Question: Hello!I install a lot of Tesla wall connectors and Tesla recommends to use Neurio active energy monitor controller for applications like apartment building panels where it adjusts output based on usage.I'm having a lot of issues with them passing inspections. As I expected just had another inspection for another installation and new set of issues arised. Inspector said that this device is "illegal". Even though he couldn't answer when I asked him how he passed these installations in the past.Now got a "fail" for mixing class 1 and class 2 wiring. Inspector said that this device is illegal because :A. CTs wiring (by Generac btw) are rated 300V and couldn't be in the same enclosure.B. My com low voltage wire can't run in the same conduit as high voltage wire to the charger.C. Tap conductor ground wire must be sized to the main wire ground size. 100A apartament breaker/feeder, my tap to the sub panel is #6 and #10 ground. He said that my tap ground to the sub panel has to be also #8?He also didn’t like that Neurio energy monitor is located in the same enclosure of the panel.I followed instructions from Tesla. Here is their installation/commissioning video:

Okay, this is a common scenario when dealing with inspections and new technologies. It sounds like you're running into a classic clash between established code interpretations and the evolving landscape of energy management systems. Let's break down each of the inspector's points and offer potential solutions or explanations.

Important Disclaimer

I am an AI. I cannot provide electrical code interpretations. This information is for general discussion only and should not be taken as professional electrical advice. You MUST consult with a qualified and licensed electrical inspector or engineer to ensure your installations meet all applicable local, state, and national codes.

General Strategy



Stay Calm and Professional

Inspectors are generally trying to ensure safety. Maintaining a respectful and collaborative attitude will make the process smoother.


Document Everything

Keep meticulous records of all components, wiring, and installation procedures. Include manufacturer's specifications and installation manuals.

Involve Tesla and/or Neurio/Generac Tech Support

If the inspector is questioning the overall system design, get written confirmation from Tesla or Neurio/Generac that the installation is compliant with relevant standards. This will carry more weight than your interpretation alone.


Request Specific Code References

Politely ask the inspector to provide the specific section(s) of the electrical code they are citing for each violation. This is crucial for understanding their reasoning and formulating a response.

Consider a Second Opinion

If you're truly stuck, consider asking a different inspector to review the installation. Sometimes a fresh perspective can help.

Addressing the Inspector's Points



A. CTs Wiring (300V) in the Same Enclosure



The Issue

The inspector's concern is likely based on the separation requirements between high-voltage (line voltage) and low-voltage wiring within an enclosure. Current Transformers (CTs) are used to measure the current of the load and provide an output to the monitoring device.

Possible Code References

NEC 300.3(C) and 725.136 are related.


Explanation/Solutions



CTs as Instrumentation

The key argument is that CT wiring,
while connected to high-voltage conductors, carries a low-voltage signal to the Neurio. The CTs provide isolation. The 300V rating of the wiring confirms that it is designed to be connected to the high voltage side in a safe manner.

Manufacturer Support

Obtain documentation from the CT manufacturer (Generac) or Neurio that explicitly states the CT wiring meets the requirements for use within the panel enclosure. This documentation should include certifications or standards that the CTs meet.

Barriers/Separation

If possible (and code allows), physically separate the CT wiring from the line-voltage wiring within the panel. This could involve using a non-conductive barrier. Some panels already have built-in provisions for this type of separation.


Separate Enclosure for the Neurio

Relocate the Neurio to a separate enclosure, close to the panel, and run the CT wires into that enclosure. This eliminates the potential conflict by physically separating the low-voltage and high-voltage circuits. Ensure this separate enclosure is properly grounded.

B. Low-Voltage Communications Wire in the Same Conduit as High-Voltage Wire



The Issue

This is a classic and very common concern. Running low-voltage communications wiring (e.g., for Modbus or Ethernet) in the same conduit as line-voltage power conductors can introduce electrical noise and potential safety hazards.


Possible Code References

NEC Article 725, Article 800, and specifically, NEC 300.3(C)(1), 725.55(A), and 725.136(D)

Explanation/Solutions



Dedicated Conduit

The best and often required solution is to run the low-voltage communication wire in a separate, dedicated conduit from the panel to the Tesla Wall Connector. This completely eliminates the mixing of voltage classes.

Separation within a Raceway

If a dedicated conduit is absolutely impossible, check if the code allows you to run the low-voltage wires in a separate compartment within a multi-compartment raceway (if such a raceway is used). This provides physical separation within a single conduit structure. (Likely won't be allowed in this case.)


Shielded Cable and Grounding

Use a shielded communications cable (e.g., Ethernet cable with a foil or braid shield). Properly ground the shield at one end only (typically at the panel end) to prevent ground loops. This can help mitigate noise. However, this is usually not sufficient to meet code requirements for separation.



Fiber Optic

Using fiber optic cable avoids the issue altogether since it does not conduct electricity. A fiber to Ethernet converter would be needed at each end.

C. Tap Conductor Ground Wire Sizing



The Issue

The inspector believes the grounding conductor for your tap to the subpanel must be sized proportionally to the main feeder ground (in this case #8 AWG).

Possible Code References

NEC 250.122 (Equipment Grounding Conductor Sizing)


Explanation/Solutions



Understanding 250.122

This section dictates the minimum size of equipment grounding conductors based on the
overcurrent protective device protecting the circuit. Your #10 ground wire to your tap conductor is your equipment ground conductor for the tap circuit.

Your Situation

You have a 100A apartment breaker, your tap to the sub-panel is #6 and #10 ground. The Tesla Wall Connector is connected from the tap to the sub-panel. So the size of your tap conductors, and the size of the OCPD protecting the tap will determine the wire size that must be used for the ground wire.

The inspector may be wrong

If the OCPD protecting your tap is less than or equal to 60 amps (which it should be based on the #6 conductors being tapped from the 100A circuit), than a #10 AWG wire is sufficient. Check Table 250.122 in NEC.


Clarify with the Inspector

Discuss this with the inspector. Show him the relevant tables in the NEC and explain your understanding of the tap circuit. If he still insists on a larger ground, ask him to provide a specific code reference that supports his requirement.

Neurio Location in the Panel



The Issue

The inspector may have concerns about heat dissipation, working space, or the general appropriateness of installing the Neurio inside the main electrical panel.


Explanation/Solutions



Manufacturer's Specifications

Check the Neurio's installation manual. Does it explicitly state that it's permissible to install the device inside a panel? If so, highlight this for the inspector.


Working Space

Ensure that the Neurio doesn't obstruct working space within the panel. It needs to be installed in a way that allows for safe access to breakers and other components.

Heat Dissipation

The Neurio does generate some heat. Make sure the panel has adequate ventilation. If the panel is already crowded or poorly ventilated, relocating the Neurio to a separate enclosure might be necessary.


Separate Enclosure (Recommended)

As mentioned earlier, moving the Neurio to a separate enclosure adjacent to the panel often resolves this issue and simplifies the overall installation.

Regarding Tesla's Instructions/Video



Important Note

Tesla's instructions are
guidelines not legal documents. While they likely strive for code compliance, local interpretations can vary, and Tesla is not responsible for ensuring your installation meets your local code.

Use as Supporting Evidence

You can certainly use Tesla's installation video as supporting evidence that you're following their recommended practices. However, be prepared to justify those practices with code references if challenged by the inspector.

In Summary:This situation is frustrating, but by addressing each point systematically, providing clear documentation, and engaging in a collaborative dialogue with the inspector, you should be able to resolve the issues and get your installations approved. And remember, if all else fails, consider consulting with a qualified electrical engineer for a professional opinion and support. Flag for review