the distribution panel is needed is likely correct and represents a prudent approach to ensure safety and code compliance. Prepare to explain your reasoning and have a thorough discussion with your AHJ. Flag for review