Question: Do we need to connect grounding transformer to LV side for each solar transformer?We have two 2000kVA XFMR connected in loopUtlity requirement-Three phase transformers on the load side of Main Disconnecting Means should be equippedwith suitable protective devices to prevent the Loss of Phase condition.Customers must carefully evaluate the operational characteristics of transformers located onthe load side of Main Disconnecting Means. Many step up / step down transformermanufacturers use a standard three-legged core design. On a grounded-wye system, the Wye/ Wye-grounded construction reduces the likelihood of ferroresonance and provides a groundsource. However, under the loss of phase condition (unbalanced voltage) or unbalanced load,this can create zero sequence voltage (zero sequence flux in the core). In the three-leggedconstruction, there is no path for this flux to circulate within the core. Thus, the flux jumpsthrough the tank and air gap. Flux through the transformer tank (enclosure) creates localizededdy current heating so much as to discolor / overheat the unit and possibly leading to failure.It is highly recommended to incorporate one of the following transformer options to helpmitigate the conditions:1. One side of the transformation being Delta connected.2. A delta tertiary connection associated with the Wye / Wye Configuration.3. Three individual single-phase transformers connected to form a three-phase bank ortriplex construction.4. A four- or five-legged core.5. Shell type core construction.6. A three-legged transformer with primary protective devices that sense loss of voltagemagnitude and unbalance. When excessive voltage unbalance is detected, allprimary phases need to be disconnected simultaneously.If this voltage transformation is associated with a DER installation (solar / energy storage /wind) that utilizes inverters, a Wye / Wye configuration with a Delta connected tertiarywinding may prevent the inverter from sensing a Loss of Phase event on a three-phasesystem. The consequence of not detecting the Loss of Phase condition would be aviolation of Standard IEEE 1547. Compliance with IEEE 1547 is required by AmerenIllinois and Ameren Missouri for all customer with DER interconnections.
Let's break down this utility requirement and your specific situation to determine if a grounding transformer is needed at each solar transformer's LV side.
Understanding the Utility Requirement
The utility (Ameren) is primarily concerned about the effects of loss of phase (unbalanced voltage) on three-legged core Wye-Wye transformers. Here's why: Three-Legged Core Transformers
These are common and economical. However, they can have problems with zero-sequence currents during unbalanced voltage conditions. The zero-sequence flux, without a dedicated path, creates eddy currents in the tank, leading to overheating and potential failure.
Grounded-Wye/Wye
While a grounded-wye connection provides a path for ground fault currents and reduces ferroresonance risk, it doesn't inherently solve the unbalanced voltage issue in a three-legged core.
Loss of Phase (Unbalanced Voltage)
This can occur due to a blown fuse, a broken conductor, or other faults in the upstream distribution system.
Mitigation Strategies
The utility recommends several options to address this issue:1.
Delta Connection
One winding (primary or secondary) being delta provides a path for circulating zero-sequence currents. This is a very effective solution.2.
Delta Tertiary Winding
Adding a small delta-connected winding (tertiary) inside the transformer provides a path for zero-sequence currents without affecting the main transformation ratio. This is common in larger transformers.3.
Single-Phase Transformers or Triplex Construction
Each transformer handles only one phase, eliminating the zero-sequence current issue.4.
Four- or Five-Legged Core
These core designs provide a flux path for zero-sequence currents within the core itself.5.
Shell Type Core Construction
Similar to 4- or 5-legged cores, offers a good flux path.6.
Protective Devices
Relays that detect voltage unbalance and disconnect all primary phases simultaneously before overheating occurs. This requires sophisticated protection.
DER (Solar) Considerations
The utility explicitly notes that if your system involves inverters (as solar installations do), a Wye/Wye configuration with a Delta Tertiary Winding might prevent the inverter from detecting a loss of phase condition. This is a critical point because IEEE 1547 (required by Ameren) mandates that DER systems disconnect from the grid under abnormal conditions, including voltage unbalance. If the inverter doesn't "see" the unbalance because of the transformer configuration, it won't disconnect, leading to a violation.
Analyzing Your Specific Case
You have: Two 2000kVA Transformers
Connected in a loop (this implies they are likely operating in parallel)
Utility Requirement
As described above.
Do You Need Grounding Transformers on the LV Side?Not necessarily. A grounding transformer creates an artificial neutral when one doesn't naturally exist (like in a delta system). Your primary concern, based on the utility's requirement, isn't necessarily the presence of a neutral; it's managing zero-sequence currents during unbalanced voltage conditions.Here's a decision process based on the utility's recommendations and your specific situation
1.
Transformer Design is Key
The most important factor is the internal design of your 2000kVA transformers. Are they:
Three-Legged Core? This is the most common and the one the utility is worried about. Four- or Five-Legged Core? Much better, as they can handle zero-sequence flux internally. Shell Type Core? Also a good option. Unknown? You need to find out! Check the transformer nameplate or contact the manufacturer.2. If Three-Legged Core
You must implement one of the mitigation strategies the utility outlines:
Easiest (Likely Best)
Have one side of the transformer windings be
Delta-connected. This provides a natural path for zero sequence currents. Delta-Wye configuration
If the high voltage side is Delta, and low voltage is Wye-Grounded, no need for grounding transformer.
Wye-Delta configuration
If the high voltage side is Wye-Grounded, and low voltage is Delta, no need for grounding transformer.
Delta Tertiary Winding
If you have Wye/Wye with a Delta Tertiary, verify this doesn't interfere with the inverter's ability to detect loss of phase and meet IEEE 1547. You might need to adjust inverter settings or protection schemes. Also be aware of the added cost of this option.
Protective Relaying
Implement fast-acting voltage unbalance protection that simultaneously disconnects all phases of the transformer primary if excessive unbalance is detected. This is complex and requires careful coordination with the utility.3.
If Not Three-Legged Core (Four- or Five-Legged, Shell)
The utility's primary concern is already addressed. A grounding transformer is likely not needed solely for the loss-of-phase issue. However, you still need to ensure you have proper grounding for fault current protection.
Specific Actions You MUST Take Determine Transformer Core Type
This is the first and most critical step.
If Three-Legged Core, Choose a Mitigation Strategy
The simplest and often best is to have one of the transformer windings delta connected.
Verify IEEE 1547 Compliance
If using a Delta Tertiary Winding, ensure your inverters can still detect voltage unbalance and disconnect as required by IEEE 1547. Work with your inverter manufacturer and a qualified engineer.
Consult with the Utility (Ameren)
Discuss your proposed solution with Ameren to ensure it meets their requirements. Get their approval in writing.
Proper Grounding
Regardless of the mitigation strategy, ensure you have adequate grounding for safety and fault current protection on the low voltage side of the transformer. This might involve a solid neutral ground or a high-resistance ground, depending on your specific system design.
Coordination Study
Perform a coordination study to ensure all protective devices (fuses, breakers, relays) are properly coordinated to protect the equipment and the grid.
In summary, you likely do NOT need a grounding transformer IF
The transformer(s) are designed with a 4 or 5-legged core, or is a shell-type design
One side of the transformer winding is delta connected (Primary or Secondary)It is recommended to consult a qualified electrical engineer for assistance in applying the utility requirements. Flag for review