User: shivam.pandey, Location: Chula Vista
Asked on: Friday, September 6, 2024 at 6:21 pm EDT
Answered on: Thursday, March 6, 2025 at 2:08 am EST
Question: Do we need to connect grounding transformer to LV side for each solar transformer?We have two 2000kVA XFMR connected in loopUtility requirement from service manual-Three phase transformers on the load side of Main Disconnecting Means should be equippedwith suitable protective devices to prevent the Loss of Phase condition.Customers must carefully evaluate the operational characteristics of transformers located onthe load side of Main Disconnecting Means. Many step up / step down transformermanufacturers use a standard three-legged core design. On a grounded-wye system, the Wye/ Wye-grounded construction reduces the likelihood of ferroresonance and provides a groundsource. However, under the loss of phase condition (unbalanced voltage) or unbalanced load,this can create zero sequence voltage (zero sequence flux in the core). In the three-leggedconstruction, there is no path for this flux to circulate within the core. Thus, the flux jumpsthrough the tank and air gap. Flux through the transformer tank (enclosure) creates localizededdy current heating so much as to discolor / overheat the unit and possibly leading to failure.It is highly recommended to incorporate one of the following transformer options to helpmitigate the conditions:1. One side of the transformation being Delta connected.2. A delta tertiary connection associated with the Wye / Wye Configuration.3. Three individual single-phase transformers connected to form a three-phase bank ortriplex construction.4. A four- or five-legged core.5. Shell type core construction.6. A three-legged transformer with primary protective devices that sense loss of voltagemagnitude and unbalance. When excessive voltage unbalance is detected, allprimary phases need to be disconnected simultaneously.If this voltage transformation is associated with a DER installation (solar / energy storage /wind) that utilizes inverters, a Wye / Wye configuration with a Delta connected tertiarywinding may prevent the inverter from sensing a Loss of Phase event on a three-phasesystem. The consequence of not detecting the Loss of Phase condition would be aviolation of Standard IEEE 1547. Compliance with IEEE 1547 is required by AmerenIllinois and Ameren Missouri for all customer with DER interconnections.DER utility requirement-For 5 kV and 15 kV class distribution systems, Ameren Illinois circuits most often employ 4‐wireconfigurations with multiple neutral grounding connections. To mitigate potential ground faultovervoltage (GFOV) conditions, new RLG customer interconnection transformers may berequired to act as a ground source, as determined by Ameren Illinois during the interconnectionstudy process.RLG systems required to act as ground sources should be designed for a coefficient ofgrounding of 0.8 or less without the consideration of connected loads for ground faults on theAmeren Illinois feeder when temporarily islanded with the RLG. The interconnectiontransformer configuration may be grounded‐wye on the high voltage side and grounded‐wyeon the low voltage side with a supplemental grounding transformer, or grounded‐wye with aneutral impedance on the high voltage side and delta on the low voltage side.Three‐phase, three‐legged, core form transformers should not be used because internalmagnetic coupling can disguise the loss of an incoming phase and prevent the proper shut‐down of inverter‐connected generation. This type of core form is more prone to ferro‐resonance during open phase conditions and grounded‐wye / grounded‐wye windingconfigurations typically produce excessive tank wall heating during ground faults due to zero‐sequence currents circulating in the tank.
Okay, let's break down the requirements and determine if you need a grounding transformer on the LV side of each solar transformer, considering your loop configuration.
Understanding the Utility Requirements
The utility (Ameren) is concerned about two primary issues:1. Loss of Phase (Unbalanced Voltage)
Three-legged core transformers are susceptible to overheating due to zero-sequence currents if there's a loss of phase or significant voltage unbalance on the primary (MV) side. They are also concerned about the inverter's ability to properly shut down during a loss of phase due to the transformer masking the condition.2.
Ground Fault Overvoltage (GFOV)
On 4-wire grounded wye distribution systems, the utility wants to ensure that the solar generation (RLG) doesn't cause excessive voltage rise on the un-faulted phases during a ground fault on their system. This is why they require a coefficient of grounding of 0.8 or less when the RLG is islanded with the utility.
Analyzing Your Situation Two 2000kVA Transformers in a Loop
This loop configuration likely refers to the MV side of the transformer. This impacts how faults propagate and how grounding is perceived by the system. It is important to confirm whether the loop is configured with any impedance or other mitigation.
Transformer Type
The utility is specifically warning against using standard three-legged core transformers with Wye-grounded / Wye-grounded connections because of the zero-sequence current issue.
DER (Solar) Application
The DER aspect amplifies the concern about loss-of-phase detection, as the inverter must trip quickly under such conditions to comply with IEEE 1547.
Do you NEED a grounding transformer on the LV side?
It depends. Here's a breakdown of the scenarios and how to interpret the requirements:1. Transformer Winding Configuration and Core Type
If your transformers are NOT Wye-grounded / Wye-grounded AND three-legged core
You might not require a grounding transformer. You could use Delta-Wye configuration. However, you MUST carefully consider if you still meet the Ground Fault Overvoltage (GFOV) requirements for Coefficient of Grounding of 0.8 or less. A Delta winding can provide some grounding contribution, but it might not be enough.
If your transformers ARE Wye-grounded / Wye-grounded AND three-legged core
You will likely need a grounding solution. This is because the utility highly recommends against this configuration due to the risk of ferroresonance, tank heating, and masking loss-of-phase conditions. You have several options from the utility document, but let's examine the possibility of using a grounding transformer: Grounding Transformer on the LV side
You could potentially add a grounding transformer on the LV side of each solar transformer to provide a low-impedance path for ground fault currents. However, this doesn't solve the loss of phase issue with the three-legged core transformer masking the condition from the inverters. Therefore, this is probably not the best solution if the other transformers are already Wye-grounded / Wye-grounded.
Delta Tertiary Winding
If your existing transformers do not have this, this would be the most effective solution.
Alternative Transformer Core or Winding Type
This is the ideal solution if transformers have not been ordered/purchased yet.2.
Ground Fault Overvoltage (GFOV) Requirement
Regardless of your transformer's core and winding configuration, you MUST perform an interconnection study to determine if your system meets the utility's GFOV requirements. This study will involve modeling your solar generation and the utility's grid to assess the coefficient of grounding. If the study shows you don't meet the GFOV requirements without additional grounding, you will need to implement one of the grounding solutions (grounding transformer, zig-zag transformer, or other method) to bring the coefficient of grounding within the acceptable range.
Recommendations
Clarify Transformer Details
Immediately determine the core type (three-legged, four/five-legged, shell type) and winding configuration (Wye-grounded/Wye-grounded, Delta/Wye, etc.) of your existing transformers.2.
Perform Interconnection Study
This is the most crucial step. The study will determine if you need a supplemental grounding solution to meet the GFOV requirements. Work closely with the utility and a qualified engineering firm to conduct this study.3.
Consider the Utility's Recommendations
If you are using three-legged core transformers, the utility strongly encourages using one of their recommended mitigation strategies (Delta winding, delta tertiary, different core type, or protective devices that sense loss of voltage).4.
If Using Three-Legged Core Transformers AND Wye-grounded LV
Consider the cost and complexity of a grounding transformer. A delta tertiary is often a better technical solution. It's essential that the inverter can detect loss of phase conditions.5.
Simultaneous Disconnect
If Option 6 is considered from the utility, ensure all phases are disconnected as zero sequence may appear in the transformer due to single phase source, which is not a utility standard. This means that the grid tied system may still experience single phase voltage which is not standard.
In summary, you might need a grounding transformer, but it depends on your existing transformer configuration, the results of the interconnection study, and your chosen method for meeting the utility's requirements for loss-of-phase protection and ground fault overvoltage mitigation. It is highly recommended to choose a better transformer that is not a three legged core or with a different transformer configuration (delta/wye) to avoid the need for a grounding transformer. Flag for review